Discuss I am Pricing a Block of Flats in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

M

Molly58

I have been asked to feed the Flats Consumer unit with 25mm 2 Core concentric cablefrom a Ryefield 18 way Board mounted at the Mains incomer. Does this comply with the 17th regs regarding mechanical protection. I must admit to using a 3 core swa in the past not concentric because of the termination problems at the consumer.
 
I have been asked to feed the Flats Consumer unit with 25mm 2 Core concentric cablefrom a Ryefield 18 way Board mounted at the Mains incomer. Does this comply with the 17th regs regarding mechanical protection. I must admit to using a 3 core swa in the past not concentric because of the termination problems at the consumer.

No it does not have sufficient mechanical protection, you will need to provide this where required.

Chris
 
Concentric submains should be in a trunking unless there is a riser cupboard (even then Id put trunking) as for the earth its part of the cable Spin check here for a bit more info on concentric cable Split concentric cable to BS7870 its a bit of a pain in a cu id imagine although wouldnt you be fitting a cable head in each flat for meter??
 

Reply to I am Pricing a Block of Flats in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Hi, while carrying out an EICR at a farm cottage on Friday i came up against a problem early on. Whilst measuring the Ze the reading i obtained...
Replies
22
Views
2K
Hi all, I hope you could share your experience and advice regarding supply 50 flats in 5 storey block of flats. We get 3 x 430A supply. What...
Replies
4
Views
1K
Background: I am not an electrician, I am a retired professional engineer high power broadcast transmitter design , but am dabbling outside my...
Replies
15
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
491
Hi everyone, A diversity question concerning 2 consumer units fed from 100amp DNO supply Background, So I have an 18th Ed compliant consumer...
Replies
9
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock