I don’t know what kind of reports you issue but the ones we issue clearly state a next inspection due date that is dependant on all C1 and C2 remedials being repaired urgently.

An unsatisfactory EICR is still signed off generally for 5/10 years. Subject to remedial works being completed.
So do your reports that list code C1 and code C2 observations, say Satisfactory or Unsatisfactory?
 
So how does it become Satisfactory?
Does the client erase ‘Un”?
Do you issue a new report?
Is it by magic?

It is really very very simple. The installation becomes satisfactory following an unsatisfactory report issued on the day of the inspection and a paper trail evidencing that the remedials have been carried out in good time.

You are either trolling (which is not even good trolling) or you are desperatly trying to justify your business model of carrying out unnecessary EICRs.
 
It is really very very simple. The installation becomes satisfactory following an unsatisfactory report issued on the day of the inspection and a paper trail evidencing that the remedials have been carried out in good time.

You are either trolling (which is not even good trolling) or you are desperatly trying to justify your business model of carrying out unnecessary EICRs.
What I’m trying to do, is work out what it is you are saying.
Because you’re about as clear as mud.

Now I have already posted that where an EICR is Unsatisfactory, appending certificates for the remedial work required, should be all that is required.
Now if you wish to disagree with that, or you consider it to be trolling, then please explain why.

However appending certification does not magically make the EICR Satisfactory. The EICR is still Unsatisfactory.

My business model is such, that if a client now requires me to alter the EICR from Unsatisfactory, to Satisfactory, I will refuse.
I would be willing to re-inspect the Installation and issue a new EICR, which may or may not be Satisfactory.

From personal experience, I have seen remedial work carried out which resulted in the upstairs and downstairs RFCs being terminated into each other’s MCBs.
Now some may consider incorrect labelling as a code C3.
However as the Consumer Unit is intended to be used by ordinary persons (i.e. non-competent, non-trained, non-skilled, etc.) I consider a code C2 to be applicable.
In any event whichever code applies, it will not have been recorded on the unsatisfactory EICR.

If you find it reprehensible that I am not prepared to state an installation will be Satisfactory for x amount of years, if the listed C1 and C2 observations are rectified by others, without first inspecting the work, you are nuts.

I also think, that you’re nuts for being willing to effectively guarantee other’s work for x amount of years, without first inspecting that work.

Of course, if you are not saying such, then explain just what it is you are saying.
Try to be clear and effective in your explanation.
 
What I’m trying to do, is work out what it is you are saying.
Because you’re about as clear as mud.

Now I have already posted that where an EICR is Unsatisfactory, appending certificates for the remedial work required, should be all that is required.
Now if you wish to disagree with that, or you consider it to be trolling, then please explain why.

However appending certification does not magically make the EICR Satisfactory. The EICR is still Unsatisfactory.

My business model is such, that if a client now requires me to alter the EICR from Unsatisfactory, to Satisfactory, I will refuse.
I would be willing to re-inspect the Installation and issue a new EICR, which may or may not be Satisfactory.

From personal experience, I have seen remedial work carried out which resulted in the upstairs and downstairs RFCs being terminated into each other’s MCBs.
Now some may consider incorrect labelling as a code C3.
However as the Consumer Unit is intended to be used by ordinary persons (i.e. non-competent, non-trained, non-skilled, etc.) I consider a code C2 to be applicable.
In any event whichever code applies, it will not have been recorded on the unsatisfactory EICR.

If you find it reprehensible that I am not prepared to state an installation will be Satisfactory for x amount of years, if the listed C1 and C2 observations are rectified by others, without first inspecting the work, you are nuts.

I also think, that you’re nuts for being willing to effectively guarantee other’s work for x amount of years, without first inspecting that work.

Of course, if you are not saying such, then explain just what it is you are saying.
Try to be clear and effective in your explanation.

What I am saying is very clear.

You issue an undatisfactory EICR and recommend a date of next inspection. That date must assume all works that are required to be done, are done. This is written in black and white and is not open to interpretation.

When giving an unsatisfatory EICR for say the incorrect OCPD installed how long would you put for the next inspection due? Giving what you have said above it would appear that you would not put any date in as you would not sign it off unless you have seen the remedial works??
 
Last edited by a moderator:
What I am saying is very clear.

You issue an undatisfactory EICR and recommend a date of next inspection. That date must assume all works that are required to be done, are done. This is written in black amd white and is not open to interpretation.

When given an unsatisfatory EICR for say the incorrect OCPD installed how long would you put for the next inspection due? Goving what you have said above it would appear that you would not put any date in as you would not sign it off unless you have seen the remedial works??

No, I do not issue am Unsatisfactory report and then specify a date for the next inspection.
Just the same as if a vehicle fails an MOT, there is no date specified for the next MOT inspection.
If I were to specify when the next inspection should be, it would be when the observations have been rectified.

See here again unclear.
What do you mean by incorrect OCPD, what is the observation, what code has been applied?
You need to specify.
Is the rating incorrect, the type incorrect, does it affect the overall type testing of the CU, is the breaking capacity too low for the measured PFC, is there no discrimination with upstream or downstream devices?

I think I would really hate to see one of your reports.
Judging by how you explain yourself on the forum, I bet any of your reports would be just full of generalities.
Things like: “No RCD in Fuse Box, code C2”.
 
If I provide an unsatisfactory EICR, I also send the invoice .....

The date for the reinspection is defined by me

Whether the person acts on my report isn’t my problem ......
 
I have to agree with @essex - it is clearly stated within an EICR if you bother to read it that the date of next inspection is subject to dangerous and potentially dangerous defects being remedied, and further investigation being carried out where required. There is no need to reissue another EICR with the word "Satisfactory". Certified remedial works for the "Unsatisfactory" EICR make it now satisfactory. The original EICR is not amended to read "Satisfactory" - there is no need for it to. The certification proves that relevant issues have been corrected.
 
No, I do not issue am Unsatisfactory report and then specify a date for the next inspection.
Just the same as if a vehicle fails an MOT, there is no date specified for the next MOT inspection.
If I were to specify when the next inspection should be, it would be when the observations have been rectified.

See here again unclear.
What do you mean by incorrect OCPD, what is the observation, what code has been applied?
You need to specify.
Is the rating incorrect, the type incorrect, does it affect the overall type testing of the CU, is the breaking capacity too low for the measured PFC, is there no discrimination with upstream or downstream devices?

I think I would really hate to see one of your reports.
Judging by how you explain yourself on the forum, I bet any of your reports would be just full of generalities.
Things like: “No RCD in Fuse Box, code C2”.

See now you are turning it personal. A standard response to someone that feels theeatened.

You have answered my question. You do not carry out EICRs to BS7671. At least you are honest about this.
 
I have to agree with @essex - it is clearly stated within an EICR if you bother to read it that the date of next inspection is subject to dangerous and potentially dangerous defects being remedied, and further investigation being carried out where required. There is no need to reissue another EICR with the word "Satisfactory". Certified remedial works for the "Unsatisfactory" EICR make it now satisfactory. The original EICR is not amended to read "Satisfactory" - there is no need for it to. The certification proves that relevant issues have been corrected.

Thank you.
 
I have to agree with @essex - it is clearly stated within an EICR if you bother to read it that the date of next inspection is subject to dangerous and potentially dangerous defects being remedied, and further investigation being carried out where required. There is no need to reissue another EICR with the word "Satisfactory". Certified remedial works for the "Unsatisfactory" EICR make it now satisfactory. The original EICR is not amended to read "Satisfactory" - there is no need for it to. The certification proves that relevant issues have been corrected.
Read my first post in this thread (post #3).
 
See now you are turning it personal. A standard response to someone that feels theeatened.

You have answered my question. You do not carry out EICRs to BS7671. At least you are honest about this.
Oh you accusing me of being a troll, is not personal?
You still haven’t explained anything.
 

Reply to EICR rectifications completed by another electrician, what now? in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

4mm T&E circuits on 32amp breaker. Parts of the circuit run through ceiling, parts through trunking and possibly even the wall. Current carrying...
Replies
6
Views
936
So I've recently had an EICR for my building. Came back with about 20 odd C2 remedials and a few F1's which resulted in UNSATISFACTORY being...
Replies
5
Views
1K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
892
Hi, I have just had an EICR carried out and it has comeback with a few C2s. The only one I disagree with is the electrician raised as a C2 the...
Replies
10
Views
2K
Afternoon all, Just wondering what everyone's response to the following scenario is. Letting agents have asked us to carry out an EICR. There was...
Replies
42
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock