Discuss Intermittent Rcd Tripping in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

S

Shane1089

Hi guys, i attended a property on friday the tenant has stated the rcd is tripping at intervals of 45-60 mins, i separated the ring legs and upon testing i was getting a reading of 0.60Mohms between Line-cpc on one end of the cable with all loads disconnected, i have never come across this fault before and my question relates to the tripping characteristics of the rcd/mcb. is this a problem you guys have come across before and should the mcb be tripping out although i know the rcd is more sensitive? many thanks in advance.
 
So..........what was tripping?

Mcb or Rcd?

Or Rcbo?

Give us a clue mate :)

Rcd .......earth fault.

Mcb .............short cct/overload/earth fault.
 
600,000 Ohms. Thats alot of Ohms!

did you test the RCD as well. Just to be sure. Seems a bit high for an RCD to trip but who knows whats going on there.
 
Hi guys, i attended a property on friday the tenant has stated the rcd is tripping at intervals of 45-60 mins,

think.........

45-60 min intervals................mmmmmm

Timeclock/pump with level switch/heating pump..............possibilities are endless but easy really when you think about it:)

Well...........sometimes lol
 
lol but are you saying the the <1Mohm reading between line to cpc has nothing to do with it? even when i attended i forgot to mention(my bad) the rcd got to a point where it was constantly tripping even with all loads plus boiler disconnected sorry if i sound like a complete novice
 
mmmm

If you have an RCD tripping with everything disconnected on the outgoing terminals then..............well..........c'mon?
 
Shane, snapped a picture of you going to work chap...

2200991.jpg
 
All jokes aside i understand the fact of mcbs tripping at under <1Mohm my original question was in regards to how the mcb could/should react with the rcd in line with this type of fault, although you may already have had your kicks for the night
 
"i have never come across this fault before and my question relates to the tripping characteristics of the rcd/mcb. is this a problem you guys have come across before and should the mcb be tripping out although i know the rcd is more sensitive? many thanks in advance."
 
All jokes aside i understand the fact of mcbs tripping at under <1Mohm my original question was in regards to how the mcb could/should react with the rcd in line with this type of fault, although you may already have had your kicks for the night

Shane..............there are many on here willing to help but your post doesn't make sense mate.
You said Rcd was tripping.............that's an earth fault..........think about it!
 
Shane. The RCD is either detecting a earth fault or its faulty. As for you IR on the CPC to Line being 0.6 Meg that should not trip the RCD . 230/0.03=7666 Ohms which is a long way off 600000 Ohms . Are you sure that nothing else is connected and if so I would IMO exchange the RCD and locate the IR fault that you have !
 
Thanks for the feedback Tony, I am visiting again tomorrow to try and reinstate the other half of the circuit, I will make sure I check for anything that I may have missed and recheck the rcds operation, many thanks.
 
Thanks for the feedback Tony, I am visiting again tomorrow to try and reinstate the other half of the circuit, I will make sure I check for anything that I may have missed and recheck the rcds operation, many thanks.


Shane1089


would be good to hear what you find & what it was in the end :)
 

Reply to Intermittent Rcd Tripping in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

Similar Threads

Cant get my head round this :( I understand N-E faults cause RCD's to trip, but I cant understand why on these 2 occasions, googled allover but...
Replies
13
Views
1K
Hi I am asking for help as a novice and 1st time user of this forum. Recently started to experience tripping of MCB & sometimes with the RCD at...
Replies
7
Views
540
Good evening, I have recently moved into a new home and I am having problems with the MCB/RCD tripping (Mem M6 Type 3 - 30mA). It intermittently...
Replies
8
Views
1K
Hi All, Weird matter happening here and I hope you can help! My 3 Pahse EC Fan is connected to a sensor and a controller for the temperature...
Replies
2
Views
872
Hi Guys, I'm having trouble diagnosing a fault on a customers downstairs socket ring, which only ever trips when the washing machine is used. The...
Replies
22
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock