Discuss Fuse board change with rear entry mounted on wood in the UK Electrical Forum area at ElectriciansForums.net

If you use rear entry you will compromise integrity of CU, you must therefore seal the openings. Two options I use is Rockwool rammed in tight, or Fire rated foam, just don't get carried away with foam............
 
The metal CU's in domestic is to contain a possible fire, not to be fire proof. Just use common sense, I also mount on wood ( so to speak!) and use a mini grinder to cut large holes in the back to accommodate a bunch of cables from all angles. So long as there are no unsheathed wires touching wood or metal...no problem. You only have to look at the old Wylex wood backed boards to see there was no issue with fire if installed properly. The only issue they had....a lack of space. I am not a fan of foam with any cables, lack of future maintenance.
 
The metal CU's in domestic is to contain a possible fire, not to be fire proof. Just use common sense, I also mount on wood ( so to speak!) and use a mini grinder to cut large holes in the back to accommodate a bunch of cables from all angles. So long as there are no unsheathed wires touching wood or metal...no problem. You only have to look at the old Wylex wood backed boards to see there was no issue with fire if installed properly. The only issue they had....a lack of space. I am not a fan of foam with any cables, lack of future maintenance.

If this was always true then there would have been no need for the current reg on 'fire resistant' CU's
 
There are no guidelines for ip ratings on the rear face


416.2.1. Live parts shall be inside enclosures or behind barriers providing at least the degree of protection IPXXB or IP2X

Doesn't this IP2X also apply to the back of CU's?

Might be me just being thick but what's the point of having a 'fireproof' CU due to fire risk and then cutting a bit hole in the back for the cables, which also lets the fire spread.
 
Sides and bottom.

But 416.2.1. implies all sides.

what's the point of having a 'fireproof' CU due to fire risk and then cutting a bit hole in the back for the cables, which also lets the fire spread.

You understand what I'm getting at with my comment above.... It just makes no sense to have no IP rating for the back of the CU.
 
You understand what I'm getting at with my comment above.... It just makes no sense to have no IP rating for the back of the CU.

I do.

But if you mount the CU on 19 mm supports, its hard enough to get a length of cable into the CU, let alone get your hand and fingers down.

However if you were to mount the CU on 300 mm supports then yo may have a point:)
 
If you use rear entry you will compromise integrity of CU, you must therefore seal the openings. Two options I use is Rockwool rammed in tight, or Fire rated foam, just don't get carried away with foam............

Why must you seal the openings? There’s a big one in the front where the MCBs go which is not sealed.

Do you de-rate the cables suitably for the increased thermal insulation you install round them?
 
We don’t have fireproof CUs, we have CU’s which are manufactured from a non-combustible material.
This means that the material which the CU is made of must not be combustible, it does not put any requirement on it being fire-proof.

Non-combustible material.... That's the wonderful phrase I was looking to use.
You all know what I meant anyhow..
 
BS7671 421.1.201 is not clear, the IET Guidance Note 4 "Protection Against Fire" seeks to clarify the intention of the regulation.
3.8.1 Consumer Units and similar assemblies in domestic premises pg. 29 states
>"The non-combustible enclosure or cabinet must provide a complete envelope (e.g. base, cover, door and any components such as hinges, screws and catches) as necessary to maintain fire containment. All blanks, circuit-breakers and other devices must be contained within the non-combustible enclosure or cabinet"
>"The installer must seal all openings into the non-combustible enclosure or cabinet for cables, conduits, trunking or ducting that remain after the installation of cables. Good workmanship and proper materials must be used and account must be taken of the manufacturer's relevant instructions, if any."

Hopefully this clarifies the situation.
 
^^ What you need to consider is that most people don't buy the guidance notes .............

If, and I say if the IET had this in mind, then it needs to be spelt out in BS 7671 18th Edition.

I would add that I've shown a number of CU's to my assessors over the years and they have never commented about the use of rear entry panels.
 
I agree it should either be in BS7671, or the guidance notes should be a compulsory addition. Personally I now have the vast majority of guidance notes as they add clarify to BS7671.

Stroma are hot on this.
 
I agree it should either be in BS7671, or the guidance notes should be a compulsory addition. Personally I now have the vast majority of guidance notes as they add clarify to BS7671.

Stroma are NOT hot on this.

Edited for you based on my personal experience

Guidance notes should be given away free for everybody paying for the 18th Edition.

Allowing the IET to produce additional documents that they can sell, is not exactly encouraging them to improve BS 7671
 
BS7671 421.1.201 is not clear, the IET Guidance Note 4 "Protection Against Fire" seeks to clarify the intention of the regulation.
3.8.1 Consumer Units and similar assemblies in domestic premises pg. 29 states
>"The non-combustible enclosure or cabinet must provide a complete envelope (e.g. base, cover, door and any components such as hinges, screws and catches) as necessary to maintain fire containment. All blanks, circuit-breakers and other devices must be contained within the non-combustible enclosure or cabinet"
>"The installer must seal all openings into the non-combustible enclosure or cabinet for cables, conduits, trunking or ducting that remain after the installation of cables. Good workmanship and proper materials must be used and account must be taken of the manufacturer's relevant instructions, if any."

Hopefully this clarifies the situation.

No it doesn’t clarify it because the thin steel which the CUs are manufactured from will not provide fire containment, fire will get through it.
Unless they specify fire containment properly then it’s impossible to meet the requirements. For a start fire containment needs to have a length of time associated with it, just look at the standard practices and regulations regarding fire barriers and compartments within buildings.

Plus the guidance notes are not part of the regulations, they are additional information. A lot of time and consideration is put in to the wording of the regulations and they are very specific, as far as I know the guidance notes are not written and approved by the full regulations committee so cannot guarantee to carry the full ‘intentions’ of the regulations.
The term ‘non-combustible’ will have been selected over ‘fire-proof’ for good reason.

What is the point in having a set of regulations where we are expected to comply with the ‘intention’ or ‘spirit’ of the regulations rather than what is clearly written?
 

Reply to Fuse board change with rear entry mounted on wood in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I had a call to a new customer who was experiencing what sounded like nuisance tripping on a kitchen ring. Some background first. It's an MK LN...
Replies
4
Views
727
Hi all, I am looking for some advice regarding old rewireable (3036) fuse boards in regards to additions and alterations. I am an electrician and...
Replies
28
Views
4K
Hi there, Any advice on this would be greatly appreciated! (Note, this is not a DIY, I'm using a fully qualified electrician, just posting here...
Replies
8
Views
648
Hi All, This might be a bit of an odd question, I would really appreciate your thoughts. I am trying to up-date my mum's home, before putting it...
Replies
9
Views
2K
Hi guys interested to know what people on here use to keep the fire integrity off the fuse board for rear entry cable entering the board. Thanks
Replies
21
Views
10K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock