just looked at a job where a glass washing machine is to be installed in a factory.
3 phase crabree board already there. plenty of spare ways and only load on the ccu is power and lighting and alarm system.

job request from customer, need a commando socket adjacent to drain to plug machine in.

the way i would install would be, three phase board 63a 3 phase breaker.
16mm to a 63a mem switch fused isolator next to board. from there run a 16mm 5 core armoured clipped direct around 45m to commando socket.

another electrician has quoted and subsequently come in cheaper as said 4 core 16mm.
and no mention of a 63a fused isolator?

advice chaps?
 
In your title it says 63a per phase, I thought WHAT! can't be. This is crazy even 20 odd amps per phase to just wash glasses! It's got to be cheaper to employ someone to do it at that draw surely. But then I installed one that was 17 ish amps per phase for a mobile bar that washes it's glasses at the base and the machine does a cycle for hundreds of glasses in a couple of hours so maybe not. Although the manufacturers insisted I should use 4mm² rather than the 2.5mm² my calcs suggested. So I suppose the other spark was going to run a 16mm² earth along with the four core or use the armour?
 
63 A MCB in DB provides OCPD and isolation of circuit. Commando plug/ socket provides local isolation of appliance. K.I.S.S. as he said ^^^^^.

and as vorti says are you sure it's 63A per phase?
 

Reply to Glass washing machine 3 phase 63a per phase in the Commercial Electrical Advice area at ElectriciansForums.net

Similar Threads

Hello All So I'm not long out of my college days and unfortunately I didn't have a lot of exposure to three phase and commercial wiring systems...
Replies
32
Views
3K
Hello, Looking for some advice following a botched 3 phase upgrade today. Some background: Commercial unit originally fitted out (4 years ago)...
Replies
7
Views
647
I have a scenario where there is a three phase DB in a commercial property where there are mixture of three phase and single phase washing...
Replies
2
Views
849
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K
I've a 3 phase storage heater currently wired to the main fuse box in an office I have. The heater has 2 supplies/isolators, 1 for charging at...
Replies
0
Views
907

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock