Search the forum,

Discuss Hot tub installation ! in the UK Electrical Forum area at ElectriciansForums.net

If the hot tub was located on bare ground or grass, i think i'd be also installing a rod, even if it was a TN-S supplied installation. Your still going to get a potential difference between true earth and the DNO TN-S earth.....


As for the Regs, i think they state somewhere, that a TNC-S supply can be used, for supplying hot-tubs and the like provided an earth electrode of a certain value is also provided.... I think that value was around 20 ohms, but i wouldn't swear to it...

Nothing like PME E54, i very much doubt you would feel any sensation on a TN-S.

As for an Electrode on a PME, for it to be any use you would be looking at very low single figures.

A lot of these Hot Tubs are class II as well.
 
Further back in this thread it was mentioned that someone had a small tingle while getting in and out with tncs to that why I've decided to tt. As long as I can get less than 199 ohms.

- - - Updated - - -

Only kidding about the 199. Don't start biting me
 
I replied in the other thread, I installed my tub using the supplied tncs earthing arrangement also putting a rod in at the tub end. This rod was well below 22 ohms as stated in the regs, the only problem I had was when you got out the tub and one leg was on the floor and one in the water you could feel a shocking feeling, slight difference between true earth and suppliers earth, therefor I disconnected the suppliers earthing and made the tub tt. Alls fine now so that's how I install them from now on!
From page 2 also he said the voltage between the water and earth rod was only 2 v
 
Further back in this thread it was mentioned that someone had a small tingle while getting in and out with tncs to that why I've decided to tt. As long as I can get less than 199 ohms.

- - - Updated - - -

Only kidding about the 199. Don't start biting me

On a PME, yes its very possible, its also possible if you TT it to, be careful where you put that rod:)

If it class II where's the risk?
 
I may be wrong here but...l even if it is class two would the element still be in contact with the water, anyway the one I'm doing this week is class one, no exposed metal but when you open the cover the pump and heater unit are metal

Back to the post I copied, personally I don't think youd feel the 2 v so the insulation in the heater is breaking down when getting hot. 2 nod thing the rcd should trip at a max of 50 v probably less
 

Reply to Hot tub installation ! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
717
I have someone that wants a hot tub installing and it’ll be my first time, I have came up with anxixeaxfwanted to check it was correct. I wanted...
Replies
10
Views
1K
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K
Hi Guys So I've never installed a hot tub supply before so take it easy on me. I've spent a bit of time researching it myself and its a minefield...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top