Discuss How much to charge for an EICR in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Those little buttons are too close together and as the 'like' and 'dislike' are next to each other I nearly gave up trying to 'like' a post on my phone. I didn't know what that brown box on the right was, I thought it was an envelope! I need a bigger phone or better eyes, whichever one is cheaper or doesn't hurt!
 
Worked for a company back in 2011 who expected testers to test 40 circuits a day, this was a large concern with many sparkies (but a high turnover of workers), the testing consisted of a quick resistance rest and maybe a trip of the RCD, the rest was "calculated" in the office. This company has contracts for local authorities testing schools, swimming pools and offices. I don't think a test can be carried out properly and the tester make any money at it.
 
Wow! How can 3 get done in a day?

By not being very thorough. Our house had a fault on the ring, it's had two inspections since it was installed (the affected ring was tested apparently) and deemed to be satisfactory because Zs was OK, despite other tests indicating an issue.

When I changed the CU as a result of a fault, I spotted the issue straight away, r2 was way over what I expected to see given r1 and rn. Turned out to be a loose earth connection in one socket that had never been touched since the day it was installed. Took the socket off the wall and the CPCs practically fell out of the terminal.
 
I thought that a high resistance reading was ok if you have an RCD somewhere , usually as a main switch? Up to a few hundred ohms?
 
I'm sorry you are unwilling to furnish me with the answers to my questions, I thought that the function of this site was to pass on relevant information. Still don't know what a troll is.
 

Reply to How much to charge for an EICR in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Can someone please guide me on this? I have virtually no experience of home alarm systems. The client has an alarm which had been fitted to her...
Replies
17
Views
1K
Hi, I recently had an EICR done at my property which unfortunately was unsatisfactory. So the electrican advised a new fuseboard from BG General...
Replies
90
Views
3K
Hi I'm looking for some advice for adding a time delay on my parent's shower room fan. My parents had a section of their garage converted into a...
Replies
8
Views
997
I commissioned an EICR to be done on a property that is in Wales as this is now a requirement in order to let on any new tenancies after 1st...
Replies
1
Views
2K
I own a top floor tenement flat that I used to live in and then rented out after I married. It is currently empty whilst some work is being done...
Replies
0
Views
176

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock