MDJ

I have spent 2 days in total doing an EICR on these boards, I won't give away too much info in this first post, I would like you new sparks who go around peoples houses changing dist boards to let me know if you think this needs ripping out and replacing? if so what is your reasons and what questions do you think you would need to ask me before making your decision?
 

Attachments

  • 016.jpg
    190.6 KB · Views: 452
  • 017.jpg
    176.1 KB · Views: 498
a few factors would decide if I would recommend replacement .........

Is the backboard or frame of any of the 3036's made of a combustible material

How do the retro MCB's fit and interface with the existing board and do the cause any exposed parts

How does the cover fit and the subsequent fuse cover fit with these in place, as if both don't fit then this contravenes manufactures instructions

Is there any sign of over heating on with the carriers, busbar or blades

Is the existing installation suitable for the loads and the size of cables and total demand

The possible lack of a single point of isolation

The reason for the test and the expectations of the client, ( some of the tests I do are required to have a clean sheet)

Measured Zs readings and their relation to the fitted protective devices and their disconnection times

The earthing arrangements, this is a Tn system but a TT would require replacement.

That's just a few to start and is not ment to be exhaustive as I'm walking round morrisons ATM lol
 
This could get interesting.

It's not my first house, I fitted two 8 way Wylex boards.
Yes it could, it is the sort of thread which could split the forum, thats why I posted it, the mods may have to watch this if it starts getting questions regarding it
 
a few factors would decide if I would recommend replacement .........

Is the backboard or frame of any of the 3036's made of a combustible material

How do the retro MCB's fit and interface with the existing board and do the cause any exposed parts

How does the cover fit and the subsequent fuse cover fit with these in place, as if both don't fit then this contravenes manufactures instructions

Is there any sign of over heating on with the carriers, busbar or blades

Is the existing installation suitable for the loads and the size of cables and total demand

The possible lack of a single point of isolation

The reason for the test and the expectations of the client, ( some of the tests I do are required to have a clean sheet)

Measured Zs readings and their relation to the fitted protective devices and their disconnection times

The earthing arrangements, this is a Tn system but a TT would require replacement.

That's just a few to start and is not ment to be exhaustive as I'm walking round morrisons ATM lol
Good questions. ZE is 0.20 for clarity to start with, all zs readings within what they should be, no evidence at all of any overheating, when the covers are on, no exposed parts evident, definately a TNCS system, dist board backs are wooden, however fire proof foam is between ceiling and wooden frame boards are sat on, all sockets down stairs covered by RCD, thats all of your questions answered I believe fella
 
Forgot to mention, Boards are in the garage which is part of the house and the ceilings are all fireproofed with fire boards.
 
Would personally have issue with that, and the wooden backboards due to there being no integral backs in those boards, don't think it would be enough to recommend replacement, I might suggest it as an improvement rather than a necessity
Good view, I might agree, I might not, lets see what the others say first, I have to shoot off now for an hour, but will be happy to pm you my findings when I get back if you want to know what I think.
 
A snakes nest of wiring! Before I say anything are my eyes working correctly:

1) The service head feeds the meter
2) Meter then feeds a henley block
3) Henley then feeds two '3036' boards and a single '3036' board.
4) The R/H '3036' board then feeds an 'RCD' enclosure
 
that is totally illegal and dangerous. it's just a question of whether you will be electrocuted or your house burns down. the whole house needs a complete rewire for which we will be happy to quote.


looking after your world (NOT).

yours greedily,

British Gas.
 
New posts

Reply to For new sparks who change dist boards in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
693
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
846
Fitted a remote second consumer unit to a detached annex. The supply to it was from a tncs system. The new db has been changed to a tt system for...
Replies
1
Views
782
What are people fitting in the 3 phase range just lately, I've had a scan at various makes and it seems to be a ---- up between Hager and Wylex at...
Replies
9
Views
842
Hey guys, Im starting to put my company out there more. And this is all a new journey for me being an apprentice and now being qualified/2391-52...
Replies
25
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock