Discuss Ir testing in the UK Electrical Forum area at ElectriciansForums.net

G

glasgospark

ir testing today on 6 circuits all >999 apart from sockets which was around >500 odd,

every socket unscrewed and walls being plastered no bags over sockets , im thinking this may be effecting the results , loose connection/condinsation etc
 
lol

i know its a pass, 0.5M is the minimum

i wasnt saying it is a fail was wondering why the meter would >999 the rest and not the ring so obv something causing it .
 
ir testing today on 6 circuits all >999 apart from sockets which was around >500 odd,

every socket unscrewed and walls being plastered no bags over sockets , im thinking this may be effecting the results , loose connection/condinsation etc
Hard to please some folk
 
breathe on the crocs will lower the reading at that level.
 
Put it into perspective,
@ 500Meg, you're leaking <1 µA, through resistance.
The circuit will be leaking considerably more than that through the capacitance of the cables when energised.
 
At those levels it could be anything but again nothing to worry about. Other option is to use a megger that only reads up to 299 Meg then you wouldn't even be asking this question. :lol:
 
Last edited:
That's it mate problem solved :lol:
 
Now go and empty these...
 

Attachments

  • Pints+of+beer.jpg
    32.6 KB · Views: 121

Reply to Ir testing in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

In my line of work it's very rare that I ever have to change a DB. I'm largely in maintenance; occasionally have to add new circuits etc. so in...
Replies
3
Views
636
So was on a call out today and cooker circuit kept tripping the RCD. Disconnected at the board and at the cooker switch and IR’d the cable and...
Replies
9
Views
399
Hi everyone. Hopefully someone can help with a little mystery i had today. The issue is fixed but I want to understand what was going on to help...
Replies
8
Views
644
Hi all, Testing question for you. I'm currently testing an existing domestic installation. The wiring is about 20-25 years old. We have rewired...
Replies
7
Views
1K
Recently changed a CU for a friend and today when visiting one of the RFC's RCBOs tripped. It was due attention anyway as open ring and no time to...
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock