Discuss Fusing of fans to comply with manufacturers recommended instructions in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Manufacturers want there fans fused to 3a on the permanent feed but the switch wire is still on the 6a MCB doing an eicr is a c2 if there is no RCD protection
 
I assume you mean as it in a bathroom or because the cable is buried in the wall? C3 for both if to a previous edition of the regs ie full supplementary bonding was in place if not C2.
 
Manufacturers want there fans fused to 3a on the permanent feed but the switch wire is still on the 6a MCB doing an eicr is a c2 if there is no RCD protection
IMO if there is a 3a fuse on the permanent line then it complies with manufacturers instruction. The switched live is only a trigger, the fan uses the permanent line to operate so a fuse on that line will serve the purpose intended.
 
IMO if there is a 3a fuse on the permanent line then it complies with manufacturers instruction. The switched live is only a trigger, the fan uses the permanent line to operate so a fuse on that line will serve the purpose intended.
Switch left on is a supply to the timer at a higher rating than the feed
 
The manufacturers want both permanent and switch line fused by a single fuse and since this involves the wiring outside the fan they cannot install a fuse in the fan.
If they only wanted the permanent line fused they could do this, but do not because that is not their intention.
From a fusing point of view the fuse is there to prevent cables being overloaded and causing fire.
From a protective point of view the fuse should disconnect the power to a piece of equipment.
Fusing the permanent line only will do the former but not the latter.
Someone removing the fuse or finding the fuse had blown might work on the fan not realising there was still a live supply to the fan (if the switch was on), though they should check for dead at the equipment and not just at the supply.
For coding this is down to the inspector, the lack of RCD protection would be a situation where in case of a fault it could give rise to danger, the lack of a 3A fuse on the switched line would be a far lower risk and almost minimal if a 3P isolator were fitted, so the coding would apply to the lack of RCD protection.
 
I’m sure this has been said before but
I’ll do it again…

A 3amp fuse on a (usually lighting) circuit that is protected by a 6amp MCB is pointless. The MCB will trip a long time before a 3A fuse will pop.

I’ve a feeling the 3A thing originally came from when the fan may be powered from something like a ring final which has a much higher current rating.
 
A lot of electricians forget that the wiring regulations stipulate that a manufacturers instructions supersedes the wiring regulations, so if a manufacturer states they require a 3 amp fuse on that product you have to install a fuse on the circuit like I mentioned previously the best way to cover this point is to install a 3amp fused spur at the loop then everything from that point onwards is protected by that fuse on both permanent and switched conductors, the idea of the 3amp fuse is to cover every eventuality on an installation from a BS 3036 fuse through to BS60898 MCB or BS61009 RCBO, I agree the MCB/RCBO would trip quicker than the fuse but at least the installation would comply with the manufacturers instructions.
 
I’m sure this has been said before but
I’ll do it again…

A 3amp fuse on a (usually lighting) circuit that is protected by a 6amp MCB is pointless. The MCB will trip a long time before a 3A fuse will pop.

I’ve a feeling the 3A thing originally came from when the fan may be powered from something like a ring final which has a much higher current rating.
Some time back there was an instance of one of these fans causing a fire, presumably it seized. It ended up in court and the manufacturers gettout was that a 3a fuse had not been fitted as per instructions. This despite the fact that we all know a 3a fuse would make no difference.
 
Some time back there was an instance of one of these fans causing a fire, presumably it seized. It ended up in court and the manufacturers gettout was that a 3a fuse had not been fitted as per instructions. This despite the fact that we all know a 3a fuse would make no difference.

Completely agree I remember reading the same article in one of the trade magazines, the blame was put back onto the installer
 
c3 if no RCD on bathroom lights but check IP ratings & zones also. Seen several installs with a split load board where the bathroom light and fan were wired off the ring via a 3a fused spur, thus providing the RCD protection.
 
Hi - sorry to be a party pooper, but a BS1363 3A fuse is more sensitive to overload than a BS60898 6A mcb. For example, the 3A fuse will always melt at 6A but the mcb will never trip.

IMG_0416.jpg
 

Reply to Fusing of fans to comply with manufacturers recommended instructions in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Just wanted to get some thoughts from other electricians who regularly do EICRS, does anyone else code a fan isolater with no 3A fuse protection?
Replies
23
Views
1K
Need to replace an old Vent-Axia extractor fan as the pull chord no longer works. I bought this -...
Replies
19
Views
1K
I've recently has an EICR (report attached) carried out on my two bed flat because I need to rent it out for a year. The electrician has come back...
Replies
19
Views
904
Installed a new ceiling fan, with no previous light or power. There is a switch in the room that controls an outlet. I am trying to draw power...
Replies
0
Views
779
Hi Everyone, New to the forum but hoping I can find a little help with my restoration project... I am adding a secondary wiring "system" to my...
Replies
14
Views
926

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock