Discuss Eicr coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Certainly no code should be attributed to that. Conduit can be used as cpc so long as it tests out and shows no signs of corrosion or damp penetration.
 
The only thing i will add and have seen so many times is to make sure if the conduit is buried within the building structure any class 1 fittings are securely earth tagged to the conduit back box behind. Seen lots if people fit metal light fittings over the top of the back box and then don't earth the fitting!!
 
i think you might need to put a sticker on the DB warning the user not to change fittings to class 1 in the future and an observation on the sheet to the same effect
 
i think you might need to put a sticker on the DB warning the user not to change fittings to class 1 in the future and an observation on the sheet to the same effect
Would only need to do this if the conduit is not suitable as a cpc which doesn't seem to be the case
 

Reply to Eicr coding in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Have been asked to do remedials on an EICR that was carried out a year or so ago by another electrician. Curious to know what code you would give...
Replies
12
Views
1K
Hi guys Completed an EICR yesterday. One of the Sockets Radials had no CPC so R1+R2 plus Zs could not be not be completed. Does anyone know the...
Replies
14
Views
605
EICR picked up no continuity on cpc on 3 pendants fittings in a grd Floor Flat. Zs measured @ other pendants & complies. Different opinions on the...
Replies
8
Views
428
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
859
I trained as a electrician in the 70s but have long since retired. Just had an EICR test done on my property in advance of selling. I have a 60s...
Replies
25
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock