also if you know any reg numbers or other type of legistation which I could look at to educate myself more on these systems would be helpful.
Enginner54 I did not say that a earth was not required at the neutral star point of the genny. I know it is earthed to the can of the genny and then on to a ground rod. As my statment read i have just started working with generators and have been informed that on a tncs system a ground rod was not always required but i know the neuteral always is earthed to the can. Also if you look in the regs at the generator system diagram the earth line to the ground is shown as opptional per system. I do not proclam to be an expert with generators and am glad you have pulled me on these comments I was just giving my view from what i have been shown. Are you saying all normal site tncs generators need a ground rod? also if you know any reg numbers or other type of legistation which I could look at to educate myself more on these systems would be helpful.
If i am reading the regs right the 1667ohm would be for the rcd part to operate correctly but anything over the 0.72 would fail for over current protection?
So could someone tell me if max zs for 25amp RCBO is 0.72ohms and test results are 3.4 ohms