Discuss In line switch for workbench ring in the The Welcome Forum area at ElectriciansForums.net

Reaction score
5
Hello to all,
I've been asked by a customer to install an intermediate ( between 32a RCBO and first socket) switch so he can easily shut off all his workbench circuits at night. I've been looking for a 4 pole NC switch with a cover but I guess in the wrong place so far.
Any suggestions please?
Thanks
 
Welcome to the forum mate.
How about a contactor activated my a key switch?
 
I personally would not connect a ring final across a four pole switch/contactor due to the possibility of failure to one of the poles. I would change it so a 32A radial is taken to the switch then connect the ring final.

I was thinking of a 'forced guided' contactor.
Also a key switch so that only the person with the key can turn off the circuit.
 
I don't see how a force guided contactor would help, a four pole one normally has two n/c and two n/o poles.
 
I don't see how a force guided contactor would help, a four pole one normally has two n/c and two n/o poles.

If one of the contacts get stuck then they all will. As in your suggestion, you can still get a contact stuck and the other working, without one. It's a safer option.
 
But a four pole has opposing contacts, two n/o and two n/c doesn't it or am I getting this totally wrong.
 
But a four pole has opposing contacts, two n/o and two n/c doesn't it or am I getting this totally wrong.

The OP will have to look for a forced guided contactor that has 4 normally open contacts. Doesn't necessarily have to be '4 pole' could be '6 pole', as long as it has 4 normally open contacts.
Or he could go along your suggestion, then he only needs one that has 2 normally open contacts.
I just mentioned a 'forced guided' contactor mate.
 
I would go with snowhead's suggestion, but you can also get four pole isolator switches, as main db type switches, that, since you mention a cover, you could put one in a 4 module enclosure.
 
What is the users intention?

Does he want to be able to clunk everything off under load as he leaves?

or..

Does he want to power everything down in a controlled and orderly manner before isolating the power to the circuit as a precaution?
 
Really need input from the OP as to what the customer requires on this. We have given him 3 options.
 
Hello, Spoon/Snowhead and all,thanks for all the input and welcome. I'd a bit more reading and a call to make..Yes, 'clunk off' is the deal. the guy is shutting up a big building each night, the benches have mebbe battery chargers, heaters and solders left on.
I looked at the rotary isolator which is the right kind of positive use design but not under load. Was thinking NC but that's relevant for emegency switch I think. This is a daily use device.
Thanks
 
Whatever switch you use is going to fail if it's switching inductive loads daily.

Maybe one of these might be suitable;

7a8f77ea3c8083792cebacde5eed8993--hobbit-hole-frankenstein.jpg
 
If things like soldering irons are left on and only turned off by this master switch then they will be turned back on again by it. So you still end up with things being left on and unattended
 
Sounds like more common sense or training of the people using the equipment is needed, rather than a switch..
 

Reply to In line switch for workbench ring in the The Welcome Forum area at ElectriciansForums.net

Similar Threads

Hello everyone, I'd like to seek your input on a matter. I'm in the process of designing the electrical connections for the following kitchen...
Replies
38
Views
3K
hello guys, hope you’re all well. We are looking at installing the Hager SFT240 changeover switch to three live aboard boats with an electric...
Replies
5
Views
1K
I hope someone can help with this as I'm stumped. My landing hallway ceiling (2016-build house) has two rose pendants which I've attempted to...
Replies
7
Views
513
Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi everyone :) my first post here. Quick background I'm a newly qualified installer of somewhat advanced years whose just starting out in the...
Replies
12
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock