D
Davem
Right guys first EICR found some C1&C2 codes obviously once thee have been rectified what certification do you give the client once a satisfactory ??
Discuss Eicr in the UK Electrical Forum area at ElectriciansForums.net
An installation cert/minor works referenced to the EICR
Thanks Trev with regards t that, I have a hob plug in a socket, shower on a to small of a breaker, no blanks in consumer unit etc. how would I go about filling the minor works cert in. I ask because I'm not really changing the wiring I'm just rectifying the problems, would there be a need a test again if I'm simply changing a breaker ?? Thanks again Trev
I don't like the sound of the junction box, should be on an outlet. Assuming the wattage is ok for a 32 amp supply then there's nothing wrong there and if the oven is less than 2KW then the recommendation for a dedicated supply doesn't apply.Shower is 10.5kw fitted with 10mm cable on 40amp mcb, for the hob it's supplied from a 32amp breaker in 6mm junction box to a double socket hob and oven plug in.
so..Thanks Trev with regards t that, I have a hob plug in a socket, shower on a to small of a breaker, no blanks in consumer unit etc. how would I go about filling the minor works cert in. I ask because I'm not really changing the wiring I'm just rectifying the problems, would there be a need a test again if I'm simply changing a breaker ?? Thanks again Trev
so...Shower is 10.5kw fitted with 10mm cable on 40amp mcb, for the hob it's supplied from a 32amp breaker in 6mm junction box to a double socket hob and oven plug in.
so...
you know that MCB will hold for upto 1.45 X its I N for upto an hour before it lets go dont you...
whats the installation method of the shower cable?
Reply to Eicr in the UK Electrical Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.