Discuss Hot tub installation ! in the UK Electrical Forum area at ElectriciansForums.net

If you're getting a tingle somethings very wrong

I believe its because everything is bonded back to an earth bar in the control box, including the pumps casings and frame, elements heating tubes etc, there is a little earth leakage from the heating element and in turn you feel it when you touch suppliers earth (in this case the water is included as its being heated and running through the heating pipes and being pumped) and true earth (in this case the concrete floor ( I had not finished the decking) not enough to hurt but enough to feel it! Iv heard of it before, a boy sat in the tub and his girlfriend who was standing on the bare ground and she gave him a kiss and got the tingles lol!
Anyway mines all fine now it's TT. Even when it was tncs with earth rod I still got the 2v pd so I isolated the suppliers earth at the hot tubs consumer unit
 
Nothing like PME E54, i very much doubt you would feel any sensation on a TN-S.

As for an Electrode on a PME, for it to be any use you would be looking at very low single figures.

A lot of these Hot Tubs are class II as well.

I didn't say it was anything like PME. However, there is still a real difference between an electrical supply TN-S earth and true earth. A potential difference will be present. Now if were talking about this hot tub being located on wooden decking, i wouldn't bother with installing a rod at all, but on bare ground or grass, ...always better to air on the safe side.

You could well be right about some of these tubs now being Class 11, but i've personally never come across one to date...., But then most of the units i've worked with or come across, have been American and Canadian jobby's and most of those are supplied with an earth rod as part of the installation kit... Also, most of those hot-tubs have integral RCD's in the control panel...
 
Also, most of those hot-tubs have integral RCD's in the control panel...

if they are USA / Canadian built then the rcd's arent going work with a UK supply.

Anyways , the hot tub install i mentioned earlier was all wood construction with metal internal control boxes that can only accessed by removing a panel using a tool
i consider this a class 2 piece of equipment , dont know how others may feel ?
 
if they are USA / Canadian built then the rcd's arent going work with a UK supply.

Anyways , the hot tub install i mentioned earlier was all wood construction with metal internal control boxes that can only accessed by removing a panel using a tool
i consider this a class 2 piece of equipment , dont know how others may feel ?

All higher powered equipment in the States like cooker ranges, tumble dyers, etc etc, are 220/240 volts.... Hence ALL hot tubs in the States and Canada are 220/240 volts... Never seen a 115 volt hot tub anywhere.
 

Reply to Hot tub installation ! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

The earthing arrangement where the hot tub will be installed is formed in the TN-C-S system. I want to install the sub-main distribution circuit...
Replies
18
Views
2K
Evening everyone . Currently looking at pricing a job up . It’s a hot tub supply . Outside socket with a few spare ways in an outdoor cu . 10mm...
Replies
7
Views
668
I have someone that wants a hot tub installing and it’ll be my first time, I have came up with anxixeaxfwanted to check it was correct. I wanted...
Replies
10
Views
1K
Replaced our old 240v hot tub with a new one, which also uses 240v for motors, heater, etc, and 120v for low amp LEDs and touch screen control...
Replies
4
Views
1K
Hi Guys So I've never installed a hot tub supply before so take it easy on me. I've spent a bit of time researching it myself and its a minefield...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock