O

Octopus

So I was first fixing a bathroom yesterday and the plumber chap has drilled the holes in the ceiling - when I looked up one of the holes I could see that the hole cutter had "kissed" one joist and had just missed another (the house has had a loft conversion hence why the 2nd joist is so close to the original ones.

When I questioned fitting the light - he said its a "fire rated" downlight so "clearances" don't matter - in fact he's fitted loads and is never bothered about all in insulation covering them (bare in mind he likes CED £10.00 halogen 50w units!)

The box the lights come in didn't have any clearance information on it, but on reading the instructions in the box, it clearly states 75mm clearance all round.

So after a bit of humming and haring - it was agree that a new hole would be drilled in a "sensible" location and be big enough for a tilt unit & that I could supply & fit the lights. He takes lights back for a refund. All good I think......


The customer sees the new hole later and asks for it to be put back to the original position - so the numpty agrees. I get a text today telling me to go to site on Monday to fit a JB and extend the cable to the "original" location.

I say I won't make the change and if he wants to do it he's on his own!

Get a text back saying send invoice to client for work done so far he'll "get somebody else" to do it.

Now me knows he dabbles with electrics so I'm sure he'll do it himself.




Now now the dilema - the man of the house is away skiing for a few days and he emails me today asking how its going ..... so how do I respond???

A) Do I submit invoice and ignore it - its not tested formally as its only first fixed?

B) Do I submit invoice and add note on covering email about joists?

C) Do I submit invoice and note on invoice issue with proximity of joists?


I'm considering B) or C)!

Thoughts chaps
 
Just income or your time and in the email wrote exactly what you wrote above regarding the scenario. Job done, you advised what needed to be done as a qualified electrician and the plumber didn't agree so it's down to him!
 
Who's your client, the home owner or the plumber?

We are both billing directly, both of us have done work for him before. But this time the plumber gave me the nod about the job - then I went in and said he needed a new CU before I would touch the bathroom - which was all done and dusted about 10 days ago!
 
Have him to agree this and crack on,as you said the plumber will move them so get him to use gu10 leds and state on the certificate that the proximity to joists was explained and it is the intention of the client to relocate the fittings
 

Reply to Fire Rated Downlights - FFS!!!!!!!!!!!!! in the Security Alarms, Door Entry and CCTV (Public) area at ElectriciansForums.net

Similar Threads

Hi I have an electrician over and he took over from an incompetent builder. The builder already installed the wiring but the electrician told me...
Replies
22
Views
1K
Looking through the fire-rated downlights out there on the market, Integral Evofire claims its canless design would let the heat off and hence...
Replies
8
Views
220
I recently came across a video on YouTube and the guy fit a fuseboard. Very tidy job but I was confused as he used couplers to have the board not...
Replies
26
Views
3K
Hi all, a very long time I did a swanky grand designs type new build in the middle of nowhere, so in the middle of nowhere that it's a house with...
Replies
1
Views
316
Hi folks, Quick query for this still practicing regarding bill payment for a job not complete. My partner recently employed an electrician to do...
Replies
11
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock