Hi,

A friend of mine owns a small unit, i have the papers from when it was last tested 10 years ago and also 15 years ago, but a lot of its been pulled out since then.

Ill be honest, I do not generally do periodics on this type of building and would like a bit of guidance.

I know how to test the circuits etc, its not that, thats the issue, its more with the BS number and what other peoples thoughts are for the setup where the board is really.

Take a look at the photos and see what you think, its a courier business and they wash vans out the front and take extensions out, nothing is RCD protected, generally the condition looks ok having walked round it yesterday.

2014-09-17 15.16.32.jpg2014-09-17 15.17.26.jpg2014-09-17 15.14.47.jpg2014-09-17 15.11.15.jpg
2014-09-17 15.11.08.jpg2014-09-17 15.09.53.jpg2014-09-17 15.12.52.jpg2014-09-17 15.12.38.jpg
2014-09-17 15.11.20.jpg2014-09-17 15.14.53.jpg
 
BS3036 for all the fuse wire carriers
BS5419 for the main switch in the single phase board

The DB could ideally not do to be half in and out the ceiling but you have proved it is accessible. C3 for ease of access and working space for DB possibly.

I would C2 the lack of RCD on sockets used outside with water jets. A simple RCD socket installed for this use is an easy remedy.

I'm now going to sit back and wait for the inevitable argument about the dangers of asbestos flash pads... on which subject I have no opinion to offer ... lol .. :p
 
Thanks Andy, I agree with your comments, yes the board and floor in the way has been there dined it was built. I said it would be nice to bung a nice shiny new board in but they didn't want it.

the rcd issue, I said I could swap them for protected ones.

the asbestos, I guess it's a C3.
 
Thanks Andy, I agree with your comments, yes the board and floor in the way has been there dined it was built. I said it would be nice to bung a nice shiny new board in but they didn't want it.

the rcd issue, I said I could swap them for protected ones.

the asbestos, I guess it's a C3.

It's a nothing on your report.... You are reporting on the electrical safety of the installation and it's suitability for continued use. Any deterioration or defects can be brought into your report, but not the suitability of materials that have no mention in BS7671. You have to justify any code with a relevant regulation.

I do not know enough about asbestos to advise you any better than this..... The white asbestos flash pads in the main DB are, as I understand it, of a low risk but still "potentially" harmful.
You could put a note on your report to the effect that the client may want to carry out their own asbestos report .... merely as an arse covering operation for yourself mind you.
 
Any 3 phase equipment fed off that Bill Board? If so each phase is individually fused which is a no-no. Will need changing so the phases on that circuit are linked i.e. 3-pole mcb.
 
Any 3 phase equipment fed off that Bill Board? If so each phase is individually fused which is a no-no. Will need changing so the phases on that circuit are linked i.e. 3-pole mcb.

Where the heck do you get that one from?.........baffles me, at times.
 
Any 3 phase equipment fed off that Bill Board? If so each phase is individually fused which is a no-no. Will need changing so the phases on that circuit are linked i.e. 3-pole mcb.

I call bovine excrement! Unless of course you can quote a law or regulation to support that theory.
 
Ok I always thought machinery, especially rotating (motors etc) should drop all three phases if one phase drops out (unless the machinery itself has this type of protection, eg. undervoltage trip).

This is to prevent harm to operators but mainly to protect the equipment itself. If this is so wrong how come 3-pole mcb's are interlinked?

Teach me people :)
 
You havent done much industrial work, so clearly havent seen that very many installs still have fuses for fault and overload protection.
Fuses are quite good at not tripping with short term overloads, so are still specified for some equipment where a circuit breaker may trip earlier, and / or cannot achieve the required Zs figures.

It isnt wrong to have 3 phase CB's interlinked, it's a good thing for isolation, but if they are not interlinked, at most it is only a C3 on an EICR.
Clearly some equipment calls for all phases to be isolated at the same time, so manufacturers rules should be followed too.
 
Ok I always thought machinery, especially rotating (motors etc) should drop all three phases if one phase drops out (unless the machinery itself has this type of protection, eg. undervoltage trip).

This is to prevent harm to operators but mainly to protect the equipment itself. If this is so wrong how come 3-pole mcb's are interlinked?

Teach me people :)

The motor overload relay in the starter will handle that, the supply to the starter will be quite happy on fuses.
 
Well I did my time years ago at Kier Sheffield, mainly domestic (decent homes scheme house bashing), but also worked on fire alarms, door entry systems etc. We did some small to medium commercial stuff which is my experience of 3 phase.

Generally it was new build so no existing older installs seen. Judging by my MISTAKEN initial post in this thread you can see I haven't had any experience with Industrial installs. Anyway a few of my mentors on commercial jobs ('experienced' time served sparks) would always suggest 3 pole mcb's for safer isolation on 3 phase systems. Their words repeated by me. Never seen a switch fuse feed a final circuit directly, only to feed sub boards generally from a bus bar chamber.

As always in this game I'm still learning, I have no desire to do Industrial and only stick to light modern commercial and domestic. I guess due to larger in-rush currents and high kilowatt machinery mcb's aren't practical compared to BS 88 fuses (etc). Basically what Alanl said in #15.
 
Well I did my time years ago at Kier Sheffield, mainly domestic (decent homes scheme house bashing), but also worked on fire alarms, door entry systems etc. We did some small to medium commercial stuff which is my experience of 3 phase.

Generally it was new build so no existing older installs seen. Judging by my MISTAKEN initial post in this thread you can see I haven't had any experience with Industrial installs. Anyway a few of my mentors on commercial jobs ('experienced' time served sparks) would always suggest 3 pole mcb's for safer isolation on 3 phase systems. Their words repeated by me. Never seen a switch fuse feed a final circuit directly, only to feed sub boards generally from a bus bar chamber.

As always in this game I'm still learning, I have no desire to do Industrial and only stick to light modern commercial and domestic. I guess due to larger in-rush currents and high kilowatt machinery mcb's aren't practical compared to BS 88 fuses (etc). Basically what Alanl said in #15.
yeah we had to reconnect, test and comission a boiler house before.

because of the way the panels are we were getting readings too high for 60898 breakers so it went on test sheet as recommended swapping to bs88 (was the overloads causing it because of the dol starters)
 
yeah we had to reconnect, test and comission a boiler house before.

because of the way the panels are we were getting readings too high for 60898 breakers so it went on test sheet as recommended swapping to bs88 (was the overloads causing it because of the dol starters)

I'm getting lost again, here.....what and where did you test?
 
yeah we had to reconnect, test and comission a boiler house before.

because of the way the panels are we were getting readings too high for 60898 breakers so it went on test sheet as recommended swapping to bs88 (was the overloads causing it because of the dol starters)

Something smells a bit fishy here, how were the overloads having an impact on the supply MCBs ?
And why are you using 60898 (domestic) MCBs for a boiler house? Should they not be 60947s
 
Something smells a bit fishy here, how were the overloads having an impact on the supply MCBs ?
And why are you using 60898 (domestic) MCBs for a boiler house? Should they not be 60947s
the overloads were after the mcb's in the panel then out to the triacs then boilers i didnt check the breaker type i posted 60898's simply so you guys knew they were breakers
 
Something smells a bit fishy here, how were the overloads having an impact on the supply MCBs ?
And why are you using 60898 (domestic) MCBs for a boiler house? Should they not be 60947s
Why? How many 'd' type TP 60898 breakers, for example, have you seen in a house?
 
Why? How many 'd' type TP breakers have you seen in a house?

What on earth has that got to do with it? Any TP d type breaker you buy will be built to 60947, but will also, almost inherently, comply with 60898.
The point is that a breaker which complies with only 60898 is only intended for domestic use whereas a breaker built to both standards or just 60947 is suitable for all.
 
What on earth has that got to do with it? Any TP d type breaker you buy will be built to 60947, but will also, almost inherently, comply with 60898.
The point is that a breaker which complies with only 60898 is only intended for domestic use whereas a breaker built to both standards or just 60947 is suitable for all.

I would imagine that in a boiler house control panel they would have been built to spec. with 60898 labelled.
 
What on earth has that got to do with it? Any TP d type breaker you buy will be built to 60947, but will also, almost inherently, comply with 60898.
The point is that a breaker which complies with only 60898 is only intended for domestic use whereas a breaker built to both standards or just 60947 is suitable for all.

Is it always as clear cut as that Dave ? I have in front of me for example a 40A TP MCB, C curve, 10kA rated that states BS EN 60898 only. Would that have been produced with domestic application in mind ?

Not trying to be tetchy or argumentative mind, just expanding my knowledge
 
Is it always as clear cut as that Dave ? I have in front of me for example a 40A TP MCB, C curve, 10kA rated that states BS EN 60898 only. Would that have been produced with domestic application in mind ?

Not trying to be tetchy or argumentative mind, just expanding my knowledge
why does it need to comply if 10ka rating is satisfactory why do you need 15ka mcbs
 
Is it always as clear cut as that Dave ? I have in front of me for example a 40A TP MCB, C curve, 10kA rated that states BS EN 60898 only. Would that have been produced with domestic application in mind ?

Not trying to be tetchy or argumentative mind, just expanding my knowledge

BS EN 60898 'low voltage circuit breakers for use in household and similar applications'

BS EN 60947-2 'low voltage circuit breakers for use in industrial and similar installations'

So it all depends on how you define 'similar installations' , I think small commercial offices/shops would be, but what else?
 
BS EN 60898 'low voltage circuit breakers for use in household and similar applications'

BS EN 60947-2 'low voltage circuit breakers for use in industrial and similar installations'

So it all depends on how you define 'similar installations' , I think small commercial offices/shops would be, but what else?
in this paticular case bs60898 breakers are adequite because of the enviroment conditions and measured test results (its located in a school)

b236eae01c135e6c6157c47fbc8fe137.jpg
 
BS EN 60898 'low voltage circuit breakers for use in household and similar applications'

BS EN 60947-2 'low voltage circuit breakers for use in industrial and similar installations'

So it all depends on how you define 'similar installations' , I think small commercial offices/shops would be, but what else?

Cheers for that Dave. First time I have heard 60898 referred to as "household" , that's what confused me.
I found this download for some informative bedtime reading ...

http://www.beama.org.uk/download.cfm/docid/6BCA1329-8A17-4C89-B86A629F18D74BB8
 
in this paticular case bs60898 breakers are adequite because of the enviroment conditions and measured test results (its located in a school)

]

You're lucky, all the school/commercial boiler rooms I get to work in around here are grotty horrible places, damp and stinking of oil. You'd assume the higher pollution rating to be specified for them.
 
You're lucky, all the school/commercial boiler rooms I get to work in around here are grotty horrible places, damp and stinking of oil. You'd assume the higher pollution rating to be specified for them.
nah the worst plant room ive worked in was city hospital in birmingham.

national grid officess plantrooms are defiantly the cleanest ive been to.

the breakers are usuallu dual standard but usually the older plant we work on is bs88 fuses
 

Reply to EICR On small industrial unit in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, Been asked to quote an EICR on a fairly large installation. Approx. 400 circuits that are a mixture of single and 3 phase. This is across...
Replies
22
Views
3K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
4K
Good morning, We have a two-bedroom flat that my wife and I rent out to supplement our income. Following the recent EICR, several issues...
Replies
42
Views
2K
Hi everyone! Im not an electrician but just a guy looking for a possible answer before I call my electricity supplier. Every month without fail...
Replies
11
Views
2K
Hi All, I am in the middle of purchasing a small 1 bed flat in England, and have been sent a Domestic Electrical Installation Certificate by the...
Replies
1
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock