  1. 9regnac
    Offline

    9regnac Regular EF Member

    House has singles with Conduit acting as cpc. All fittings are class 2. r2 tested perfect. Code 3?
     
  2. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    C3 = improvement recommended So what improvement are you recommending?

    Based on the information provided I cannot see anything that requires a code
     
    • Like Like x 1
  3. rattlehead85
    Offline

    rattlehead85 Electrician's Arms

    Certainly no code should be attributed to that. Conduit can be used as cpc so long as it tests out and shows no signs of corrosion or damp penetration.
     
  4. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    Plus of course it needs to meet the minimum csa requirement as calculated using the adiabatic equation.
     
  5. rattlehead85
    Offline

    rattlehead85 Electrician's Arms

    20mm /25mm conduit tends to be the norm on domestic lighting so is ok normally.
     
  6. Flanders
    Offline

    Flanders Regular EF Member

    Location:
    Tamworth
    As all above if good earth continuity throughout then no code .was the IR results ok
     
    Last edited: Jan 13, 2016
  7. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    It's almost always fine for any circuit, but worth mentioning that it needs checking.
    A lot of the steel conduits in domestic installs will be imperial 3/4" and 5/8" rather than metric.
     
    • Like Like x 1
  8. rattlehead85
    Offline

    rattlehead85 Electrician's Arms

    The only thing i will add and have seen so many times is to make sure if the conduit is buried within the building structure any class 1 fittings are securely earth tagged to the conduit back box behind. Seen lots if people fit metal light fittings over the top of the back box and then don't earth the fitting!!
     
    • Like Like x 1
  9. Flanders
    Offline

    Flanders Regular EF Member

    Location:
    Tamworth
    Yes ive seen yhat too but Should be ok in this case , the op said they were all class 2 lights
     
  10. mrloy99
    Offline

    mrloy99 Regular EF Member

    i think you might need to put a sticker on the DB warning the user not to change fittings to class 1 in the future and an observation on the sheet to the same effect
     
  11. AndyL
    Offline

    AndyL Electrician's Arms

    Would only need to do this if the conduit is not suitable as a cpc which doesn't seem to be the case
     
  12. davesparks
    Offline

    davesparks Trusted Advisor

    Location:
    guildford
    Why when there is a cpc automatically present at every point in a steel conduit installation?
     
    • Like Like x 1
Loading...
Similar Threads - Eicr coding Forum Date
EICR coding for transportable unit Periodic Inspection Reporting & Certification Sep 24, 2018
Burnt out ballast EICR Coding Periodic Inspection Reporting & Certification Aug 20, 2018
Thread Status:
Not open for further replies.

Share This Page

Electricians Directory Post a Domestic Job Post a Commercial Job