^^^ I am looking at the pair of your comments. IMO my 2 pence worth if an EICR has been carried out, and lets say c1 for x c2 for y has been recorded, and remedial work has been carried out to correct the installation with paper work ie MWC, then in my mind that would go hand in hand with the previous EICR end off.
 
^^^ I am looking at the pair of your comments. IMO my 2 pence worth if an EICR has been carried out, and lets say c1 for x c2 for y has been recorded, and remedial work has been carried out to correct the installation with paper work ie MWC, then in my mind that would go hand in hand with the previous EICR end off.
Yes, that should by rights be the case.
But what if that work isn’t done for 6 years?
 
what a farce ........... nobody can agree ............ but thing is for sure, and based on personal experience......... handing an unsatisfactory EICR and a couple of MWC's to a letting agent doesn't always guarantee they will "accept" that the installation is now "satisfactory"
 
what a farce ........... nobody can agree ............ but thing is for sure, and based on personal experience......... handing an unsatisfactory EICR and a couple of MWC's to a letting agent doesn't always guarantee they will "accept" that the installation is now "satisfactory"

To be fair it is only one member that seems to not understand how it should work.
 
Only for that item of work. Not the whole installation.
Judging from your comments regarding clients wanting a report to state ‘Satisfactory”, I can only assume you rarely conduct periodic Inspection and Testing.
In my experience which dates back to before the IEE/IET introduced the model forms, the majority of installations which require the client to obtain a report, would not willingly accept a report which states ‘Unsatisfactory’.

Personally, before completing and issuing a report, I will inform the client of the defects I have found, and offer to rectify those defects, in order to issue a ‘Satisfactory’ report.

Others will issue the report, offer to rectify the defects and also offer to issue another ‘Satisfactory’ report once the work is completed.

Others still will attend a property to Inspect, rectify any faults, not issue any certification for their work, make no notification and then issue a Visual.
 
Judging from your comments regarding clients wanting a report to state ‘Satisfactory”, I can only assume you rarely conduct periodic Inspection and Testing.
In my experience which dates back to before the IEE/IET introduced the model forms, the majority of installations which require the client to obtain a report, would not willingly accept a report which states ‘Unsatisfactory’.

Personally, before completing and issuing a report, I will inform the client of the defects I have found, and offer to rectify those defects, in order to issue a ‘Satisfactory’ report.

Others will issue the report, offer to rectify the defects and also offer to issue another ‘Satisfactory’ report once the work is completed.

Others still will attend a property to Inspect, rectify any faults, not issue any certification for their work, make no notification and then issue a Visual.

We do more than enough. Regardless of how many we do my ability to understand and read basic guidance is not linked with how many I carry out.

Experience means nothing if during that time you were doing it incorrectly.
 
If you do more than enough, how is it you are unaware of the widespread demand for ‘Satisfactory’ reports?
I’ve spoken to Insurance companies on a number of occasions regarding this issue, not always successfully.
Client has had an ‘Unsatisfactory’ report, had the work done to rectify the defects, the Insurance company wants a new ‘Satisfactory’ report.
 
If you do more than enough, how is it you are unaware of the widespread demand for ‘Satisfactory’ reports?
I’ve spoken to Insurance companies on a number of occasions regarding this issue, not always successfully.
Client has had an ‘Unsatisfactory’ report, had the work done to rectify the defects, the Insurance company wants a new ‘Satisfactory’ report.

Maybe you do not educate your clients as well as I do. I do about £50k worth of EICRs a year and never have the issue you describe.
 
might get some from SWD, now he's gender neutral. :eek::eek::eek:.
 
The last EICR I did was an unsatisfactory based on inadequate sized main earth and Equipotential bonding. A simple fix as it was all in a cellar.

Problem is that the customer decided to DIY the upgrade himself - and I never went back. So he (maybe) has ‘satisfactory’ Installation but an unsatisfactory report. He was the land lord of this rented property as well - so I wonder how he would get on with the insurers?

It’s all a bit of a minefield?
 
The last EICR I did was an unsatisfactory based on inadequate sized main earth and Equipotential bonding. A simple fix as it was all in a cellar.

Problem is that the customer decided to DIY the upgrade himself - and I never went back. So he (maybe) has ‘satisfactory’ Installation but an unsatisfactory report. He was the land lord of this rented property as well - so I wonder how he would get on with the insurers?

It’s all a bit of a minefield?

It is really not a minefield. It is very very simple.

The insurer would probably not accept anyone not a member of a scheme carrying out the works.
 
The last EICR I did was an unsatisfactory based on inadequate sized main earth and Equipotential bonding. A simple fix as it was all in a cellar.

Problem is that the customer decided to DIY the upgrade himself - and I never went back. So he (maybe) has ‘satisfactory’ Installation but an unsatisfactory report. He was the land lord of this rented property as well - so I wonder how he would get on with the insurers?

It’s all a bit of a minefield?

Not your problem .............
 
If a report is unsatisfactory there will be a list of observations , If those observations have been rectified there will be paper work to show that ,
We produce a spread sheet listing them so its easy to cross referance .we have done doing this for years and all our customers find it easy to understand for example
Item ................Observation .............. Action carried out ............Results
1 . Broken socket in reception ...........Replaced socket...........0.45

Just a ruff example we put all relevant test reading depending on what work carried out.
 
How about doing the appropriate certificate for the remedial work plus an EICR with detailed limitations referenced to a copy of the unsatisfactory report?
An EICR has already be done so the condition of the installation has been reported there is no requirement to carry out another EICR untill the current one is out of date
 
I realise that but if the customer is not happy with certs and want another EICR... but then how many clients actually know what they are asking for?
 
What certification would be issued for replacing a broken socket front or switch plate?
How about a missing MCB blank?
Missing cover for a CU?
Switching over cables on incorrectly labelled circuits?
Replacing a socket with a blanking plate?
 
What certification would be issued for replacing a broken socket front or switch plate?
How about a missing MCB blank?
Missing cover for a CU?
Switching over cables on incorrectly labelled circuits?
Replacing a socket with a blanking plate?
No cert I just send them a signed document listing these items and stating what has been done to recticy them with any releveant test results
 
What certification would be issued for replacing a broken socket front or switch plate?
How about a missing MCB blank?
Missing cover for a CU?
Switching over cables on incorrectly labelled circuits?
Replacing a socket with a blanking plate?

A MWC.

Again; it is really very simple.
 

Reply to EICR rectifications completed by another electrician, what now? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

4mm T&E circuits on 32amp breaker. Parts of the circuit run through ceiling, parts through trunking and possibly even the wall. Current carrying...
Replies
6
Views
981
So I've recently had an EICR for my building. Came back with about 20 odd C2 remedials and a few F1's which resulted in UNSATISFACTORY being...
Replies
5
Views
1K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
987
Hi, I have just had an EICR carried out and it has comeback with a few C2s. The only one I disagree with is the electrician raised as a C2 the...
Replies
10
Views
2K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock