By the way this is the manual I found online..
Discuss Heating Wiring Problem - cylinder thermostat not working in the The Welcome Forum area at ElectriciansForums.net
I just loaded a manual from Google instead of their website and it looks more like yours. It appears that it doesn't accept any switched live but expects a switched signal between 3 and 4. The orange and grey cores are the switched ones from the valves and could be used for that.sure - do you mean the boiler label (below)?
I WAS TOLD THIS PCB IS NEW!! I paid ÂŁ250 for it... did the guy rip me off bringing me a used one??
View attachment 100150
I just loaded a manual from Google instead of their website and it looks more like yours. It appears that it doesn't accept any switched live but expects a switched signal between 3 and 4. The orange and grey cores are the switched ones from the valves and could be used for that.
Do you have a meter to test that there is 230v on terminal 4?
The white flex appears to be connected in all the right places, albeit sub-standardly.sure - do you mean the boiler label (below)?
I WAS TOLD THIS PCB IS NEW!! I paid ÂŁ250 for it... did the guy rip me off bringing me a used one??
View attachment 100150
Also the pump usually runs on for a few minutes after the demand for heating or hot water has ceased, in order to take the excess heat away from the boile.sure - do you mean the boiler label (below)?
I WAS TOLD THIS PCB IS NEW!! I paid ÂŁ250 for it... did the guy rip me off bringing me a used one??
View attachment 100150
I just loaded a manual from Google instead of their website and it looks more like yours. It appears that it doesn't accept any switched live but expects a switched signal between 3 and 4. The orange and grey cores are the switched ones from the valves and could be used for that.
Do you have a meter to test that there is 230v on terminal 4?
Hi, thanksThe white flex appears to be connected in all the right places, albeit sub-standardly.
I would turn the heating and hot water to the off position and then check to see if there is any voltage between neutral and the grey wire. The boiler and pump should only fire up when there is a demand for either heating or hot water or frost protection situation, which is highly unlikely at the moment, due to all the glorious sunshine.