Discuss Help cable calculation please newbe in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
10
I have a design unit and 14 circuits to do. Can some one please help as I have completed 1 of my knowledge and before I crack on any help on this would be great. It's a rough copy so excuse the mess. Thanks. It's question 4. Thanks
15306247718722410266349729000938.jpg
15306248122057682730515543286264.jpg
15306247718722410266349729000938.jpg
 
So far the information you have given as answers appears correct, there are a couple of minor points to note (in bold).
question 4 only.jpg

a. Design current is the expected load in watts divided by the supply voltage. You have stated 1900W/230V =8.26A
b. Based on the design current the circuit breaker must be rated higher than the design current, for a load of 8.26A the next highest standard breaker rating is 10A so the minimum is 10A but higher can be used, also the characteristics of the load may require a type B, C or D circuit breaker. If the load does not show high current peaks on starting (or stopping) then a B type breaker is a good choice.
As the circuit is part of a swimming pool and assuming it is not SELV or electrically separated then it would require 30mA RCD protection as well.
c. The cable appears to be twin and earth cable installed in conduit on the surface, not a usual choice, but this would be installation method B, however BS7671 does not give tabulated current ratings for twin and earth in conduit, but insulated and sheathed multicore cable tables are pretty close.
d. from your answer the only rating factor that applies is an expected ambient temperature of 40°C (Ca at 0.91)
e. Determining the minimum csa for current carrying capacity means applying the rating factors to the In (16A in your case) as a divisor and referencing the appropriate table and installation method. With a corrected design current of 17.58A the minimum csa live conductor that can carry this load is 2.5mm² (for multicore cable thermoplastic insulated and sheathed).
Determining the minimum csa for voltage drop would mean a rearrangement of the usual equation to say:
mV/A/m (min) = (Max volt drop permitted * 1000) / (Ib*L)
Max volt drop for lighting is 3% of supply voltage, for a 230V supply this is 6.9V, Ib is 8.26A, L=46m
mV/A/m(min) = 6900/8.26*46 = 6900/389.16 =18.16 mv/A/m
From the tables of volt drop the next size of cable that has a volt drop <=18.16 is 2.5mm² as 2.5mm² has a volt drop of 18 mV/A/m.
f. The actual volt drop can now be calculated as you have done and got 6.83 V just within the 6.9V limit for lighting.
g. For 230V final circuits <=32A: on TN system earthing 0.4s, on TT earthing 0.2s; for distribution circuits and >32A circuits: TN system earthing 5s, TT earthing 1s.
h. earth fault loop impedance is calculated from Zs = Ze = (R1+R2) as you have done.
Because you have used resistance values at 20°C this would be equivalent to a measured value and so the maximum Zs you would refer to would be from the OSG and for a B16 this would be 2.2Ω (0.8* the BS7671 value to correct for temperature of the conductors).
i. the maximum earth fault loop impedance stated in BS7671 is 2.73Ω, this is different from the value you have given (2.87) because it is taking into account the Cmin value of 0.95.

Overall pretty good, I think.
 
noticed you had 1.44 Zs for a 16A RCBO. should be 2.88.(if a type B). if you are using type C, then i stand corrected.
 
Would you recommend using all type B breakers m8. I am cracking on today and there is no cost involved I can use any breakers I like and and chose rcbos for the extra protection. Thanks Telectrix
Also was it not 1.97 thanks
 
2.88 before applying correction factors. 230V/(16 x 5), for type B. depending on the type of lighting, i.e. if florry or LED with high inrush currents, go for type C,
 
I am not sure why your Ze (not ZE) is 1.01Ω.
On your previous post the length of circuit was, I thought, 46m it is now 40m.
Remember to use the correct case for your symbols.
The first Zs value you give (in b) for the circuit breaker is the one from the previous edition of BS7671.
Work out your volt drop calculation again in sections e and f and select your cable size on this basis. This affects the later calculations.
Check what page in BS7671 gives you maximum disconnection times, which is what is asked for in g.
h starts the line below g. Remember you state at the top your design parameter is single core cables and so you have a choice of cpc size, it is not dictated by the twin and earth values.
you have labelled as H the answer for i.

An example answer for your reference since you have been working on this and are getting very close.
Swimming Pool Floor Plan – Pool Lights Ze = 1.01 Ω TNCS 0.35 Ω

Design Specifications

Ca = 40 °C (ambient temperature)

Wiring system – 90 °C insulated unsheathed cables in PVC conduit

a) Design Current (Ib) = Power rating of equipment / voltage

19 lights @ 1900 W total 1900/230 = 8.26 A

b) Circuit breaker selected 10 A Type B RCBO to BSEN61009-1 (with maximum Zs of 4.37 Ω)

In = 10 A

c) Installation Method – B – singles in PVC conduit

d) Rating factor that applies ambient temperature (Ca) @ 40 °C, Ca is 0.91

e) Minimum csa of cable for current carrying capacity

It >= In / factors It is the minimum rating for the cable to be selected

It >= 10/ 0.91 = 10.98 A

From table 4E1A 1mm² cable can carry 17 A for reference method B and so is the minimum csa for current carrying capacity.

Minimum csa for volt drop, volt drop limit for lighting is 3% of supply voltage = 6.9V
mV/A/m = (max Vd * 1000) / (Ib *L) = (6.9*1000) / (8.26*40) = 20.88 mV/A/m

From table 4E1A the nearest cable size with a mV/A/m <20.88 is 2.5mm² cable at 19 mV/A/m.

The minimum csa cable that can accommodate both current carrying capacity and volt drop is 2.5mm² cable.

f) Actual volt drop

Vd = (mv/A/m * Ib * L) /1000 = (19 * 8.26 * 40)/1000 = 6.28 V

g) From p.55 table 41.1 BS7671 10A Type B RCBO BSEN61009-1 disconnection time of 0.4s for a final circuit <=32A on TNCS.

h) Using 2.5mm² line conductor and 1.5mm² cpc.

(R1/m+R2/m) * L / 1000 = (7.41 + 12.10) * 40 /1000 = 0.78 Ω at 20 °C

Compensating for a conductor temperature of 90 °C multiply by 1.28 = 0.998 Ω

Zs = Ze + (R1+R2) = 1.01 + 0.998 =2.01 Ω @ conductor temperature of 90 °C

i) The maximum Zs given in BS7671 on p.58 for a 10 A RCBO to BSEN61009-1 with 0.4 s disconnection time is 4.37 Ω.
 
Sorry my head is done in as I have basically been left in the lurch and I finish next week hmm. It's appreciated tho allot Richard. They know I am a little dyslexic but I started course late and because of founding am 33yr old.
 
Sorry I am out of time at the moment, but on a quick look the actual Ze at the origin of the installation is 0.09 Ω.
Then there is a supply to your distribution board and at that board the Zdb is 0.11 Ω, note this is different from 1.01 Ω.

For your calculation use the value 0.11 Ω as the additional resistance from the non final circuit part of the fault path, equivalent to Ze for your calculations.

On a quick view the numbers look right for your first post about circuit two but disconnection times are on p.55 not p.58.

On the redone one you have the calculation for volt drop wrong.
The answer you get (6.2V) is for a mV/A/m value of 19, which would be 2.5mm² cable.
You have written the calculation using 31 which is the value for 1.5mm² cable. This makes all the following calculations wrong because the cable size is incorrect.
 

Reply to Help cable calculation please newbe in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Happy New Year all. Quick question regarding cable sizing. I have a 25m run from DB to car charging unit. The 25m run will mean approx 8m is run...
Replies
5
Views
673
Hi. Im looking for some advice when calculating submain cables. Basically there is a new connection of 80Amps that is to be used for a dwelling...
Replies
5
Views
392
Hi everyone, On a job at the moment and trying to Work out cable size needed for property supply. Lots going on and struggle to work out...
Replies
10
Views
406
Help please! I need a Tesla Gen 2 EV charger fitted in my garage which is 22m from the consumer unit. My electrician is proposing to route a 6mm...
Replies
15
Views
2K
Hi all, New to the forum. I have been asked to look at this for one of our guys who's had an issue onsite after some electrical works had been...
Replies
4
Views
788

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock