Discuss Hypothetical situation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Reaction score
0
Hi guys
Hypothetical question here

What are the symptoms (if any) of a ring within a ring main?
Is there anything to look out for physically or symptomatically or are they just sonething you stumble across?

Thanks

D
 
Hi guys
Hypothetical question here

What are the symptoms (if any) of a ring within a ring main?
Is there anything to look out for physically or symptomatically or are they just sonething you stumble across?

Thanks

D
Strange readings when doing end to end and figure of 8 tests.
 
Operationally you are unlikely to notice anything wrong. There would be no obvious symptoms until a conductor overheats, which is of low probability.
Physically a very careful check of the wiring at each socket and a good understanding of how the circuit cables have been run from socket to socket may allow you to identify the cross connection but casual examination would only appear to show spurs.
The defining identification is the readings obtained from the ring final testing as said above.
 

Reply to Hypothetical situation in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Been asked to move, remove and add some sockets the kitchen and I’ll need to add a circuit for an electric hob. Looked at the board and it’s one...
Replies
17
Views
728
Hi I've got an new outbuilding that needs power run out to it, the building is very close to the house and the original plan was to run an...
Replies
9
Views
949
Hello, I have a hypothetical question (I'm an electrical engineer) to better understand RCBOs and how they are used in the USA. Let's say I would...
Replies
9
Views
1K
evening everyone . Quick question here I’ve recently took over a job that a friend of mine first fixed it’s a 3 bed semi house rewire. I don’t...
Replies
10
Views
2K
Hi, A lot about this fault confused me to be honest. So customer complained the doorbell was not working as intended. By that I mean the chime...
Replies
2
Views
700

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock