Rough. Is that the main fuse for all 8 flats? It says 60A?
The burned plug and extension lead has nothing to do with the electrician.... that belongs the tenants. Maybe a loose fuse connection in the plugtop? (or the 13A fuse has been replaced with a nail)
The property needs an EICR before any tenants can move in. That should have picked up any faults and reported to landlord.
If this has been a rewire with sitting tenants, then they should have completed a test certificate and notified to LABC.
Is this 8 flats, or is it an HMO?
Hi this is the reportRough. Is that the main fuse for all 8 flats? It says 60A?
The burned plug and extension lead has nothing to do with the electrician.... that belongs the tenants. Maybe a loose fuse connection in the plugtop? (or the 13A fuse has been replaced with a nail)
The property needs an EICR before any tenants can move in. That should have picked up any faults and reported to landlord.
If this has been a rewire with sitting tenants, then they should have completed a test certificate and notified to LABC.
Is this 8 flats, or is it an HMO?
I knew it was bad please explain more please. I need to sue the landlordwho wrote those observations?
Johnny aged 5?
Well, as said before it is rough as fack
However, cowboy electrical probably installed that lot 30 years ago.
Fuse carrier has become weak with age and been arcing
Change burnt socket
Put enclosure round cable terminals feeding socket on floor, whilst your at it, screw it to the wall?
New fuse And holder or even better a fused isolator.
Back on supply, write report, suggest full eicr.
Off to next job by lunch time.
[automerge]1593590357[/automerge]
Just noticed the OP is listed as Tennant on profile.
My advice would be,
Write to landlord or agent asking for a copy of the electrical inspection report.
Consider your own actions,
it is not advisable to run heaters from extension leads, a heater is likely to use all the electricity the lead and adapter can handle safely without the added power of the other things plugged into it.
I am assuming that it is a heater or other powerful device that is running for long periods of time that is attached to the plug with burn marks.
It is also likely that the wall socket with burns around 1 pin has been caused by overloading it, by chance is that where the damaged extension lead plugs in?
Council issued hazard awareness cert and that’s it, it should of been prohibition order. Council have conspired with landlord, I mean can you tell me any hmo that has no fire doors but has a licence. He was running it for over 2 years without a licence then he gained one in 2017 and still no fire doors. I have been through everyone and I have solicitor, I just wanted more opinions from qualified electrical guys like yourself and the othersLook... you won’t get anywhere saying that “a bunch of electricians on an online forum said it was bad”
Try citizens advice, or a solicitor. They will know the rules regarding renting out a flat with no heating and the electrics the way it is.
Have you got a trusted friend or a social worker that could contact the landlord and find out what’s happening?
I find it difficult to see how the council can ignore this.
who wrote those observations?
Johnny aged 5?
I believe this is fraudulent and the company he is using operate under two names I don’t like how this has been dealt with 8 flats £260 each flat per weekand those schedule of test results.... For a use of a word, Shocking, half the results are missing and incomplete
looks like he just copied and pasted the descriptions from the inspection schedule straight into the observations..... No locations, lacking any detailed descriptions; and the technical terminology he's used on the odd occasion he's bothered are something else...
All signed off by a Niceic approved contractor too... Is that really the standard they allow???
And he can afford skilled trades men he has handymen doing skilled work for penniesI believe this is fraudulent and the company he is using operate under two names I don’t like how this has been dealt with 8 flats £260 each flat per week
Hi what would you advisewho wrote those observations?
Johnny aged 5?
I believe this is fraudulent and the company he is using operate under two names I don’t like how this has been dealt with 8 flats £260 each flat per week
[automerge]1593607643[/automerge]
And he can afford skilled trades men he has handymen doing skilled work for pennies
[automerge]1593608351[/automerge]
Hi what would you advise
I’m not expecting you to be involved in the action I take, I just wanted a professional opinion on what I have posted. Been going on for years and it has to stop. I really appreciate your opinionsI can't / won't get involved with the whole suing the landlord thing you mentioned earlier.
I'm merely making observations on what i see as a shoddy report that's been issued. You could make a complaint about the standard of it to the NICEIC as that's the scheme they're members of, however, you may not get very far as it was the landlord who ordered and paid for the work.
If the licensing authority are being difficult or you believe that they are not taking this seriously, I would advise you contact your MP, as much as I hate most politicians, they can come in handy when a bit of force is needed, also handy if there is an election coming up.I’m not expecting you to be involved in the action I take, I just wanted a professional opinion on what I have posted. Been going on for years and it has to stop. I really appreciate your opinions
If you are that unhappy... the easiest thing, is for you to move out and find some other accommodation. Hope you appreciate my opinion.Been going on for years and it has to stop. I really appreciate your opinions
Agreed, and it undoubtedly is unsatisfactory, but the thing is if you look at the report in any kind of detail it doesn't exactly inspire confidence due to the amount of data missing and the language used.am i missing something here... the report says unsatisfactory and gives various reasons why.
How much more advice would you want? Contact Building Control personally and explain the situation. Get a name and if nothing is done 7/10 days contact Citizens Advice regarding a Solocitor... SimpleCouncil issued hazard awareness cert and that’s it, it should of been prohibition order. Council have conspired with landlord, I mean can you tell me any hmo that has no fire doors but has a licence. He was running it for over 2 years without a licence then he gained one in 2017 and still no fire doors. I have been through everyone and I have solicitor, I just wanted more opinions from qualified electrical guys like yourself and the others
[automerge]1593606879[/automerge]
I sent video of plug in flat crackling an smoking, that was in 2017 they did nothing because I complained I was threatened with eviction and his electrical guy said he hopes the flat burns down over my head
Didn’t notice the date of OP. Wish there was an alert when going on threads if they have been on for longer than a month say.No updates since the middle of last year suggest the situation has been resolved in some way or is no longer a priority.
I know other forum softwares have add-ons that alert a user is they're replying to a thread that hasn't been replied to in a set period of time, maybe there is something for hereDidn’t notice the date of OP. Wish there was an alert when going on threads if they have been on for longer than a month say.
wander what happened!
Well spotted ?No updates since the middle of last year suggest the situation has been resolved in some way or is no longer a priority.
Nor did I, and it was me that woke it up again. Oops.No updates since the middle of last year suggest the situation has been resolved in some way or is no longer a priority.
I don't think it's always as straight forward as just moving out for some people. If Raymond has the option to move out, then he should do that. If not, then he needs a solicitor.I don't think it's always as straight forward as just moving out for some people. If Raymond has the option to move out, then he should do that. If not, then he needs a solicitor.
Good luck Raymond.
Good luck Raymond.
Thank you so much you hit the nail on the head. I can’t move out. High risk group plus, this whole electrical situation with the land lord was the start of him trying to illegally evict me.
After 6 months of the hazard awareness notice landowners did nothing. The garden flat I live in had no planing permission, when I moved in he told me I could use one part as my kitchen, I have all evidence of that, even got it in a transcript to prove it too. I wasn’t aware at the time he could use that part of the flat. Camden council had already issued him notice. The housing team at camden have also breached there duties.
3 years later a power cut happened, this was one of so so many. Went 3 day with no electricity also the hmo was all down too. Because I’m disabled I had to have electricity cables over the wall to next door for use of electricity.
That was final for me. Because I have a protected characteristic and the landlord knows of my condition, this shouldn’t happen.
I reported to camden and they didn’t come out to do inspection to my flat or the hmo property that landlord was running without a licence for over a year.
Instead the EHO ISSUED prohibition order. But left me in the property. Technically I’m homeless. Made so by the landlord because flat not git enough to live in. So he must pay compensation or the local authority.
So I got a qualified electrician to visit the property and as soon as he opened the cupboard he said it’s a CODE 1 camden council ignored his response to this.
Cut this story short: ukpn supplied a 3 phase network and the landlord apparently has paid out over 30k.
We are in court I have an amazing solicitor and barrister. No rent has been paid for over a year that is also in court.
The disrepair is in court too
Also he told the electrical company eon that there was a marijuana farm at my flat and this was the cause of the electrical ? in the property. This is also recorded and was passed onto action fraud.
8 flats he was collecting the money from the coin meters ever month and not paying the bill.
Because it was very high bill the landlord told them I had left the property because of a marijuana farm at my flat and all windows were painted black.
THIS OF COURSE IS ALL LIES.
So that issue is also in court for DEFAMATION my barrister has asked for 60k because of this.
Now all meters are outside in the same cupboard but updated.
I removed my meter off there fraudulent setup so I have my own meter and I pay 17£ per month and get my disability discount on electricity.
Before we were paying 50 to 80 per week in the winter, all 8 flats. One guy had his family round for Christmas he paid into the coin meter over £100.
I have faced harassment and it’s all on cctv I have evidence of everything. No hot water for over a year to today no heating. Breach of human rights. The energy Onbudsman upheld my complaints and issued compensation I refused it because it means I’m satisfied with the end result. NO WAY AM I SATISFIED.
This ROGUE LANDLORD never knew I’m a secret agent ??????
I wish lol.
I’m just a disabled tenant wanting to live safe. Is that to much to ask for?
Ahh also I forgot to say hes name is not on the land register but he signed statements of truth that he is. His illegal eviction WILL be struck out and I hope he gets put on the ROGUE LANDLORDS REGISTER
I don't think it's always as straight forward as just moving out for some people. If Raymond has the option to move out, then he should do that. If not, then he needs a solicitor.The electrician has done his job in identifying serious issues.
he has made it unsatisfactory and given 6 months Till next inspection.
he reports he was unable to test one board due to mess. ( mess is my words, he says neutrals and earths terminated in wrong sequence. we all know that’s code for mess). This is why he has not tested it all.
I have not read full report, but picked up that this electrician has done his job in so far as he knows its a mess and said so within his limits.
ok I agree I would word things differently,
i agree he hasn’t tested everything, but I possibly wouldn’t either if it means extra work not quoted for to put right before I could begin testing.
his coding seems ok to me, but some will rip that apart because of our different views On coding.
advice for Tennant.
It looks like notices have been issued to landlord to get things moving. The council are involved. Unfortunately these thing take time. And Under covid restriction will take longer.
Even if the landlord does acknowledge he needs to do something, it will take time to find contractors to do the job. and actually carrying out the works will take a fair bit of time.
a lot of landlords in my area are selling up due to the new electrical inspection laws out on 1st April. Your land lord may decide to sell up Rather than pay to get the works done. It’s going to cost a substantial amount to do.
If I was you and I was in a position to I would move out.
legally I’m afraid I dont believe there is anything you can do to speed things along.
I think the advice on going to your local MP surgery may help, but since the council are involved already then maybe it won’t.
good luck.
When I woke up this morning I could smell fire this is what I found. I only have 1 working plug socket in the whole flat I’m worried there is going to be a fireI don't think it's always as straight forward as just moving out for some people. If Raymond has the option to move out, then he should do that. If not, then he needs a solicitor.
Good luck Raymond.
Thank you so much you hit the nail on the head. I can’t move out. High risk group plus, this whole electrical situation with the land lord was the start of him trying to illegally evict me.
After 6 months of the hazard awareness notice landowners did nothing. The garden flat I live in had no planing permission, when I moved in he told me I could use one part as my kitchen, I have all evidence of that, even got it in a transcript to prove it too. I wasn’t aware at the time he could use that part of the flat. Camden council had already issued him notice. The housing team at camden have also breached there duties.
3 years later a power cut happened, this was one of so so many. Went 3 day with no electricity also the hmo was all down too. Because I’m disabled I had to have electricity cables over the wall to next door for use of electricity.
That was final for me. Because I have a protected characteristic and the landlord knows of my condition, this shouldn’t happen.
I reported to camden and they didn’t come out to do inspection to my flat or the hmo property that landlord was running without a licence for over a year.
Instead the EHO ISSUED prohibition order. But left me in the property. Technically I’m homeless. Made so by the landlord because flat not git enough to live in. So he must pay compensation or the local authority.
So I got a qualified electrician to visit the property and as soon as he opened the cupboard he said it’s a CODE 1 camden council ignored his response to this.
Cut this story short: ukpn supplied a 3 phase network and the landlord apparently has paid out over 30k.
We are in court I have an amazing solicitor and barrister. No rent has been paid for over a year that is also in court.
The disrepair is in court too
Also he told the electrical company eon that there was a marijuana farm at my flat and this was the cause of the electrical ? in the property. This is also recorded and was passed onto action fraud.
8 flats he was collecting the money from the coin meters ever month and not paying the bill.
Because it was very high bill the landlord told them I had left the property because of a marijuana farm at my flat and all windows were painted black.
THIS OF COURSE IS ALL LIES.
So that issue is also in court for DEFAMATION my barrister has asked for 60k because of this.
Now all meters are outside in the same cupboard but updated.
I removed my meter off there fraudulent setup so I have my own meter and I pay 17£ per month and get my disability discount on electricity.
Before we were paying 50 to 80 per week in the winter, all 8 flats. One guy had his family round for Christmas he paid into the coin meter over £100.
I have faced harassment and it’s all on cctv I have evidence of everything. No hot water for over a year to today no heating. Breach of human rights. The energy Onbudsman upheld my complaints and issued compensation I refused it because it means I’m satisfied with the end result. NO WAY AM I SATISFIED.
This ROGUE LANDLORD never knew I’m a secret agent ??????
I wish lol.
I’m just a disabled tenant wanting to live safe. Is that to much to ask for?
Ahh also I forgot to say hes name is not on the land register but he signed statements of truth that he is. His illegal eviction WILL be struck out and I hope he gets put on the ROGUE LANDLORDS REGISTER
I’m worried there will be a fire ? I woke up smelling burning and found this electric heaterI don't think it's always as straight forward as just moving out for some people. If Raymond has the option to move out, then he should do that. If not, then he needs a solicitor.
Good luck Raymond.
Thank you so much you hit the nail on the head. I can’t move out. High risk group plus, this whole electrical situation with the land lord was the start of him trying to illegally evict me.
After 6 months of the hazard awareness notice landowners did nothing. The garden flat I live in had no planing permission, when I moved in he told me I could use one part as my kitchen, I have all evidence of that, even got it in a transcript to prove it too. I wasn’t aware at the time he could use that part of the flat. Camden council had already issued him notice. The housing team at camden have also breached there duties.
3 years later a power cut happened, this was one of so so many. Went 3 day with no electricity also the hmo was all down too. Because I’m disabled I had to have electricity cables over the wall to next door for use of electricity.
That was final for me. Because I have a protected characteristic and the landlord knows of my condition, this shouldn’t happen.
I reported to camden and they didn’t come out to do inspection to my flat or the hmo property that landlord was running without a licence for over a year.
Instead the EHO ISSUED prohibition order. But left me in the property. Technically I’m homeless. Made so by the landlord because flat not git enough to live in. So he must pay compensation or the local authority.
So I got a qualified electrician to visit the property and as soon as he opened the cupboard he said it’s a CODE 1 camden council ignored his response to this.
Cut this story short: ukpn supplied a 3 phase network and the landlord apparently has paid out over 30k.
We are in court I have an amazing solicitor and barrister. No rent has been paid for over a year that is also in court.
The disrepair is in court too
Also he told the electrical company eon that there was a marijuana farm at my flat and this was the cause of the electrical ? in the property. This is also recorded and was passed onto action fraud.
8 flats he was collecting the money from the coin meters ever month and not paying the bill.
Because it was very high bill the landlord told them I had left the property because of a marijuana farm at my flat and all windows were painted black.
THIS OF COURSE IS ALL LIES.
So that issue is also in court for DEFAMATION my barrister has asked for 60k because of this.
Now all meters are outside in the same cupboard but updated.
I removed my meter off there fraudulent setup so I have my own meter and I pay 17£ per month and get my disability discount on electricity.
Before we were paying 50 to 80 per week in the winter, all 8 flats. One guy had his family round for Christmas he paid into the coin meter over £100.
I have faced harassment and it’s all on cctv I have evidence of everything. No hot water for over a year to today no heating. Breach of human rights. The energy Onbudsman upheld my complaints and issued compensation I refused it because it means I’m satisfied with the end result. NO WAY AM I SATISFIED.
This ROGUE LANDLORD never knew I’m a secret agent ??????
I wish lol.
I’m just a disabled tenant wanting to live safe. Is that to much to ask for?
Ahh also I forgot to say hes name is not on the land register but he signed statements of truth that he is. His illegal eviction WILL be struck out and I hope he gets put on the ROGUE LANDLORDS REGISTER
View attachment FullSizeRender.movThe electrician has done his job in identifying serious issues.
he has made it unsatisfactory and given 6 months Till next inspection.
he reports he was unable to test one board due to mess. ( mess is my words, he says neutrals and earths terminated in wrong sequence. we all know that’s code for mess). This is why he has not tested it all.
I have not read full report, but picked up that this electrician has done his job in so far as he knows its a mess and said so within his limits.
ok I agree I would word things differently,
i agree he hasn’t tested everything, but I possibly wouldn’t either if it means extra work not quoted for to put right before I could begin testing.
his coding seems ok to me, but some will rip that apart because of our different views On coding.
advice for Tennant.
It looks like notices have been issued to landlord to get things moving. The council are involved. Unfortunately these thing take time. And Under covid restriction will take longer.
Even if the landlord does acknowledge he needs to do something, it will take time to find contractors to do the job. and actually carrying out the works will take a fair bit of time.
a lot of landlords in my area are selling up due to the new electrical inspection laws out on 1st April. Your land lord may decide to sell up Rather than pay to get the works done. It’s going to cost a substantial amount to do.
If I was you and I was in a position to I would move out.
legally I’m afraid I dont believe there is anything you can do to speed things along.
I think the advice on going to your local MP surgery may help, but since the council are involved already then maybe it won’t.
good luck.
Camden council are a bunch of well I have string words for them.you cannot continue like this. It’s disgusting. Someone really needs to get there finger out here.
anyone see the news yesterday regarding the local authority rentals in hackney. I was absolutely gobsmacked. Even the newsreader who is meant to be unbiast was shocked.
The electric sockets and lights full of water.
the inspector who visited said it was an immediately dangerous situation. Yet the electrics are still switched on and people were living there.
What was said about camden? I can add there discriminating ways of service I’m totally sick of camdenSaw that last night about Camden. Unbelievable. I would imagine someone will be for the high jump now that this has come out.
What was said about camden? I can add there discriminating ways of service I’m totally sick of camden
The council flats judged the worst in Britain | ITV News
The pictures, filmed by ITV News at a London tower block, have been described by experts as the worst housing conditions they have ever seen. | ITV National Newswww.itv.com
hope the link works
Reply to Electrical fire in house in the Certification NICEIC, NAPIT, Stroma, BECSA Forum area at ElectriciansForums.net
We get it, advertisements are annoying!
Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.