Discuss Feed to flat in escape route - best option? in the UK Electrical Forum area at ElectriciansForums.net

Dartlec

Esteemed
Arms
Reaction score
2,441
I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted building.

The ground floor is a separate front entrance, the upper flats have a side entrance with stairwell, which is protected with smoke and EL, though not sure if a FRA exists, or if it counts as a protected escape route (there is an external metal staircase as well).

The current T&E is buried in the wall, but for ease/cost I'd like to surface mount from the meters (under the stairs at ground level) and up to the flat.

My current thinking is SWA surface clipped with Dline or Linian clips. Obviously there will be a suitable fuse in the meter cupboard to protect the run.

Anyone see an issue with that and feel an alternative is better or required (steel trunking for example)? I haven't worked with steel conduit or MICC so would rather this wasn't the job to start on...

If I go with SWA, should I be sourcing BS 7846 fire resistant cabling? If so, anyone know of a wholesaler that sells it by the metre?
 
It's always difficult to comment on jobs and sites you have never seen as to the suitability of a solution, I assume this is just a vertical run of cable which shouldn't pose any problems although where a cable comes up through a floor I do like to install some additional protection to prevent damage to the sheath at low level
 
Vertical from under stair cupboard on ground floor up through half landings on the first and second flight of stairs (wooden) and then horizontally across wall and into the flat..

I was thinking of possibly chasing a channel out to go from bottom to top of the mini stair landing it needs to cross vertically - could possibly fit some conduit in there as additional protection.
 
I have a job coming up where I likely need to replace old twin and earth (imperial size) feeding one, perhaps two flats in a 3 storey converted building.

The ground floor is a separate front entrance, the upper flats have a side entrance with stairwell, which is protected with smoke and EL, though not sure if a FRA exists, or if it counts as a protected escape route (there is an external metal staircase as well).

The current T&E is buried in the wall, but for ease/cost I'd like to surface mount from the meters (under the stairs at ground level) and up to the flat.

My current thinking is SWA surface clipped with Dline or Linian clips. Obviously there will be a suitable fuse in the meter cupboard to protect the run.

Anyone see an issue with that and feel an alternative is better or required (steel trunking for example)? I haven't worked with steel conduit or MICC so would rather this wasn't the job to start on...

If I go with SWA, should I be sourcing BS 7846 fire resistant cabling? If so, anyone know of a wholesaler that sells it by the metre?
What size is the current T AND E CABLE
 
Seems a reasonable way to do it, rather than chasing a channel would it not be easier to install a 50x50 metal trunking
I was thinking surface mounted for most of the run, just the bit that passes through the wooden staircase in something. With a small van and just me I'd prefer not to fiddle with metal trunking, though may be that I need to bite the bullet and go for it...

Cost is certainly an issue since it's a joint freehold place so everyone has to agree.
 
I was thinking surface mounted for most of the run, just the bit that passes through the wooden staircase in something. With a small van and just me I'd prefer not to fiddle with metal trunking, though may be that I need to bite the bullet and go for it...

Cost is certainly an issue since it's a joint freehold place so everyone has to agree.
Pre premature collapse regulation I would have almost certainly done something like this in T4 trunking , but now I would bite the bullet and put up some nice galv trunking
 
Pre premature collapse regulation I would have almost certainly done something like this in T4 trunking , but now I would bite the bullet and put up some nice galv trunking
Would the linian or Dline clips work with SWA for premature collapse approval though? The only issue then is whether surface SWA is suitable in an escape route - There already is plenty of plastic trunking in the hallway for the EL and smokes, to be fair (not installed by me and been in well before the 18th and premature collapse )
 
Would the linian or Dline clips work with SWA for premature collapse approval though? The only issue then is whether surface SWA is suitable in an escape route - There already is plenty of plastic trunking in the hallway for the EL and smokes, to be fair (not installed by me and been in well before the 18th and premature collapse )
I quite often use plastic trunking with all round band or metal P clips fixing the cable inside it and have done for a number of years
 
IWith a small van and just me I'd prefer not to fiddle with metal trunking,

What has the size of your van got to do with the design of the electrical installation.

I've recently completed a job which used around 60m of galv trunking and over 100m of galv conduit and I've got a Honda CR-V and that was also just me on my own.
 
The ground floor is a separate front entrance, the upper flats have a side entrance with stairwell, which is protected with smoke and EL, though not sure if a FRA exists, or if it counts as a protected escape route
Protected escape routes are normally devoid of almost everything, made of concrete, with nothing at all combustible in them. If there's an external fire escape I'd be surprised if this was a "protected escape route". (See appendix 13)
Would the linian or Dline clips work with SWA for premature collapse approval though? The only issue then is whether surface SWA is suitable in an escape route
I'm not seeing any issues. Linian clips often support FP200 cables in normal escape routes.
 
If it's not defined as such in a Fire Risk Assessment, then it's not a protected escape route.
And you've got until 27 September before you must work to Amendment 2.
 
If I go with SWA, should I be sourcing BS 7846 fire resistant cabling? If so, anyone know of a wholesaler that sells it by the metre?
Would it need to be fire resistant cable (i.e. is it powering emergency support stuff)?
Superlec do it by the metre but smallest is 25mm:
As a minimum I would look at LSZH SWA which they also do, and it thinner sizes (e.g. 16mm) and slightly cheaper, for comparison of same 25mm 3C:
But the idea of using some steel trunking is very appealing as well. How many runs of SWA would you be looking at? With metal trunking you might get away with 16mm T&E as no cable penetration protection issues, assuming it meets other electrical requirements like VD and bond size, etc.
 
I still would go for large galv trunking

It looks nice , it meets all the pre collapse escape plan stuff and it is not that expensive
 
I was thinking surface mounted for most of the run, just the bit that passes through the wooden staircase in something. With a small van and just me I'd prefer not to fiddle with metal trunking, though may be that I need to bite the bullet and go for it...

Cost is certainly an issue since it's a joint freehold place so everyone has to agree.
Does your wholesaler not deliver although if you can't get it in your van then it goes on the roof rack
 
Does your wholesaler not deliver although if you can't get it in your van then it goes on the roof rack
Don't have a roof rack because I need to fit under 2m for underground car parks sometimes. Might see if they can deliver, otherwise need to find places that sell them in 2m lengths, but will definitely investigate it as an option.
 
Don't have a roof rack because I need to fit under 2m for underground car parks sometimes. Might see if they can deliver, otherwise need to find places that sell them in 2m lengths, but will definitely investigate it as an option.
I have a Thule roof rack that I can fit quickly when needed and removed just as quick when not needed to help keep the fuel consumption and noise down
 

Reply to Feed to flat in escape route - best option? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi all, I have two questions regarding wiring and containment on commercial property stairwells in Ireland. We are currently wiring a 3 story...
Replies
10
Views
734
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
494
I've just finished an installation on a large outhouse around 50 meters from the main property, but I'm having issues with unusually high Zs...
Replies
11
Views
4K
Hello, I am trying to find out the requirements/regulations/law which apply to residential multi-storey (3) fire exit/escape lighting. Can...
Replies
11
Views
2K
Short Version Is it permissible to have 2 feeds to 2 separate consumer units in a detached garage? Is it permissible to run SWA underground...
Replies
15
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock