- Reaction score
- 2,043
What KVA have the DNO supplied as that looks like a 70KVA max head. So if you want 80KW for charging you will struggle,
Discuss EV - after few pointers please in the UK Electrical Forum area at ElectriciansForums.net
Yes correct - 70KVA (3off 100A fuses). As with EVSE's, the DC charger can be configured to limit power delivery so the main fuses don't blow.What KVA have the DNO supplied as that looks like a 70KVA max head. So if you want 80KW for charging you will struggle,
Well lets say you are building a housing estate. Developer will arrange for DNO to lay 3-phase in the pavement on each side of the road. That is the expensive part.Sounds like you haven't been involved in organising supplies to buildings before, there will likely be a very large difference In single and three phase.
Reply to EV - after few pointers please in the UK Electrical Forum area at ElectriciansForums.net