I'm looking for some input on minimum installation standards for an installation that is a hybrid of US and EU equipment for an installation I am working on.
The project is located in a Caribbean island that uses 230/400V 60Hz. My solar training is all US focused although I am originally a UK trained electrician, many years ago.
The island has very confused electrical standards, most of the electrical equipment is American but the conduit and boxes are often British. High voltage customers with recently built plant typically use 120/208V US based designs and so everything would be US equipment and standards.

This customer has a lot of US sourced refrigeration equipment running 480V compressors on 420V to 440V supply through booster trafos.

The project is pretty large, multiple roofs in multiple locations, all 3 phase 230/400V. As no US inverter manufacturer could offer a suitable inverter, we decided to use SMA inverters sourced from Germany, and we went with a multiple string inverter design with as many as 8 inverters on the largest installation. The most common inverter we are using is a Sunny Tripower 20000TL and 17000Tl, which I think are beautiful pieces of equipment.

The standard US design would include a fused DC string combiner, DC disconnect and single connection to the inverter in conduit. As far as I can determine, the design that the inverters are intended to use involve direct connection of the strings to the inverter with no fusing or disconnects. They have an Electronic Solar Switch that protects the inverter from reverse current by shorting the strings to make them safe. From the manual, SMA's preferred method to disconnect the strings seems to be to turn off the AC disconnect, in which case the DC current is near zero and therefore safe to unplug the strings. I can see why these inverters are not available in the US where the NEC likes to see a big DC disconnect before the inverter, however, I can also see why SMA would not see that as necessary as disconnecting the AC does reduce the input current to near zero.

I don't have any code requirements to consider, there is no code to cover solar pv, so I am having to make this up as I go. I want to take advantage of the features of the inverter such as Intelligent String Failure Detection which monitors the strings, builds a profile over several days and can detect loss of strings.

I'm looking for advice on how to implement a common sense design using available components. All our electrical supply comes from the US. My biggest issue is on the DC side, I believe that a non-fusible 600V 60A 3 phase disconnect on the AC side covers the bases. I love the idea of being able to safely test the strings at the inverter with our Seaward Solar PV150 test set, something you can't do on an American system as the strings are hard wired at the combiner.

What advice can the members offer on best practices we should follow?
 
p.s. also hook the SMA inverters up via the RS485 module to sunny Webbox (RS485 version) to Sunny Portal via the internet - invaluable for on-line and remote monitoring of systems.

You'll end up with something like this:
1-IMG_1230.JPG
 
I don't have any code requirements to consider, there is no code to cover solar pv, so I am having to make this up as I go. I want to take advantage of the features of the inverter such as Intelligent String Failure Detection which monitors the strings, builds a profile over several days and can detect loss of strings.

I'm looking for advice on how to implement a common sense design using available components. All our electrical supply comes from the US. My biggest issue is on the DC side, I believe that a non-fusible 600V 60A 3 phase disconnect on the AC side covers the bases. I love the idea of being able to safely test the strings at the inverter with our Seaward Solar PV150 test set, something you can't do on an American system as the strings are hard wired at the combiner.

What advice can the members offer on best practices we should follow?
don't use the string failure tool if there is any seasonal shading, as it sees this as a string failure - only use in unshaded situations.

the 20,000TL has a fairly narrow voltage range, and single string - the 17,000 dual MPPT option has much wider voltage range and dual MPPT so could be better for multi roofs etc. you also don't usually need to worry about fusing the strings due to the split MPPT set up, as long as you size the cables to take possible reverse current from the strings connected to that side of the dual MPPT set up.

they do optional add in string fuses and surge protection.

talk to SMA technical design team, they know their stuff and you should be able to configure the inverters properly with their help.
Please call +44 001908 304899
[email protected]
 
One of the useful triggers from the Sunnyportal is the relative inverter performance, where there are multiple inverters on a site we have found that this highlights any string or invereter problems. Also by plotting multiple sites against each other (which we site up as the first screen we see on login) it's easy to pick up unusual variances so that we can then investigate remotely (in our case from a warm office, in your case from a nicely air-conditioned / beer cooled office)
 
don't use the string failure tool if there is any seasonal shading, as it sees this as a string failure - only use in unshaded situations.
THanks. There's no shading on this project, just huge steel warehouse roofs. We don't get a lot of shading concerns in the Caribbean locations, not a lot of tall trees, no chimneys, lots of flat concrete roofs.

- - - Updated - - -

Dont need any help fitting them, do you?
I might have space for an intern, yes.
 
"the 20,000TL has a fairly narrow voltage range, and single string"
We are using mostly 20000TLEE with 1000V SolarBOS fused combiners with disconnect. I only have one 17000 specified, but when I went to install it I was very impressed with the features. We don't have those advanced SMA products in the US market.
 
That link made my day. It is exactly what I am looking for a relatively simple guide with diagrams.
I read the string fusing requirements, so much more complex than NEC. Under NEC, 1 or 2 strings, no fuse. 3 up, fuses are required.
that's essentially what it boils down to most of the time anyway;)
 
On the 17000TL, are the 5 Input A connections isolated? Surely they would then require external fusing, in which case what's the point of them?
 
is that the dual MPPT or single MPPT model?

If it's dual MPPT, we'd generally combine the strings for each side in parallel on the roof, use 4 or 6mm2 double insulated single core cables throughout (so it can handle any potential fault current even from all 3 strings with ease) then run them down in a single cable so you usually end up with 2-3 strings per MPPT combined, which we've not usually needed to fuse.

If it's single MPPT, then that's a different matter, and you'll probably need to fuse the strings either on the roof, or by the inverter using a separate string fuse unit.

Aurora Power-One do 20 & 30 KW inverters with built in string fuses as an alternative, which is generally what we use for anything that's going to end up needing fusing, and is why I'm a little hazy on how I'd do it with the single string 17000TL.

as to what's the point of the 5 inputs...... I too have wondered that, but I guess it gives flexibility for individual strings with individual string fuses, which might be needed in some countries. SMA build their kit to be versatile for use anywhere in the world to comply with all standards.
 

Reply to European installation standards for US based installer in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi, I have nearly finished installing my first solar system for my brother in law. havent installed a DC isolator on the string lines (none in...
Replies
4
Views
2K
Hi everyone, this is my first time using a forum so please don’t criticise to much. I recently done by EESS course but I didn’t actually find it...
Replies
4
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
465
I decided to get solar panels, the inverter instructions say one can use type AC, so the existing 14 x RCBO CU seems OK, may be a good idea to fit...
Replies
4
Views
1K
  • Article
Electrical2Go - Green2go Launches for All Your Solar, EV Charging and Renewable Needs Green2Go - for All Your Solar, EV Charging and Renewable...
Replies
1
Views
312

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock