Discuss EICR SWA not buried. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

robd

-
Arms
Reaction score
339
Hi All,

Just writing up an EICR I did today, got a long garden with SWA feeding shed at bottom, armoured not earthed (code 2) but I also noticed for part of it's run, near the veg patch, the SWA is lying across the ground. It doesn't meet 522.8.10 so I'm guessing code 2 and a recommendation that either I drag it out and cleat to fence or I get my spade out again.

Anyone got any thoughts on a code?
 
Last edited:
Which one? To my mind the lack of earthing is a 2 because if someone sticks a spade through it the armoured is not earthed and the cable sitting above the surface is possibly a 2 because of the likelihood that you could stick a spade through it and that it doesn't meet 522.8.10 which says it should be buried at sufficient depth to avoid being damaged, although it doesn't mention laying across the top.
 
Southern comfort what a film. lol

Dave although I agree that southern comfort is a fantastic film, I thought dueling Banjo's was from the the other classic Deliverance
 
People tend not to stick knives and forks into cables laid across carpets, so I'm pretty sure people wouldn't normally stick a spade into a cable on the surface of a garden.

Maybe all flexes should be buried beyond the depth of an average knife and fork.
 

Reply to EICR SWA not buried. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi guys, long time lurker first time poster. I have an SWA 3 core armoured cable buried that runs to my back garden. This originally serviced an...
Replies
12
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
437
Hello all, Looking for help here as I've come across a strange call-out today. Bare with me here: Got a call from a customer saying they had...
Replies
13
Views
2K
As the title says, I am looking for a recommendation for an enclosure and gland arrangement to electrically isolate or divorce the earth/armouring...
Replies
25
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock