Hi.
i have a application where I need to run 2.3 kW (2300 watts) for up to 2 hours continuous. It will need to be a 12 or 24 volt inverter.
What size lead acid batteries in ah will I require to get this power from a suitable inverter.
a generator cannot be used due to noise and location.
Any sums and formulas to work this out would be very helpful.
Many thanks.
 
2300 / 12 = 191.66 x 2 = 383.33ah

2300 / 24 = 95.83 x 2 = 196.66ah

You would need 400ah 12V or 200ah 24V minimum. Ask inverter manufacturer about compensating for loses.
 
Last edited:
pretty much as above. ideally a 200AH battery, but allowing for losses and reduction in volts on low battery, at least a 300AH.
 

Reply to Inverter to run 2.3kw for up to 2 hours in the Solar PV Forum | Solar Panels Forum area at ElectriciansForums.net

Similar Threads

Hi everyone. The owner of the business I work for along with myself have created a DIY inverter setup that is giving us some issues. We bought...
Replies
4
Views
1K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
477
Hi. I want to open a mobile coffee shop. I'm finding it difficult to power it without going duel fuel. I'm thinking 4x110ah 12v agm leisure...
Replies
17
Views
2K
Good Afternoon All, So I have a new situation to me that I cannot seem to get a definitive answer for. I trained as an electrician and did...
Replies
0
Views
785
Hi Everyone, I'm new to this forum and am hoping someone can give me some advice, as I'm absolutely clueless when it comes to these things. I'm...
Replies
11
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock