Discuss Electrical Certificates in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
1
Hi guys,

I'm just wondering if; when you install a new sub-main cable off an existing distribution board which feeds an out building, do i need to fill out 2 separate certificates or can i combine them as one?
 
Hi guys,

I'm just wondering if; when you install a new sub-main cable off an existing distribution board which feeds an out building, do i need to fill out 2 separate certificates or can i combine them as one?
What certificates are you planning to issue?
 
By rights, it should be 2 certificates.
One for the sub main and the other for the new board and any out going circuits.
However most would do it on one certificate, with the sub main results recorded first on the Schedule, then a gap and the results for the new board.
 
My usual way would be one cert with a separate schedule of test results for each board.
On larger installations I might even do a separate inspection schedule but for this domestic job that would not really be needed.
 
Personally, for me, it depends on whether the sub board is using the same earthing system as the main DB or not. If they are on the same earthing system I use 1x EIC, with 1x schedule of inspections and 2x test sheets (one for each board). If they're on different earthing systems I issue 2x separate EICs (each with 1x schedule of inspections and 1x test sheet).
 
And assuming its domestic you need to issue a Part P certificate too ...
What is a Part P certificate? I used to do the notification on-line years ago and the customer/occupier used to get sent a building regulations compliance certificate by the competent scheme provider.
 

Reply to Electrical Certificates in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I am a home owner and our builder has completed a garage conversion with the electrician installing a new 4 way distribution board. The...
Replies
18
Views
1K
Good morning all, I am currently working on a House in Multiple Occupation (HMO) consisting of 10 flats, with three parking spots equipped with...
Replies
9
Views
544
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Hi all, how do you go about filling out a EIC or a minor works certificate when you have multiple installers that have worked on the circuit...
Replies
5
Views
747
I am seeking a job as an electricians mate / improver / labourer around South Yorkshire. I am based in Doncaster, i have a uk full driving licence...
Replies
3
Views
505

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock