Discuss Insulation test L to E long length of SWA in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Reaction score
16
Insulation test live to earth = 0.7 ohms.
This is a long length of buried swa cable (approx 100m) from mains in to submain.
Test done with live and earth disconected at main and with switch off at sub main.
Question - is this an accurate reading or am I misding something.
Its a big job to replace if I've got this wrong ?
 

Attachments

  • 20240228_091021.jpg
    565.6 KB · Views: 25
If this is a genuine reading, then the cable is severely damaged, and must be repaired, replaced, or taken out of service.
Why would L+N to earth give any better reading?
Chances are that the cable is damaged at one point, and similar measurements taken at the other end of the cable should give some indication of where.
 
Also the CPC should be connected to earth during any IR tests.

Here (if SWA) it is very unlikely to make a difference, but more generally with stuff like T&E you can have a live nicked by a screw/nail and it is leaking to the wall, etc, but not to the CPC that still has the insulation separating them (and from wall, etc).
 

Reply to Insulation test L to E long length of SWA in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

Similar Threads

Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
637
I want to check the insulation of the 3-phase 400VAC asynchronous squirrel cage motor. Motor's stator windings are connected in delta. I've read...
Replies
10
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
510
Hi guys, Can I ask you a DIY question? I'm refurbing a detached garage and adding a garden building. Garage currently has a submain supplied by...
Replies
1
Views
838
Afternoon everyone.. During some testing I have found an IR reading of 0.01MΩ between N-E. This is on a length of SWA buried underground from the...
Replies
17
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock