engineer54 I have always thought a tncs system worked your way but as i have never worked beyond an installation ie in the network so have not had any experience of working with to many differnt systems. When I started my new job working along side generators two sparks there explained to me that an earth rod was not always needed on a tncs system. I did question this but eager not to look unexperienced and as they both had experience in this field and also ship wiring which uses no earth rod, I assumed I had miss understood the system. Since you pulled my comment i have found as many sources of information as I can and educated myself reguarding tncs sytems. I am happy to have been wrong as otherwise I would still be non the wiser. I have explained to these sparks and concluded that they some how had the IT system for ships and a TNCS system mixed up and that a source of earth was always required for a TNCS. Reguarding the generators most already come with a neutal earth link inside with a label on the front stating this. All the generators have rods installed, it was just the fact I was told that if removed the ocpd would still work fine, which we can safely say I know now to be wrong. Anyway thanks for pulling my comment and I think ill keep my advice to myself unless 100% sure next time, oh well
 
Well we have both learnt something from this thread then...lol I now know that marine electrical systems, use an insulated neutral arrangement...lol!!

Always better to ask questions, or ask to confirm your understanding of things, than keeping quite. Nothing stopping you giving advise on these forums, if your wrong you'll get someone here that can correct you, ...just another way of learning and picking up things!!
 
Robbie what is the trip rating in mA of the RCD part of your RCBO ?

The max Zs values for RCD's RCBO's depend on the mA rating, and are as follows:

30mA = 1667 ohms
100mA = 500 ohms
300mA = 167 ohms
500mA = 100 ohms

So your Zs values will be fine


The OCP part requires more thought, as your Ze values are low, it is the (R1 +R2) values which are giving the higher part of your readings.

If it is a TN system and a distribution circuit, a 5 second disconnection time will be allowed.

As a 25 A C type OCPD will require 250 A to operate instantaneously, 10 X 25A , 230/250 = 0.92 ohms, but if you are allowed a disconnection time of 5 secs this can be higher.

Edit; I have not included any correction factors here for clarity
 
Last edited:
This is a boat and is outside the scope of BS7671 - think you need to consult a grown up.

As a previous poster has mentioned you need to have fault monitoring devices installed.
 
Until we know the precise method of “earthing” the generator neutral it’s like trying to plat fog.

Totally impossible.

You keep prevaricating around the questions, which leads me to think you’re in the mire over your head.

I’ll PM Durham
 
hehehe!! im in no position to give advice to the un advisable!

on a water based craft we had NO earth and tbh EFLI and RCD's we unheard of in the RN..!
yes we had a constant IR monitoring system checking for Earth Faults to the Hull of the ship..! our limit was under 600k ohms then we had to investigate, on a good day 999m ohms was achievable but seen as our MG sets used to eat carbon brushes for dinner it soon dropped rapidly! out come the Air guns and rags!! on completion it seemed like scene from marry poppins and the chimney sweeps..!


any way back to the point...! do you have a Neutral Earth TX at the generator? to assist with fault current when starting up and running etc..?
 
You need a marine engineering consultant, this area is a minefield and there's many variables you need to consider before designing this kind of system. The system needs to consider safety of people on the barge as well as people not on the barge primarily but corrosion implications can cost astronomical amounts if not considered correctly.

I'm not an expert in this field but the marine projects I have been involved in have taught me you can't cut corners.
 
Hi again Robbie

The generator is likely to lose output voltage after half acycle when delivering fault current. personally would give greaterconsideration to this then I would to Zs’s.
Also. Residual current devices may become unreliable in saltladen air.
If you are going to get the blame for something badhappening it’s likely to be in connection with a job like this one so doconsider all the “what if’”s you can think of . first. Good luck.
 
Probably but there are a few salt water inlets also named loch,Please would Robbie dip his finger in (with the generator locked off) & report back

Lol, the swearword filter doesn't like you talking about salt-water.

I'll stand to be corrected but it would certainly influence the installation method. Some more info on the generators would also be nice. This is still a job I would refer to someone more qualified for a spec to be issued.
 

Reply to generators in the Canada area at ElectriciansForums.net

Similar Threads

I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
288
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
1K
Hi, any help would be greatly appreciated. I’ve been asked to wire up a second hand 3 phase pto generator to an existing generator switch (see...
Replies
2
Views
2K
As a young man, I was an electrician, but now I'm getting on, I am strictly DIY. I used to have a cheap old 900W petrol generator connected to a...
Replies
8
Views
1K
Hi, I've been asked to look at installing a generator changeover switch at a property, so that they have some level of backup in the event of...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock