Search for tools and product advice,

Discuss EICR Code C3 Meaning in the UK Electrical Forum area at ElectriciansForums.net

N

NickD

Current GN3 p.80 says C3 means "Improvement required".

Current GN3 p.105, model EICR form, says C3 means "Improvement recommended".

Your thoughts? Bit of a cock-up if you ask me.
 
I haven't got GN3 but well spotted Nick! Quite a difference between 'recommended' and 'required'.

I think it will be 'required' that is incorrect though.. Best practise guide 4 says 'recommended'.
 
My take on this is that GN3 says "additional protection RCD absent where the current regs say it should be present" is a 'classic' C3. But we cannot say that any improvement is required here, because the installation has grandfather rights to be as per the regs on the day it was put in. So a C3 can be no more than a recommendation.
 
When conducting an EICR you do it aginst current regs not regs in-force at the time of installation ...... so if current regs say you should have a thingy and it doesn't have a thingy then it doesn't meet current regs and needs coding. (I dont think there is anything about grandfather rights anywhere?) Whether you code it 1,2 or 3 is down to you as to your view on is it safe/dangerous etc.... using your knowledge/experience of the installation and its use, coupled I would suggest with any guidance from the ESC (or whatever its latest name is!). In your specific example, if you believe no RCD is not dangerous/potentially dangerous in a modern electrical installation (or an old installation being used in a modern electrical environment as opposed to when it was designed) code it C3.
 
When conducting an EICR you do it aginst current regs not regs in-force at the time of installation ...... so if current regs say you should have a thingy and it doesn't have a thingy then it doesn't meet current regs and needs coding. (I dont think there is anything about grandfather rights anywhere?) Whether you code it 1,2 or 3 is down to you as to your view on is it safe/dangerous etc.... using your knowledge/experience of the installation and its use, coupled I would suggest with any guidance from the ESC (or whatever its latest name is!). In your specific example, if you believe no RCD is not dangerous/potentially dangerous in a modern electrical installation (or an old installation being used in a modern electrical environment as opposed to when it was designed) code it C3.

Agreed - and if you think that NO RCD protection throughout is an issue regarding power out in the garden, then you may consider coding it 2 (potentially dangerous regardless of prior regs)
 
Agreed - and if you think that NO RCD protection throughout is an issue regarding power out in the garden, then you may consider coding it 2 (potentially dangerous regardless of prior regs)

And showers with no RCD protection? They worry me no end.
 
An periodic inspection is conducted by considering the current regulations but EICR coding is not to indicate a breach of the current regulations but a situation that may give rise to danger.
If it does not meet the current regulations but it is safe to use then there would be no need to code.
 
C3 cannot mean anything is actually required, because you could be knee deep in C3s and still give it a Satisfactory overall. If it required work it could not be satisfactory. This is logical, Captain.
 
C3 cannot mean anything is actually required, because you could be knee deep in C3s and still give it a Satisfactory overall. If it required work it could not be satisfactory. This is logical, Captain.
it would require work to comply with latest regs though? which you could recommend!!
 
£60 for 7671....£20 for GN's.....amendments aplenty.....AND STILL they can't sort out their ducking typo's!

OP; it's defo the required wording wrong IMO. It's recommended for improvement but not necessarily unsafe as to warrant a Code 2. If it was unsafe then recommended would be required and would be Code 2 not the recommended Code 3 as it would now be required and a Code 2!!
 
Last edited:
£60 for 7671....£20 for GN's.....amendments aplenty.....AND STILL they can't sort out their ducking typo's! OP; it's defo the required wording wrong IMO. It's recommended for improvement but not necessarily unsafe as to warrant a Code 2. If it was unsafe then recommended would be required and would be Code 2 not the recommended Code 3 as it would now be required and a Code 2!!
Hell thats confused me! Do I code 3 if i think it maybe a code 2 just to be safe, but if a code 2 and unsure give it a code 3?
 
Current GN3 p.80 says C3 means "Improvement required".

Current GN3 p.105, model EICR form, says C3 means "Improvement recommended".

Your thoughts? Bit of a cock-up if you ask me.

Well spotted. I would go with recommended as this is what BS7671 says.

I have read through this thread and one or two key points are getting missed.

Someone had said that the EICR is conducted and assessed against the current version of the regs, and this is true.

What the regs say, is that just because an installation was constructed etc to an earlier version of the regs, then this does not deem the installation to be unsafe.

If the installation was constructed to an earlier version, and it is still safe to remain in use, then we can only recommend improvements to it.

What needs to be remembered is that we have never been allowed to install anything dangerous even going back as far as the first edition. the only thing that has changed is the technology, and as this advances then we can recommend improvements to make things safer than it was, and move with the times. all we can say is "The installation is safe, but i can recommend some improvements which will make it safer".

What we can't and mustn't do, is put our opinion on it, we can only state facts,

Cheers........Howard
 
I personally treat it as improvement recommended. always have, always will.
If I think whatever I'm inspecting is 'improvement required' I'd give it a C2
 
When conducting an inspection in accordance with the requirements of BS7672, we are required to note any defects, damage, deterioration or non-compliances which may give rise to danger.
There is no requirement to note something that is not dangerous, or potentially dangerous.
To my mind, code C3 is just there to replace the old Code 4.
 
Stone the crows and f**** the pigs and pass the ammunition...its just semantics and really is not that much of a problem surely sherley...if you take SirKit Breakers analogy -

"The installation is safe, but i can recommend some improvements which will make it safer".
which is no different from....
"The installation is safe, but it requires some improvements which will make it safer".

So you can recommend the improvements or you can say it requires some imrovements....maybe its just me but I cant see what the difference is:)
 
"Mrs Scroggins, your electrics are basically safe, however there are recommendations for improvements" - all is well.

"Mrs Scroggins, your electrics are basically safe, however there are requirements for improvements" - old dear coughs up for them all when she didn't have to and you end up on Rogue Traders.
 
"Mrs Scroggins, your electrics are basically safe, however there are recommendations for improvements" - all is well.

"Mrs Scroggins, your electrics are basically safe, however there are requirements for improvements" - old dear coughs up for them all when she didn't have to and you end up on Rogue Traders.


wow....a breakthrough.

better times ahead Nick?...
 
You can recommend things which aren't required - wise.

You can require things which aren't recommended - unwise.



It's difficult to discuss if you don't know what the words actually mean.
 
"Mrs Scroggins, your electrics are basically safe, however there are recommendations for improvements" - all is well.

"Mrs Scroggins, your electrics are basically safe, however there are requirements for improvements" - old dear coughs up for them all when she didn't have to and you end up on Rogue Traders.

Poor grammar, but i'll go with it just to help poor old Mrs Scroggins.....:)

......however there are recommendations for improvements"
.....however there are requirements for improvements"
requirements is not the same as requires..requirements insinuates some sort of Regulatory thing.

If it said "I recommend that an RCD be installed to meet current Regulations" or "an RCD is required to meet current Regulations" whats the difference.....maybe certain words have more power to certain people.....Requirements has more power, and is a word used in the same context as "compliance" etc.....requires and requirement can mean completely different things...in legalese "may" is synonymus with "must" and may or must be read as such:freak:
 
You can recommend things which aren't required - wise.

You can require things which aren't recommended - unwise.



It's difficult to discuss if you don't know what the words actually mean.

also;
you can recommend things which are recommeneded, and
you can require things which arent requirements

Its really about context, not miss-understanding what a word means:)
 
Last edited by a moderator:
If you recommend something that will make the installation safer, it suggests that there is a potential for danger present. In other words, a code C2.

I see what you are saying Spin but according to ESC BPG the lack of a old-new colours sticker is a Code 3..... I would not really classify that as there being a potential for danger and could never Code 2 it....even find a Code 3 a lil over zealous TBH. My thought would be if that you cannot distiguish between black/blue and red/brown then you should nae be tinkering.

As you say, Code 2 is for things that could become dangerous; a regularly used DSO with only one (loose) 3.5mm machine screw perhaps...
 
If you recommend something that will make the installation safer, it suggests that there is a potential for danger present. In other words, a code C2.

It suggests you've identified a risk and can recommend a way to mitigate it, it doesn't necessarily suggest potential for danger. IMHO Danger = a risk of injury or damage that is either unacceptably likely to happen, or unacceptably severe in its outcome if it does happen, or both. Or something like that.
 
Again.
We are required to report on defects, deterioration, damage, dangerous conditions and non-compliance with the Regulations which may give rise to danger.
There is no requirement to report on anything else.
 
But further to those requirements we may note and report on improvements, otherwise they would not have provided code C3. Indeed the existence of code C3 suggests we are recommended to do so. :)
 
But further to those requirements we may note and report on improvements, otherwise they would not have provided code C3. Indeed the existence of code C3 suggests we are recommended to do so. :)

a 3s got sod all to do with being `recommended to report on anything you find`.....

its about identifying non-conformances that neither pose an immediate danger...nor a danger due to fault conditions...

you record on what your findings are by making note/s...together with alloting the neccessary codes should they warrent it....regardless of whether its Mrs. Brady old lady..

or professor plumb with his millions and numerous rolls/bentley`s etc...
 
Fair point. All I was trying to say is that we don't only report on stuff that does/could give rise to danger, which is what spin seemed to be suggesting (well alright what he said was that that was all we were required to report). I'm not suggesting C3 is for reporting any bell bang or whistle we might think of. Cos it isn't.
 
If you report on conditions which you are not required to report on, can you then declare that the report has been compiled in accordance with BS7671?

GN3 says C3 is for where C1 and C2 do not apply, so where danger is neither present nor potential. C3 is obviously there to be used, and so a report using it to correctly record noncompliance that is neither dangerous nor potentially dangerous is in accordance with GN3?
 
Interesting arguements showing what we all know, BS7671 and its phletero of supporting documentation is contradictory and open to interpretation. As I read it .....

BS7671, GN3 and the ECS guide (all linked into the IET!) require that defects etc ... that give rise to danger or may give rise to danger should be recorded during an inspection --- for me these are the clear C1 ( Danger present do something immediate about it) and C2 (Potentially dangerous do something urgently about it) codes. The ambiguity then starts around the C3 code and does it just apply to just danger/potential danger or not.

BS7671 doesn't give a clear definition but in its model form (EICR) it suggests that "observations" classifed as "improvement recommended" be C3. I interpret that as being the "observation" isn't dangerous or you would have coded C1 or C2. It doesn't define exactly what you should record as an 'observation' however.
GN3 then describes the new codes as being for "danger and non-compliances to BS7671". It defines C3 as "to be cited where C1 or C2 do not apply" I interpret this as meaning these codes (C1 & C2) apply to danger and the (C3) to non-compliances to BS7671. This then leads me to think that the 'observations' to be recorded on the EICR under BS7671 are for non-compliances to BS761 which are then coded for danger (C1 & C2) or improvement (C3).
ESC publication informs us "BS7671 no longer requires departures from the current edition of BS7671 that do not give rise to danger or require improvement be included in condition reports". Again I interpret this as meaning 'observation' on the EICR should not only cover the "give rise to danger" (C1 & C2) but also the "require improvement" (C3) to BS7671 angle. It then gives specific example of where the C3 codes could be applied. e.g. Lack of RCD protection is a C3 -- not dangerous or potentially dangerous or we would be condeming all 3036 boards but certainly a recommendation for upgrade to improve safety. It also gives some examples of where it recommends departures from BS7671 as not recorded. e.g. inadequate cross-sectional area of main protective bonding conductors, provided certain conditions are met!

My interpretation of the whole mish mash is that you conduct an inspection, EICR or whatever you want to call it, against the current BS7671 and record all departures from BS7671 as "Observations", not just those dangerous/potentially dangerous. Using your engineering judgement you then code these "Observations" C1/C2/C3 depending on how you assess them. If in doubt there is some clear guidance from the ESC as to what codes apply and where -- plus what observations shouldn't even be recorded.

Ultimately though this is my interpretation and I'm risk adverse so I like to cover my 'butt' by including as much as I can. A code 3 doesn't give an "unsatisfacory" EICR but highlights to the client what I consider to be safety improvements "recommended". If they don't want to do anything about them that's their call but I feel I've done my bit and advised them against current regulations!.

If granny gets a 400V shock through her pinny whilst stood in the pond using the electric mower outside from a "Y" adaptor plugged into the kitchen light because the 3036 nail didn't "melt", don't come looking at me, I recommended you upgrade to an RCD ...... (stretched I know but hopefully you get the point!)
 
If you look in the OSG and GN3, C3 is also to be applied to installations constructed to an earlier edition of BS7671, OSG APP G 3.2 pg. 153, and GN3 3.12 pg. 80, if the departure warrants an improvement recommendation, otherwise no code.
 
Though it also opens up another arguement that if it doesn't conform to BS7671 why wouldn't you automatically C3 it rather than not record it?

I know the ESC doc gives examples of this (e.g. the bonding) but if for example BS7671 is recommending 10mm for that particular application and you've got 6mm wouldn't it be an improvement to replace a 6mm with 10mm even if there isn't signs of thermal overload etc .....
 
If you look in the OSG and GN3, C3 is also to be applied to installations constructed to an earlier edition of BS7671, OSG APP G 3.2 pg. 153, and GN3 3.12 pg. 80, if the departure warrants an improvement recommendation, otherwise no code.

Exactly, in the guidance on the forms it specifically says they expect to see a C3 coding minimum for absence of RCDs where they should be present by current regs - specific requirement to record a (probably) non-danger situation with a C3. Ergo we are not required only to report on danger.
 
Last edited by a moderator:
Exactly, in the guidance on the forms it specifically says they expect to see a C3 coding minimum for absence of RCDs where they should be present by current regs - specific requirement to record a (probably) non-danger situation with a C3. Ergo we are not required only to report on danger.
eh?

visual + test/s will/should confirm whether danger is present or not...either immediate or under fault conditions...if it is..then it aint a 3....is it.
 
To simplify definitions a bit,try looking at it this way in law when something is compulsory they use the word required,not recommended,as in the law requires you to wear a seat belt when in a motor vehicle,so from my point of view if something says requires then implies
that it needs to be done not that you may want to think about doing it.As other have said they need to decide on what they mean
 

Reply to EICR Code C3 Meaning in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hello, I had an eicr done in 2021and it passed with four C3 items. They recommend next test date to be in 3 years instead of 5 on the certificate...
Replies
15
Views
1K
Another thread asked about two circuits sharing a common multi-core cable and regulation 521.8.1 was mentioned. A friend of mine has inherited...
Replies
13
Views
704
Trying to organise a CU replacement at home. It's a 1930s property. It's got a 10way CU but with no RCD protection. Was after a larger unit with...
Replies
65
Views
4K
Just had an EICR done and C2 (dangerous) applied to 3-way consumer unit which is exclusively for 3 x Storage Heaters. Pic below. Yes its plastic...
Replies
24
Views
2K
I have been asked to look at this report as the customer has been given (in their words) 'A very high quote plus VAT'. It doesn't look well...
Replies
5
Views
674

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock