Hi Guys

After bit of advice please....

Called back to kitchen job today, Hamilton light switch we fitted has burnt out?!
Normally decent gear so just trying to make sure nothing we have done (as Client not so friendly on this one.)

Switch in question is powering all the feature lighting which consists of:

4x75watt (240watts being used) & 1x40watt (30watts being used)/ 24v drivers running various LED cabinet lights.

Trying to check back spec of drivers can only find data sheet for 100watt version so be less than this:
Input 1.2amps so well under 10amp rating of switch and even before that it's on own 6a rcbo (new db installed) which would trip if overloaded.
But on spec sheet has inrush current <15amps, could this be causing the prob ? Not something I'm so familiar with being honest.

Hoping it's just the switch

Thanks Sy
Screenshot 2023-03-17 at 14.48.44.png
 
Any photos? Has it burnt out around the switch mechanism, or around the terminals?
 
Any photos? Has it burnt out around the switch mechanism, or around the terminals?
melted point on side - terminals blackened also, but cable were still in there tight.
 

Attachments

  • IMG_8481.JPG
    208.6 KB · Views: 19
  • IMG_8480.jpg
    309.8 KB · Views: 20
Is it just me or does the C and E marking look very close together?

Dodgy copies???

Not saying it is, but maybe worth a check.

Edit.

Added photo.

This is what I’ve got to hand… oral B electric toothbrush. CE mark looks to have a space between.

13975AC3-1E27-442E-8591-C7B45D0B5516.jpeg
 
I would remove the yellow cover .Would give more detail . Never had ONE issue with hamiltons .Very nice gear
same here.. decent stuff used for yonks !

I'm going to send back as less than 12months old and was bespoke item cost £25.
so don't really want to pull part and not be able to get back together... if you know what I mean.
 
I'd be very surprised if an instantaneous theoretical 15A inrush would cause that amount of damage - has it failed open or closed? There must be hundreds of thousands of 10A switches interrupting LED drivers up and down the land without issue, why should this one be any different?

I would be sending it back to Hamiltons for an inspection under warranty to see what they have to say.
 
I'd be very surprised if an instantaneous theoretical 15A inrush would cause that amount of damage - has it failed open or closed? There must be hundreds of thousands of 10A switches interrupting LED drivers up and down the land without issue, why should this one be any different?

I would be sending it back to Hamiltons for an inspection under warranty to see what they have to say.
failed open.... it's going back to Hamilton, see what the outcome is
 

Reply to Hamilton switch... burnt out ! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hoping someone can give some input on what could be possible causes of what happened here. I am going to investigate the situation next week but...
Replies
27
Views
2K
I’m running in cabinet led strip (tape) lighting using DV24V strips powered by a 24V 60W driver. I had tried to use a lower wattage driver for the...
Replies
1
Views
846
Hello everyone. Thank you in advance for any help you can provide. I tried installing a dimmer to a 3-way circuit. The dimmer has a hard...
Replies
3
Views
1K
Doing some testing today on a Wet Room installation. Fed from its own small CU. And consists of 2 x seperate 50A (for 10.5kw shower) circuits...
Replies
23
Views
3K
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock