Search the forum,

Discuss Interlink smokes wired in 3core flex in the UK Electrical Forum area at ElectriciansForums.net

P

p11jor

As title, just clocked this on a job I am on, all conductors correctly sleaved,

Has anyone saw this before?

I have always used 3core&e
 
All 230volt circuits require a cpc, even if it isn't connected to a piece of equipment that needs earthing, so my answer is no its not wired correctly and anyway a flex shouldn't be used as fixed wiring in my opinion.
 
would a circuit that is soley dedicated to smoke alarms require connected earths at each point even though they wouldnt be connected

Yes - all points must be earthed and these connected back to the consumer unit or D.B., even it the point has a class fitting on it.
 
Whether the load (alarm/light/socket) needs an earth or not is irrelevant. As has been stated the cable itself needs an earth to help detect faults if it is damaged. I believe this is why in T&E the cpc is not sleeved: so that a damaged line or neutral has more chance of touching it and tripping the protective device. Otherwise it would need the insulation of the line AND earth to be damaged to make a connection to the CIRCUIT protective conductor.
 
I have actually just had to purchase 100metres of 3core & earth 1mm for a little commercial job. £42 incl vat......so I think it goes down to lazyness oppose to cost, as I am sure flex is a bit more expensive than that......correct me if I am wrong
 
All 230volt circuits require a cpc, even if it isn't connected to a piece of equipment that needs earthing, so my answer is no its not wired correctly and anyway a flex shouldn't be used as fixed wiring in my opinion.

Absolutely nothing wrong with it when used appropriately. Not saying this is appropriate though!
 
I use a fair bit of flex on mains wiring, it's double insulated and rated for 230, so in the right situation I really don't see why not. However using 3 core on interlinked smokes is a big no!!
 
I wish I could find the thread discussing earths in circuits we discussed a few months back lol, I had a look via the search but as of yet I can't find it for looking, there were some good arguments regarding class 2 circuits and no earths, I think I got a hiding from memory sugesting CPCs were essential in the cable even if they were not connected, some members here turned me over and others about this haha, you may well change your mind about cpcs in cables for class 2 equipment if you read it LMAO.
 
Main argument for me is that in the future the Class 2 device might be replaced with something needing an earth. And of course, the presence of a CPC in a cable does make it more likely that the protective device will operate if the cable is damaged.
 
thing is though when you design a circuit you don't need to think about what may or not may happen in the future, so that argument won't hold, however IMO every 230 volt circuit should contain a CPC, end of, but as mentioned there was some good arguments about this last time we went down this route, even though I was right haha
 
How about replacing all smokes with mains powered radio linked units instead and re-establishing the earth core... cheaper and rewiring the lot i would assume.....
 

Reply to Interlink smokes wired in 3core flex in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

I've asked a similar question before I think and we came to the conclusion that apart from new houses and HMO's etc there aren't any rules about...
Replies
3
Views
368
Any issues with wiring lighting in 4core flex rather than 3core and earth? Approximately 50 LED panels to wire all fitting into a suspended...
Replies
19
Views
1K
Hi all. I have been asked to take over a job an electrician has started, and has moved abroad. The house is a big mansion, with a 3PH supply...
Replies
49
Views
4K
I have a spare 2.5mm 3 core flex cable. Can I use it for an outdoor light? It will be connected a junction box that's already supplying...
Replies
2
Views
1K
Hi, The wire of my dehumdifier is broken (Meaco 20L Low Energy). The wire was being pulled over a period of time, which seems to have lead to a...
Replies
3
Views
229

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock