Discuss Hey guys, what does for example 300A rating on a 3 pole MCB means? in the The Welcome Forum area at ElectriciansForums.net

Reaction score
2
Hey guys, what does for example 300A rating on a 3 pole MCB means? Does it mean each phase carries 300A i.e. (Current in R=300A, Y=300A, B=300A) or it represents total currents in all the 3 phases i.e.(Current in R+Y+B=300A)?

Please assist, it is confusing me a lot with my calculations of breaker ratings, thanks to all helping hands I advance.
 
300A per phase.
just think of it as 3 x 100A single phase breakers joined Together.
 
300A per phase.
just think of it as 3 x 100A single phase breakers joined Together.
Hi thanks for ur reply but now I am even getting more confused!
Here is why,
I have a 300A 3 pole MCB connected breaker which has a load current per phase as follows:-
R=101A, Y=98A, B=118 all summed up totalling to 317A ... you said I should think of it as a 100A per phase system and NOW I have above issue at hand where R and B phase is above the 100A and the MCB is tripping after some times of operation, not frequent but it's nuisance sometimes once in a week or even once in a fortnight, but one time it tripped three times in a week!!!

The question is, does it mean the R and B phase is loaded leading to Overload????? The breaker is rated 300A. Thanks once again.
 
Oops, as @Risteard pointed out my typing mistake should read 3 x 300A

you either have a faulty breaker or the load on at least one phase is going over 300A by a considerable margin.
 
Hi thanks for ur reply but now I am even getting more confused!
Here is why,
I have a 300A 3 pole MCB connected breaker which has a load current per phase as follows:-
R=101A, Y=98A, B=118 all summed up totalling to 317A ... you said I should think of it as a 100A per phase system and NOW I have above issue at hand where R and B phase is above the 100A and the MCB is tripping after some times of operation, not frequent but it's nuisance sometimes once in a week or even once in a fortnight, but one time it tripped three times in a week!!!

The question is, does it mean the R and B phase is loaded leading to Overload????? The breaker is rated 300A. Thanks once again.

James had an unfortunate typo in his response. The rating on circuit breakers is per phase, so a 300A is 300A on each of L1/2/3.

On a side note, it's very unlikely your breaker is an MCB (Miniature Circuit Breaker). They top out at about 100-120A, you are probably dealing with an MCCB (Moulded Case Circuit Breaker).
 
Not sure if it was a typo or a brain fart moment!
was thinking 3 x 300 but somehow 3 x 100 got on the page And I didn’t notice.

top marks to @davesparks for calling me out on it, I don’t get many disagree marks but that one was well deserved.
 
Not sure if it was a typo or a brain fart moment!
was thinking 3 x 300 but somehow 3 x 100 got on the page And I didn’t notice.

top marks to @davesparks for calling me out on it, I don’t get many disagree marks but that one was well deserved.

Not sure if it was a typo or a brain fart moment!
was thinking 3 x 300 but somehow 3 x 100 got on the page And I didn’t notice.

top marks to @davesparks for calling me out on it, I don’t get many disagree marks but that one was well deserved.
Thanks @James & everyone, now I get it 100%. (300A per phase for a 300A 3 pole rated MCCB, it's actually MCCB not MCB as i mentioned b4🙏) Thanks so much once again for support and response from everyone
 
James had an unfortunate typo in his response. The rating on circuit breakers is per phase, so a 300A is 300A on each of L1/2/3.

On a side note, it's very unlikely your breaker is an MCB (Miniature Circuit Breaker). They top out at about 100-120A, you are probably dealing with an MCCB (Moulded Case Circuit Breaker).
Thanks a lot @ElectroChem , I've got it clearly. It's actually MCCB not MCB as I mentioned b4
 

Reply to Hey guys, what does for example 300A rating on a 3 pole MCB means? in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Absolutely losing my brain here guys What I would like to be able to do is power our 3 phase motor on a single phase supply. Thought I had it...
Replies
3
Views
654
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
446
Hi - just after thoughts on this please. I've been doing some testing on a 20 year old MCC. On the original EIC, Ze was reported as 0.04 R, PFC...
Replies
18
Views
2K
Hi all, Just to be clear, I'm not looking for advice on upgrading but rather just clarification of our existing setup. We need to upgrade the...
Replies
12
Views
1K
Hi all, I have a question regarding the breaking capacity of circuit protective devices. So, the breaking capacity rating of devices in domestic...
Replies
13
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock