Hi,
I'm sorting out an off grid installation and I've been provided with 25mm cable labelled "Hi=Flex 25mm CE made in EU" to connect the batteries to an inverter. Looking them up they appear to be rated at between 140A and 170A depending on which website you go to.

Now the batteries will be providing 24V to a 3kW inverter, so the cables only need to carry 125A, so there is going to be a 125A inline fuse. If these cables are rated correctly everything should be good.

I've only been able to find one document which implies these cables are to BS6862 and has it's own data table. Question is are they to BS7671 or am I going to have to list these in the paperwork as a departure ?
 
Last edited:
I assume you have H07RN cable. It complies with BS7671
This is the dilemma I've got. If I go with the cables listed in BS7671 I'd have to go up to 35mm. On further research these cables are specifically designed for 100V or less applications where high current is present, and need high flexibility and a high probability of being used outdoors temporarily or environments where there is a high probability of prolonged vibration (ie Cars, Caravans etc)
 
Why not call a cable manufacturer for their recommendations & BS standards? Or go with the 35mm cable as BS 7671 assuming they will fit the terminations on the inverter. If put down as a departure then you are almost saying the cable you fitted was not really suitable for purpose. Is the installation indoors/outdoor or both?
 
Tri-rated cable is easy to use and generally available by the meter, for example:

Bear in mind some auto cables are short-term rated (e.g. for jump leads) and others like tri-rated have assumed working temperatures as high as 110C which is unsustainable for many accessories, so look at the BS 7671 table for the method and, say, 70C PVC when looking to size the CSA needed. I would be thinking 35mm here.

Finally voltage drop - it will seriously bite you are ELV and may impact on the behaviour of the inverter, if not on the overall power efficiency under load. If the cables are of any non-trivial length you might be in for a very large cable.
 
Also generally battery cables are in free air from battery to chassis or to starter motor solenoid, a bit like meter tails, so they need significant de-rating if clipped to a surface or enclosed in any sort of trunking or conduit.
 
I've been provided with 25mm cable labelled "Hi=Flex 25mm CE made in EU" to connect the batteries to an inverter. Looking them up they appear to be rated at between 140A and 170A depending on which website you go to.

Now the batteries will be providing 24V to a 3kW inverter, so the cables only need to carry 125A, so there is going to be a 125A inline fuse. If these cables are rated correctly everything should be good.

I've only been able to find one document which implies these cables are to BS6862 and has it's own data table. Question is are they to BS7671 or am I going to have to list these in the paperwork as a departure ?
 

Reply to Hi-Flex Cable CE Made in EU ? in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
446
Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
I don't "do" solar, but I've been asked to comment on an aspect of a new domestic solar installation by others. There is no overload or fault...
Replies
7
Views
1K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K
So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
553

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock