Ner123ak

Hi
We have just spent quite a lot on having a new kitchen in another part of our house. This was a complete installation including new electrics plumbing etc.
It us now apparently finished and quite frankly the electrics scare me
The power cables are running in and out of the radiator pipes everywhere for a start. When I asked I was told it's ok it's heat protected cable.
Couple of pictures below I have many more from all over.
The hob and oven are just on a 13 amp plug and that don't seem right to me as well. The whole work is quite shocking but I will stick to electricals image.jpgimage.jpg
Please could someone help me as I don't know what I should do
thnx v much for any advice
k
 
I was going to put this in the diy section but you may get more help in the main forum if you are just asking for opinions.
 
Picture 1 needs to give a larger view for any useful comment
Picture 2 is bleak,very bleak

A oven on a plug top may or may not be adequate,it depends on rating
Hob on a plug top sounds very iffy to say the least

You need more pictures and much more info to be provided
There are skill/quality and building regs questions that will need answering

Who engaged the worker doing these electrics
Was he an electrician is the first question
Were references sought
Was he chosen because he was extra cheap
 
looks very rough. may be worth getting another electrician to have a look and test the installation. if theres is some serious issues have the first contractor come and sort it out...
 
Hi
We have just spent quite a lot on having a new kitchen in another part of our house. This was a complete installation including new electrics plumbing etc.
It us now apparently finished and quite frankly the electrics scare me
The power cables are running in and out of the radiator pipes everywhere for a start. When I asked I was told it's ok it's heat protected cable.
Couple of pictures below I have many more from all over.
The hob and oven are just on a 13 amp plug and that don't seem right to me as well. The whole work is quite shocking but I will stick to electricalsView attachment 28425View attachment 28424
Please could someone help me as I don't know what I should do
thnx v much for any advice
k

Is that a concrete floor and WHY are the copper pipes just lying on it?

Those pipes below the socket ..... the clips aren't closed onto them. It's not "that" important but it's quick and easy to close them but if they can't be arsed to do that what else had been skimped on??

If those pipes are for central heating they can be running at 80 degrees C for long periods. I'm not sure I would want cable as close as those are!!

Is your hob an electric one or is it gas with electric ignition?

Finally, did these contractors arrive at your premises in a motor vehicle or a horse drawn covered wagon? :cowboy:
 
Last edited by a moderator:
...Looks like a pretty common attempt,where the electrical part of your project has taken a lower priority on your contractors' list...

I genuinely feel for the OP.who probably went through the process of getting quotes,and assumed all players read from the same hymn sheet.

See this,and much worse,every month. Last one was an impressive,and expensive two-property rear orangery,bi-folds and feature log burner...the works. The door to the kitchen,opened in to the addition,and a cupboard/shoe store had been built on the lock side.

A double S/O had been fitted on the side of this,30mm pattress,cables in cupboard in trunking...all neat...until you plugged something in and tried to open the door...

Owner had asked my opinion on this issue,although several rational options were apparent...someone needed punching :icon12:
 
Shoddy lazy work. I feel for the OP as they should give the, ahem, electrician, cough, splutter, the chance to rectify the issues. But I would not want someone like that anywhere near my house ever again. The grey cable is not heat resistant and I doubt the white flex is either. So shoddy work and a liar. And I hope the hob is gas with electric ignition!

More photos as others have suggested. May be worthwhile talking to another local electrician expressing your concerns and seeing if they can spend an hour to give it a visual check over.

GOOD LUCK!!
 
Caveat emptor: Employing a kitchen fitters to carry out other trades is a recipe for disaster.

The law provides for recompense against poor workmanship. If the OP is aggrieved only he can take it up with the kitchen fitters.
 
Hi.people sorry late reply just back from work to let the electrician in to apparently put things right
We paid half the money before work started. We are supposed to get certs when we pay the remainder.
Update so the electrician has just been round again and has put trunking around the cables and moved away from pipes a bit and tidied up the cables strewn across the loft. Although I haven't looked too close and will post some pictures later.
Our other worry the hob and oven just on two 13 amp plugs to the wall. He just baffled me with numbers and when I said. I don't see plugs mentioned in the installation manual He said its because people would try and plug them into light circuits. I replied I've never seen a light switch with a plug socket in it and why wouldn't they just plug it in the wall anyway. But then got swamped with techno talk
i really appreciate all the kind responses and will post back later when we are home
thnx all again
 
Hi.people sorry late reply just back from work to let the electrician in to apparently put things right
We paid half the money before work started. We are supposed to get certs when we pay the remainder.
Update so the electrician has just been round again and has put trunking around the cables and moved away from pipes a bit and tidied up the cables strewn across the loft. Although I haven't looked too close and will post some pictures later.
Our other worry the hob and oven just on two 13 amp plugs to the wall. He just baffled me with numbers and when I said. I don't see plugs mentioned in the installation manual He said its because people would try and plug them into light circuits. I replied I've never seen a light switch with a plug socket in it and why wouldn't they just plug it in the wall anyway. But then got swamped with techno talk
i really appreciate all the kind responses and will post back later when we are home
thnx all again

Have you got the make and model numbers for the oven and hob?
 
Last edited by a moderator:
The first thing to ascertain is, ...is this a particularly rough qualified electrician, or a DI (Domestic Installer) that at best has been to a training center for 5 Weeks or at worst , for just 17 days??

My guess is the latter, and a perfect example of why these chancers should not be allowed into people homes....

Anyway what are you, or should i say, how far are you prepared to go to get your electrical installation back to a reasonable expected standard??

How about posting a few more photo's of what you are considering not up to scratch or indeed dangerous...
 
Here's a couple more pics top and bottom going up wall into loft.
Also worryingly I think for us the hob and oven are electric they are Lamona side control hob. Lamona fan assisted oven. LAM3301. Will post pictures later
We will be giving him a chance to out things right. But are still very worried about and would appreciate all comments.
thnx
 
The first thing to ascertain is, ...is this a particularly rough qualified electrician, or a DI (Domestic Installer) that at best has been to a training center for 5 Weeks or at worst , for just 17 days??

My guess is the latter, and a perfect example of why these chancers should not be allowed into people homes....

Anyway what are you, or should i say, how far are you prepared to go to get your electrical installation back to a reasonable expected standard??

How about posting a few more photo's of what you are considering not up to scratch or indeed dangerous...

This has all the hall marks of a kitchen fitter doing the work and a spark coming to test and sign ofF. Done lots by very established sparks from my experience.
 
Here's a couple more pics top and bottom going up wall into loft.
Also worryingly I think for us the hob and oven are electric they are Lamona side control hob. Lamona fan assisted oven. LAM3301. Will post pictures later
We will be giving him a chance to out things right. But are still very worried about and would appreciate all comments.
thnx
no pics!
 
Is there no way the OP can find out if the guy is actually an electrician?
Should'nt the electrician have proof?
 
Is there no way the OP can find out if the guy is actually an electrician?
Should'nt the electrician have proof?

I think it's perfectly reasonable for a client ask to see an artisans qualifications. Any decent electrician will be only too proud to show them too, ....unless he hasn't got anything apart from a couple of worthless add on things...
 
Let him rectify any works he has said he would, ask for a certificate first as he cannot withhold it as a bargaining chip for payment, (the cert is his way of saying the work he has done is compliant and up to a good standard).. arrange a day to pay but in the mean time get a registered company to assess his work and give you there opinion (verbally at first), if its a bad report ask them to do an inspection on the new kitchen works and write a report up for you... it may be a little more money but may save you a lot of aggro' in the long run if he knows you have had someone who's competent inspect his work... If it is in questionable condition then I would withhold final payment until all issues have been resolved at no extra cost...

If he then gets arkward and refuses and demands payment - explain that you will get another company in to rectify the work to meet regulations and will deduct it off the final bill, any issues with you doing so express you will get a solicitor involved.


Try do all communication by Email or text or recorded calls.... show in these that you have given plenty of opportunity for the work if substandard to be rectified.
The more evidence you have the tighter the corner he gets backed into is.
 
Last edited:
image.jpgimage.jpg

Sorry thought these had loaded.
He apparently works for a known company that I don't want to name. We haven't seen any qualification. I should have asked I know.
The hob manual LAM1701 1702. Hob left front 1700 rear left 1200 rear right1200. Front left 1700
total power5800 watt
cable type. HO5V2V2-F 2.5 mm 3 core or equiv min. Which on readin worry some as he told me he had changed it to a 1.5
Oven. LAM3301 2.4 kw
Both manuals say should be connected to a double pole control unit I did bring this up but was swamped with jargon like I said
Will post pic of plugs when get sent them from home.
thx all
 
totally unacceptable. that cable should be supported throughout it's length. as for the hob, it need to be hard wired through a 45A isolator and a cooker connection point. same with the oven. if located close together, a single 45A isolator and a dual outlet CCU will suffice. feed cable should be 6mm on a 32A MCB.
 
Darkwood thns
Probably the only sensible thing we did was conduct everything by email. Even him telling us it's ok they are heat shielded cables. The hob and oven on plugs is ok
They have already mailed us the final bill We have never not paid a bill in our lives and don't like the thought if all this hassle at all. But I will not pay till satisfied and that does seem a long way off .
Already 5 k down the drain time to stop the leak.
thnx
 
image.jpgHead is now at saturation point.
Home now to listen to the voice recorder I hid when I went back to work leaving them alone to sort things out.
Sly I know but our backs against the wall.
Heres the plug for the cooker n hob.
 
New posts

Reply to Help new kitchen nightmare in the UK Electrical Forum area at ElectriciansForums.net

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock