Discuss Insulation added after second fixing! in the UK Electrical Forum area at ElectriciansForums.net

Reaction score
2
Hi everyone.
I need a little advice please. Several months ago I first fixed and second fixed a timber frame loft conversion ( open plan living area and kitchen) for a friend /client. I haven't signed it off yet as I was waiting to install I new CU for him and for him to fit the kitchen. I fitted a kitchen ring final in 2.5mm, socket radial 2.5mm, 2x 6mm hob/oven supplies, a radial, and 2 lighting circuits in 1mm. And smoke detector.1mm. At the time it was simply kingspan with cables through timbers mostly not touching the insulation I used Reference method 102 for calculations. I have however returned to connect up an electric skylight and noticed that every cavity including the 18 inch floor space has been packed with wool insulation changing the reference method to 103. As we know a ring final should not be installed when using ref meth 103 and the radial 2.5m current carrying capacity will be reduced to 13.5A, the 6mm cables to 23.5A. The walls have been plastered and the tongue and grove flooring down and glued. Does anyone have any suggestions on what I can do to remedy this situation? Many thanks in advance.
Si
 
All you can do is derate the circuit breakers providing that the connected loads will not then exceed the rating of the circuit breaker.

It sounds like you've put plenty of thought into designing the installation which is great to hear :)
 
I feel the pain on this one - lots of thought went in and they stuffed it up (almost literally) for you.
The other problem is that this is a loft conversion, and building regs will have been inspecting it. So this isn't really one to bend the rules too much on.
One creative thought - the merits of which can be critiqued!
If you change the first and last socket on the kitchen ring to a 13A FCU, split the ring in the middle, and feed from two 16A breakers on the basis of downstream overload protection..... then if the loads are neatly divided you get the max 26A of design current out of what is there then.
 
Hi everyone.
I need a little advice please. Several months ago I first fixed and second fixed a timber frame loft conversion ( open plan living area and kitchen) for a friend /client. I haven't signed it off yet as I was waiting to install I new CU for him and for him to fit the kitchen. I fitted a kitchen ring final in 2.5mm, socket radial 2.5mm, 2x 6mm hob/oven supplies, a radial, and 2 lighting circuits in 1mm. And smoke detector.1mm. At the time it was simply kingspan with cables through timbers mostly not touching the insulation I used Reference method 102 for calculations. I have however returned to connect up an electric skylight and noticed that every cavity including the 18 inch floor space has been packed with wool insulation changing the reference method to 103. As we know a ring final should not be installed when using ref meth 103 and the radial 2.5m current carrying capacity will be reduced to 13.5A, the 6mm cables to 23.5A. The walls have been plastered and the tongue and grove flooring down and glued. Does anyone have any suggestions on what I can do to remedy this situation? Many thanks in advance.
Si
Were you aware of work undertaken whilst you were first fixing, if son down to you to sort the problem, I THINK.
 
Hi everyone.
I need a little advice please. Several months ago I first fixed and second fixed a timber frame loft conversion ( open plan living area and kitchen) for a friend /client. I haven't signed it off yet as I was waiting to install I new CU for him and for him to fit the kitchen. I fitted a kitchen ring final in 2.5mm, socket radial 2.5mm, 2x 6mm hob/oven supplies, a radial, and 2 lighting circuits in 1mm. And smoke detector.1mm. At the time it was simply kingspan with cables through timbers mostly not touching the insulation I used Reference method 102 for calculations. I have however returned to connect up an electric skylight and noticed that every cavity including the 18 inch floor space has been packed with wool insulation changing the reference method to 103. As we know a ring final should not be installed when using ref meth 103 and the radial 2.5m current carrying capacity will be reduced to 13.5A, the 6mm cables to 23.5A. The walls have been plastered and the tongue and grove flooring down and glued. Does anyone have any suggestions on what I can do to remedy this situation? Many thanks in advance.
Si
Advice for what its worth study the entire spec for the building before you start any work.
 

Reply to Insulation added after second fixing! in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Please advise what I should test / check next. My usual qualified electrician who did all of the work here is in Ireland for 4 weeks and not...
Replies
45
Views
3K
Hi there, long time lurker, first time poster here. Straight down to it.. A friend asked me to add some sockets and additional lights to a small...
Replies
0
Views
908
Just after a bit of advice regarding the following. First up I am not electrically qualified and know limits of what I would and would not...
Replies
6
Views
2K
Hi Guys New to forum and enjoying reading the threads, all interesting, so.. Looking to re-wire my kitchen due to re-fit and some of you will be...
Replies
64
Views
6K
Evening all. Working on a bungalow at the minute with the dreaded stramit walls. All my new cables have been surface, galv capped and the builder...
Replies
2
Views
5K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock