Discuss Help what test do you carry out on the off peak ccu in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Reaction score
1
hi what test do you do and how do you put it down on niceic installation certificate for off peak heating (economy 7). They on on the same ccu as the rest of the house but it is a dual feed ccu (2 sets of tails) same main earth

I have done: insulation, R1=R2

thanks!!
 
Still the same head, and by the sounds of it the same consumer unit too, test as one unit and right a note saying that off peak zs has been calculated or as done people I know do lim, lim, lim, lim
 
2 separate sets of circuit details and test tesults with the headings filled in for each, ie ze, pscc, rcd details, db designation etc.
Sheet(s) 1, shows circuits 1 to 8 for example and sheet(s) 2 shows circuits 9 to whatever.
You have 2 suppplies, 2 main switches etc so basically treat it as 2 dbs.

Boydy
 

Reply to Help what test do you carry out on the off peak ccu in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi, So I'm trying to understand what's going on with my off-peak electricity supply, as something's wrong with it and I'm trying to determine if...
Replies
5
Views
1K
Hi, need some advice, I moved over from Sse in 2020 to Octpus energy. Whilst I was with SSE I was on E10 when I went over to octopus they put me...
Replies
1
Views
439
Hi Absolutely 0 knowledge of this so excuse language / terms / explanation. Electric only ground floor 2 bed flat ( 3 external walls) On peak...
Replies
59
Views
5K
Recently visited a new build to do a very minor job and spotted a few dodgy looking items so Client asked me to do an EICR. Following items I...
Replies
6
Views
951
Hi, My flat uses an Economy 7 tariff. When I use the boost heater, it works fine. But the off-peak water heater doesn't heat up the water...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock