Search for tools and product advice,

Discuss How to calculate an MCB size in the UK Electrical Forum area at ElectriciansForums.net

davidmi

DIY
Reaction score
0
I am doing a campervan conversion and have a 16A/250V shore power connection coming into a consumer unit which has two breakers - one for the AC input into a Victron Multiplus inverter and the other to go to a plug socket for non inverter loads. I would like to know how to size the MCB for the AC input into the inverter - how the calculation is done. So 16amp coming in. The inverter is a 12v/500/20 Multiplus so continuous output power at 25C is 430W and peak power is 900W.
 
surely the inverter input is 12V D.C. !!
 
The MCB is there to protect the cabling and circuit connected to it, not the appliance (inverter) on the other end. I would suggest a 10A circuit on a 1.5mm cable from the CU would be more than sufficient.
 
One feed in from the 12V leisure battery and one feed in from shore power at 240V. It is the consumer box between the shore power connection and the inverter (the AC input) that I am talking about.
 
The Multiplus is a combined inverter / charger including a transfer switch that I believe can handle 16A regardless of the rating of the inverter itself. The input current will be the total socket load (less whatever is plugged into the raw mains direct socket) plus the charger load of an amp or two. Therefore the input cabling and the MCB protecting it should be rated for the full 16A, to avoid unnecessarily limiting what is available from the sockets.
 
Glad your still with us Tel
had a few health issues ( water retention was one. boke femur another. where the break was, not repairable as in fix break; needed artty ball joint. now worth a bit in scrap value). spent 2 sessions in horsepital, both issues fixed up to a point. you maybe pleased to know that I'm still using the 1553 wot I bort offa you 10 years ago.
 
I am really pleased your okay Buddy, glad your still using the 1553, I have forgotten how to use one these days hehe, your a good man Tel, chuffed your health is improving

had a few health issues ( water retention was one. boke femur another. where the break was, not repairable as in fix break; needed artty ball joint. now worth a bit in scrap value). spent 2 sessions in horsepital, both issues fixed up to a point. you maybe pleased to know that I'm still using the 1553 wot I bort offa you 10 years ago.
 

Reply to How to calculate an MCB size in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
530
I thought I had an understanding of how to size an inverter but I think I have become slightly confused after taking to some proposed installers...
Replies
3
Views
2K
Hi, I am doing a self build campervan conversion and currently in the process of doing the electrics. I'm confident with the 12v circuit design...
Replies
2
Views
2K
When I joined this forum a decade or so back, there was a discussion going on about a welder that was connected with a 3-core cable to L1, L2 and...
Replies
3
Views
2K
I apologise for what must seem an elementary question to most of you: I have need to power a series of LED lamps (in total, up to 60). I am...
Replies
17
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top