Discuss eicr buried cables in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

T

thekingiam

doing an eicr and have swa going into outside enclosure into terminal block into 10mm twin and earth then into plastic trunking going underground to outbuilding located about 15 meters away.
outbuildings electrics are then split using fcu's for lighting electric door an alarm etc.
i am looking into what regs say and i thought twin and earth needed beter protection than the plastic corugated enclosures?
page 122 on site guide says for use underground in conduits or pipes?
 
Another problem a shower cable has been run in pvc trunking and sealed with silicon down from ceiling and into bottom of shower what reg if any?
 
If there isn't a means of a single point of isolation at the outbuilding it won't comply!! The outbuilding's electrical supply needs, should be met by a CU with DP isolator or RCD device, (depending on arrangement) with an appropriate number of OCPD ways.


If this 10mm cable has been installed in that flimsy corrugated conduit, it's probably already crushed on to the cable, under the weight of back-filled soil!! Personally i'd never even contemplate using T&E cable in any underground routed conduit/duct. It was never designed for such installations!!
 
I would test the circuit and ensure readings are good.
LIM the reference method as you can't prove it on an EICR.
Put an observation down down if you feel that way inclined.

You cant put a limitation on for the installation method, it should have N/V "not verified". limitation is not for this purpose. In my humble opinion it is code 3. Cant justify code 2 because what is the worse that can happen? the cable crushes and the breaker trips.

Cheers...........Howard
 

Reply to eicr buried cables in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Did an EICR that passed 5 years ago Several things in the picture raised concerns for me. Comments please - photo at end First photo shows a...
Replies
9
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
425
Morning all So the site I'm based at recently had some work done (think partitioners). This package of work included electrical. This was...
Replies
44
Views
8K
Hi everyone Ive just had an electrical condition report conducted on a mixed-use property, and I am extremely surprised that after the last report...
Replies
11
Views
2K
Hello All, new to the forum. Would be grateful for advice on whether the following proposal is an acceptable solution or open to any suggestions...
Replies
9
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock