If you use rear entry you will compromise integrity of CU, you must therefore seal the openings. Two options I use is Rockwool rammed in tight, or Fire rated foam, just don't get carried away with foam............
Discuss Fuse board change with rear entry mounted on wood in the UK Electrical Forum area at ElectriciansForums.net
If you use rear entry you will compromise integrity of CU, you must therefore seal the openings. Two options I use is Rockwool rammed in tight, or Fire rated foam, just don't get carried away with foam............
It’s not for ip rating, it’s for protection against fire
The metal CU's in domestic is to contain a possible fire, not to be fire proof. Just use common sense, I also mount on wood ( so to speak!) and use a mini grinder to cut large holes in the back to accommodate a bunch of cables from all angles. So long as there are no unsheathed wires touching wood or metal...no problem. You only have to look at the old Wylex wood backed boards to see there was no issue with fire if installed properly. The only issue they had....a lack of space. I am not a fan of foam with any cables, lack of future maintenance.
There are no guidelines for ip ratings on the rear face
Doesn't this IP2X also apply to the back of CU's?
Sides and bottom.
what's the point of having a 'fireproof' CU due to fire risk and then cutting a bit hole in the back for the cables, which also lets the fire spread.
You understand what I'm getting at with my comment above.... It just makes no sense to have no IP rating for the back of the CU.
what's the point of having a 'fireproof' CU due to fire risk
If you use rear entry you will compromise integrity of CU, you must therefore seal the openings. Two options I use is Rockwool rammed in tight, or Fire rated foam, just don't get carried away with foam............
We don’t have fireproof CUs, we have CU’s which are manufactured from a non-combustible material.
This means that the material which the CU is made of must not be combustible, it does not put any requirement on it being fire-proof.
Sunk in?........and I don't mean the CU....Non-combustible material.... That's the wonderful phrase I was looking to use.
You all know what I meant anyhow..
I agree it should either be in BS7671, or the guidance notes should be a compulsory addition. Personally I now have the vast majority of guidance notes as they add clarify to BS7671.
Stroma are NOT hot on this.
BS7671 421.1.201 is not clear, the IET Guidance Note 4 "Protection Against Fire" seeks to clarify the intention of the regulation.
3.8.1 Consumer Units and similar assemblies in domestic premises pg. 29 states
>"The non-combustible enclosure or cabinet must provide a complete envelope (e.g. base, cover, door and any components such as hinges, screws and catches) as necessary to maintain fire containment. All blanks, circuit-breakers and other devices must be contained within the non-combustible enclosure or cabinet"
>"The installer must seal all openings into the non-combustible enclosure or cabinet for cables, conduits, trunking or ducting that remain after the installation of cables. Good workmanship and proper materials must be used and account must be taken of the manufacturer's relevant instructions, if any."
Hopefully this clarifies the situation.
Edited for you based on my personal experience
Guidance notes should be given away free for everybody paying for the 18th Edition.
Allowing the IET to produce additional documents that they can sell, is not exactly encouraging them to improve BS 7671