Discuss Earthing inside a submain panel from main swa incomer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

G

Guest 004

OK, going to keep this short.

Supply is 150mm 4 core SWA, with NO supplymentary earth ( calcs done by others, )

QUESTION IS. Do you NEED to run an earth ( is it a regulation) from banjo on inside to earthing terminal inside board. Common sense and a simple ohms continuity test (0.01 ohms) says no. Just want people's thoughts on this.
 
Is the gland fitted into a gland plate?
Is the banjo fitted with heavy duty serrated washers to ensure good contact through any paint or the paint has been removed fully from the contact area?
Is the enclosure a 1 piece enclosure or segmented panelling which is screwed together?

If in doubt, tail it out!
 
Did common sense and simple continuity testing get a value of 0.01 ohms at a test current roughly equivalent to the PFC at the panel? A value of 0.01 measured with a multimeter with a sub-1A test current could be through a tiny spot of good contact which will pretty much melt instantly under the available fault current (which is presumably significant on that size supply)

In short, unless you have ensured a good high current connection to the earth bar by other mans then yes a suitably sized flylead is a damned good idea if not essential.
 
Reg 543.2.7...where the protective conductor is formed by metal conduit, trunking or ducting or the metal sheath and/or armour of a cable, the earthing terminal of each accessory shall be connected by a separate protective conductor to an earthing terminal incorporated in the associated box or other enclosure.
 
Did common sense and simple continuity testing get a value of 0.01 ohms at a test current roughly equivalent to the PFC at the panel? A value of 0.01 measured with a multimeter with a sub-1A test current could be through a tiny spot of good contact which will pretty much melt instantly under the available fault current (which is presumably significant on that size supply)

In short, unless you have ensured a good high current connection to the earth bar by other mans then yes a suitably sized flylead is a damned good idea if not essential.

The safety devices will open mate, the sheath will carry any fault currents that are generated, and the protective devices are 80kA. Don't want to go that route really, just want people's thoughts in the real world.

OK, so I m okay with with a 'fly lead' from banjo, so now what size?
 
The safety devices will open mate, the sheath will carry any fault currents that are generated, and the protective devices are 80kA. Don't want to go that route really, just want people's thoughts in the real world.

OK, so I m okay with with a 'fly lead' from banjo, so now what size?


Adiabatic equation and table 54.7
 
Last edited:
Is the gland fitted into a gland plate?
Is the banjo fitted with heavy duty serrated washers to ensure good contact through any paint or the paint has been removed fully from the contact area?
Is the enclosure a 1 piece enclosure or segmented panelling which is screwed together?

If in doubt, tail it out!

Good answer like it.
No gland plate, no serated washers, 1 piece enclosure.
 
No supply into the building yet, but the HV chamber is next door, so we are looking at Zs values of 0.01 by calculation, as we are top of the Tx
 
I repeat the HV chamber is next door, so from thr Tx the run is about 6 metres fed by 630mm parallel supply, so we can safely say that the impedance will be on 0.01. Again I repeat all this has been calculated and all protective devices have been designed to take fault current of 0.01 x root 3.
 
If and when you test it, you may have to introduce a fixed resistive component as the TX is so close that the resolution of your testers won't be able to measure it thus your reading will fluxuate wildly ;)
 
I repeat the HV chamber is next door, so from thr Tx the run is about 6 metres fed by 630mm parallel supply, so we can safely say that the impedance will be on 0.01. Again I repeat all this has been calculated and all protective devices have been designed to take fault current of 0.01 x root 3.


Why haven't they specified the size of the protective conductor?
 
The safety devices will open mate, the sheath will carry any fault currents that are generated, and the protective devices are 80kA. Don't want to go that route really, just want people's thoughts in the real world.

OK, so I m okay with with a 'fly lead' from banjo, so now what size?

Not your mate!

The sheath won't carry any fault current at all if it is SWA as the sheath is made of PVC, the armour will carry the fault current.
I was not saying anything about the cable's ability to handle the fault current, but that of the connection between gland and enclosure. The connection to the connection to the gland will have to carry that exact same fault current, if it is only making contact on a tiny area like the rough edge of the hole then it may well break down when that fault current flows before the protection operates.

Personally I prefer to use earthing nuts (yes they do make them that big) or else fit a brass gland plate with holes tapped to take the glands of the the SWAs terminated to the board.
 
OK, that will equate to about a 6mm :)

Didn't want to go the abiabatic route, because an earth was not being taken back to source, as the the calcs state no supplymentary.

What do you mean you don't want to go the adiabatic route? How did you calculate that the armour is adequate without using the adiabatic?
Supplementary what?
 
Not your mate!

The sheath won't carry any fault current at all if it is SWA as the sheath is made of PVC, the armour will carry the fault current.
I was not saying anything about the cable's ability to handle the fault current, but that of the connection between gland and enclosure. The connection to the connection to the gland will have to carry that exact same fault current, if it is only making contact on a tiny area like the rough edge of the hole then it may well break down when that fault current flows before the protection operates.

Personally I prefer to use earthing nuts (yes they do make them that big) or else fit a brass gland plate with holes tapped to take the glands of the the SWAs terminated to the board.

Oh I stand corrected, sorry I thought the sheath was the armour.
 

Reply to Earthing inside a submain panel from main swa incomer in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K
Hi all, looking for a bit of advice and confirmation on my proposed plans for a SWA sub main to a ISO metal storage container. I've calculated the...
Replies
23
Views
3K
Good Morning everyone. Quick question regarding a sub main from a TNCS supply feeding an outbuilding on TT. This is a domestic installation not...
Replies
7
Views
3K
Hopefully someone wiser than me can help explain some odd measurements I’ve taken at my own home. This is a long read, I’ve tried to give as much...
Replies
21
Views
4K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock