Called back to kitchen job today, Hamilton light switch we fitted has burnt out?!
Normally decent gear so just trying to make sure nothing we have done (as Client not so friendly on this one.)
Switch in question is powering all the feature lighting which consists of:
4x75watt (240watts being used) & 1x40watt (30watts being used)/ 24v drivers running various LED cabinet lights.
Trying to check back spec of drivers can only find data sheet for 100watt version so be less than this:
Input 1.2amps so well under 10amp rating of switch and even before that it's on own 6a rcbo (new db installed) which would trip if overloaded.
But on spec sheet has inrush current <15amps, could this be causing the prob ? Not something I'm so familiar with being honest.
Hoping it's just the switch
Thanks Sy