hi guys i have to do an ir test tomorrow but my problem is that there are appliances connected as it is an existing installation. basically i want to test an installation but has a plc connected that controlls alot off the circuits that are in the fuseboard. if i join the l + n and test to earth will this save the plc compondments from damage.
as i did this the other day and there was a fluoresence light connected and it brought down all the readings and when i dis connected the light everything was fine. hope some body can understand
 
It's the preferred way of IR testing on a periodic inspection on other than small domestic installations.

Some fixed equipment and surge protection devices can still affect readings though.

You don't sound like you've done much testing?
 
no not done alot off testing am only familar with domestic unfortnately. and am afraid off damaging the equipment and can not just disconnect it as it controls a lot off the installation. is it ok to test it the way i mentioned and if it is then how come the pluoresence brought down my readings before
 
Did the fluorescent have an integral emergency light?

I'm assuming you didn't test L-N on the fluorescent? If you did then you're just seeing a reading influenced by the ballast/control gear.
 

Reply to ir testing in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

Similar Threads

Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
659
Hello all, I hope you're all keeping well. I have a question regarding insulation resistance testing. Whether doing a single circuit IR test or...
Replies
9
Views
615
In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
647
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
403
Hi all, Testing question for you. I'm currently testing an existing domestic installation. The wiring is about 20-25 years old. We have rewired...
Replies
7
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock