Search for tools and product advice,

Discuss In line fuse holder in the UK Electrical Forum area at ElectriciansForums.net

mhar

-
Esteemed
Arms
Reaction score
423
Got some coastal apartments which have a mixture of downlights, pendants and 5A round pin wall plugs all controlled by conventional light switches and everything is switch fed. OCPD is a B10 mcb which if I derated it to a B6, would still be over the 5A rating of the sockets and plugs. All the 5A rated plugs used are unfused.
I am looking for small inline fuseholders for 3A 1362 fuses (or anything else suitable) which I can fit in the switch backboxes. Otherwise I will have to come out of the cu from the 10A mcb to an sfcu fused at 5A which, whilst easier, doesn't feel right. Or am I missing something?
 
As long as no part of the wiring or any accessory can be overloaded, I wouldn't worry about it. The 5A plug will only be serving one lamp, presumably?
 
They are generally considered as being part of a lighting circuit, you could use 16A if you like, as the others say how likely is it they will be overloaded because the current is limited by the nature of the load. I put 2As in my lounge on 10A devices.
 
Whilst I completely agree, it is for an EICR and so justifies a code under 433.1.1. I can see the common sense argument for a C3 but as Murdoch is implying, who knows. How would others report this please?
 
Whilst I completely agree, it is for an EICR and so justifies a code under 433.1.1. I can see the common sense argument for a C3 but as Murdoch is implying, who knows. How would others report this please?
I wouldn't comment on it at all, B15 and B22 lamp holders are rated at 2A but Reg 559.5.1.204 allows them to be protected at 16A because they are not likely to be overloaded, the same applies. Reg 559.5.1 deems them to be suitable luminaire couplers (BS546) and you rarely see them used for other purposes.
I don't see how it relates to 433.1.1
 
Historically, prior to their use as luminaire couplers, BS546 5A outlets for fixed loads <5A were permitted to be fused at 15A and 2A outlets fused at 5A. I cannot give even a hint as to which edition of regs you might need to search for that though.
 
I thought, not that I am old enough to know. 15A socket, 15A fuse and 5A socket, 5A fuse but you could have three 5A sockets on a 15A fuse.
Maybe 8th, 9th Ed.
 
Which is partly my concern. The manufacturers are supplying a light complete with a 3A fuse to protect their device and cable, we then discard this and connect into a 10A supply.
Thanks for the replies
Dumb question, sorry, but are you saying the light had a manufacturers 3A fuse which has now been removed ?
 
Yes. BS1362 plug which has to be removed to put on the unfused 5A plug. Therefore quite likely a .5mm cable being protected by a 10A ocpd
 
Yes. BS1362 plug which has to be removed to put on the unfused 5A plug. Therefore quite likely a .5mm cable being protected by a 10A ocpd
Are you missing something, do you seriously believe the cable is going to be subject to overcurrent conditions.
 
Hi Westie - Overload current agreed no prob. But perhaps manufacturer's cable not sized to trip mcb under all fault currents, which may be why they put 3A fuse ?
 
Using the adiabatic eqn and Wylex i2t data sheet for their 10A B type I get 0.5mm is good for about 1200A of fault current. This calc has a 12:12 warranty - 12minutes or 12reads :)
 
Hi Westie - Overload current agreed no prob. But perhaps manufacturer's cable not sized to trip mcb under all fault currents, which may be why they put 3A fuse ?
Yes is possible but the manufacturer has to fit a plug and for this country it is going to be a 13A plug. OP you could try the 5A plug from MK part no. 643WHI which comes with a 5A fuse but you could probably change it for a 3A. I would guess it is a BS646 fuse.
 
Yes is possible but the manufacturer has to fit a plug and for this country it is going to be a 13A plug. OP you could try the 5A plug from MK part no. 643WHI which comes with a 5A fuse but you could probably change it for a 3A. I would guess it is a BS646 fuse.

Now I like that - not seen them before. There's your answer then OP.

Daz
 

Reply to In line fuse holder in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I have a question which is confusing me and I cannot find a definitive answer and I hope someone can help. So I have a PC and Monitor and I have...
Replies
4
Views
490
Hi, My current oven is hardwired to a fused connection plate with a 13Amp fuse inside and power switch. That is then connected to the MCB labelled...
Replies
1
Views
982
Hi there I have a few questions related to the power ratings of certain devices and how this interplays with the fuse. The reason I am asking...
Replies
4
Views
995
  • Locked
I read once, never seen one for sale, that there is a solid brass replacement for the standard 13A fuse in a 13A plug. This is to eliminate the...
Replies
162
Views
12K
  • Locked
  • Sticky
Beware a little long. I served an electrical apprenticeship a long time ago, then went back to full time education immediately moving away from...
Replies
55
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top