Hi,

A friend of mine owns a small unit, i have the papers from when it was last tested 10 years ago and also 15 years ago, but a lot of its been pulled out since then.

Ill be honest, I do not generally do periodics on this type of building and would like a bit of guidance.

I know how to test the circuits etc, its not that, thats the issue, its more with the BS number and what other peoples thoughts are for the setup where the board is really.

Take a look at the photos and see what you think, its a courier business and they wash vans out the front and take extensions out, nothing is RCD protected, generally the condition looks ok having walked round it yesterday.

2014-09-17 15.16.32.jpg2014-09-17 15.17.26.jpg2014-09-17 15.14.47.jpg2014-09-17 15.11.15.jpg
2014-09-17 15.11.08.jpg2014-09-17 15.09.53.jpg2014-09-17 15.12.52.jpg2014-09-17 15.12.38.jpg
2014-09-17 15.11.20.jpg2014-09-17 15.14.53.jpg
 
BS3036 for all the fuse wire carriers
BS5419 for the main switch in the single phase board

The DB could ideally not do to be half in and out the ceiling but you have proved it is accessible. C3 for ease of access and working space for DB possibly.

I would C2 the lack of RCD on sockets used outside with water jets. A simple RCD socket installed for this use is an easy remedy.

I'm now going to sit back and wait for the inevitable argument about the dangers of asbestos flash pads... on which subject I have no opinion to offer ... lol .. :p
 
Thanks Andy, I agree with your comments, yes the board and floor in the way has been there dined it was built. I said it would be nice to bung a nice shiny new board in but they didn't want it.

the rcd issue, I said I could swap them for protected ones.

the asbestos, I guess it's a C3.
 
Thanks Andy, I agree with your comments, yes the board and floor in the way has been there dined it was built. I said it would be nice to bung a nice shiny new board in but they didn't want it.

the rcd issue, I said I could swap them for protected ones.

the asbestos, I guess it's a C3.

It's a nothing on your report.... You are reporting on the electrical safety of the installation and it's suitability for continued use. Any deterioration or defects can be brought into your report, but not the suitability of materials that have no mention in BS7671. You have to justify any code with a relevant regulation.

I do not know enough about asbestos to advise you any better than this..... The white asbestos flash pads in the main DB are, as I understand it, of a low risk but still "potentially" harmful.
You could put a note on your report to the effect that the client may want to carry out their own asbestos report .... merely as an arse covering operation for yourself mind you.
 
Any 3 phase equipment fed off that Bill Board? If so each phase is individually fused which is a no-no. Will need changing so the phases on that circuit are linked i.e. 3-pole mcb.
 
Any 3 phase equipment fed off that Bill Board? If so each phase is individually fused which is a no-no. Will need changing so the phases on that circuit are linked i.e. 3-pole mcb.

Where the heck do you get that one from?.........baffles me, at times.
 
Any 3 phase equipment fed off that Bill Board? If so each phase is individually fused which is a no-no. Will need changing so the phases on that circuit are linked i.e. 3-pole mcb.

I call bovine excrement! Unless of course you can quote a law or regulation to support that theory.
 
Ok I always thought machinery, especially rotating (motors etc) should drop all three phases if one phase drops out (unless the machinery itself has this type of protection, eg. undervoltage trip).

This is to prevent harm to operators but mainly to protect the equipment itself. If this is so wrong how come 3-pole mcb's are interlinked?

Teach me people :)
 
You havent done much industrial work, so clearly havent seen that very many installs still have fuses for fault and overload protection.
Fuses are quite good at not tripping with short term overloads, so are still specified for some equipment where a circuit breaker may trip earlier, and / or cannot achieve the required Zs figures.

It isnt wrong to have 3 phase CB's interlinked, it's a good thing for isolation, but if they are not interlinked, at most it is only a C3 on an EICR.
Clearly some equipment calls for all phases to be isolated at the same time, so manufacturers rules should be followed too.
 
Ok I always thought machinery, especially rotating (motors etc) should drop all three phases if one phase drops out (unless the machinery itself has this type of protection, eg. undervoltage trip).

This is to prevent harm to operators but mainly to protect the equipment itself. If this is so wrong how come 3-pole mcb's are interlinked?

Teach me people :)

The motor overload relay in the starter will handle that, the supply to the starter will be quite happy on fuses.
 
Well I did my time years ago at Kier Sheffield, mainly domestic (decent homes scheme house bashing), but also worked on fire alarms, door entry systems etc. We did some small to medium commercial stuff which is my experience of 3 phase.

Generally it was new build so no existing older installs seen. Judging by my MISTAKEN initial post in this thread you can see I haven't had any experience with Industrial installs. Anyway a few of my mentors on commercial jobs ('experienced' time served sparks) would always suggest 3 pole mcb's for safer isolation on 3 phase systems. Their words repeated by me. Never seen a switch fuse feed a final circuit directly, only to feed sub boards generally from a bus bar chamber.

As always in this game I'm still learning, I have no desire to do Industrial and only stick to light modern commercial and domestic. I guess due to larger in-rush currents and high kilowatt machinery mcb's aren't practical compared to BS 88 fuses (etc). Basically what Alanl said in #15.
 

Reply to EICR On small industrial unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been asked to quote an EICR on a fairly large installation. Approx. 400 circuits that are a mixture of single and 3 phase. This is across...
Replies
22
Views
3K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
3K
Hi everyone! Im not an electrician but just a guy looking for a possible answer before I call my electricity supplier. Every month without fail...
Replies
11
Views
2K
Hi All, I am in the middle of purchasing a small 1 bed flat in England, and have been sent a Domestic Electrical Installation Certificate by the...
Replies
1
Views
1K
Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock