Again you are mixing max Zs up with Over current protection.

Your Earth fault current is taken care of by the RCD part, which allows up to 1667 ohms for a 30mA device

Zs = Ze + (R1 + R2)
 
Last edited:
So what is the point on having that table then?? I am not used to testing where zs is higher than this table without it being a fail?
 
The OCP part follows a different path, being either R1 + Rn or R1 + R1, either phase to neutral, or phase to Phase, Ze does not play a part in this. You will probably find the fault path impedance is a lot lower (with no Ze to add).

Your EFLI path is taken care of by the RCD part.

The tables also relate to where an RCD is not used, as is the case in many applications.
 
Last edited:
As I said and the start of this posts,I am unfamiliar with these type of readings so wanted some experienced people to inform me,so these readings are acceptable that I am getting??
 
I will try to explain a bit.

Zs = Ze + (R1 +R2)

For instance a lighting circuit protected by a B type 6A MCB

If we had a Ze of say a 100 ohms, and an (R1 + R2) reading of 1 ohm.

A type B6 amp MCB requires 5 X 6A to break instantanously (5 being the multiplier for a B type device).

230/(5X6) = 230/30 = 7.6 ohms (max Zs)

Zs = Ze + (R1 + R2) = 100 + 1 = 101 ohms for our Zs value, clearly this value is far too high to trip the B6 MCB, so by adding a 30mA RCD, this will increase the max Zs allowed up to 1667 ohms, our circuit above will then trip to give the required disconnection time.
 
Last edited:
Using the above values for Short circuit/over current protection, assuming the same size CPC as our line conductor.

Our fault path this time being R1 + Rn, (R1 + Rn) = 1 ohm (which is a far lower reading without the much higher Ze), which is lower than the 7.6 ohms allowed, and so the MCB would trip in the required time.

Using an RCD does not replace the need for low (R1 + R2) values, but does mitigate the higher Ze readings.
 
Last edited:

Reply to generators in the Electricians' Talk | All Countries area at ElectriciansForums.net

Similar Threads

I am interested in having a home generator that would provide power to my home when the power is out during hurricane season, etc. I have 2...
Replies
0
Views
314
Hi everyone, I wondered if anyone could help me with something that has been niggling me please?! When a Solar PV feed in circuit is installed...
Replies
14
Views
2K
Hi, any help would be greatly appreciated. I’ve been asked to wire up a second hand 3 phase pto generator to an existing generator switch (see...
Replies
2
Views
2K
As a young man, I was an electrician, but now I'm getting on, I am strictly DIY. I used to have a cheap old 900W petrol generator connected to a...
Replies
8
Views
1K
Hi, I've been asked to look at installing a generator changeover switch at a property, so that they have some level of backup in the event of...
Replies
1
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock