Search the forum,

Discuss joining 16mm T&E in the Australia area at ElectriciansForums.net

B

BristolSpark

Any ideas on joining a 16mm T&E.

Its fed from a main switch up into a flat. Its mechanical sound just to short to reach new board. it needs to be joined under the floor.

But we are lost on best practice for this.
 
Would a 60A junction box help you? What's the rating of the cables protective device?

click-60a-3-terminal-box-junction-box_549_1_medium.jpg
 
....can you pull it back, the cable, so to speak, to an accessible area, and use the JB pictured? They are very good I like them. Very up-to-the-job.
 
If it’s going to be inaccessible then I’d crimp and sleeve.
But to be honest it would be better if it can be made accessible those JB’s look a good bit of kit.
 
This supply will pop out of the floor by about 6- 8inchs max. so we could put a small enclosure then JB it. Then ininstall the new board. We have not had proper chance to view the switch, from the height we are at we assume at present 63A supply.

Running a new cable was original thought thought, but due to location and being a third floor flat, access is rather bad, the route is not easy.
 
As it sounds like the 16mm T&E are the "tails" wouldn't it be better to run new tails completely? You'll have to run a new main earth so why not do the lot?
 
If you've got 6-8 inch to play with and seen as the 16mm t+e is for your main incomer, just wall mount henly tail connectors and run your tails from them to the new board. This way you comply with 543.3.3 for testing as Murdoch pointed out.

images-246.jpg
 
use 16mm cable link, clamp properly and wrap with PVC tape

Welcome to the forum.

Unfortunately the member in question hasn't been active in some time and this discussion dates back to 2011. In the UK we have a few options for joining cables of this type and size, but wrapping with PVC tape would not be permitted as a suitable means of insulation and protection.
 
So many names have disappeared from this thread.
I wonder what happened to spartykus, I liked him.
Pity we have to see the given name 'sausage'. I'm sure who ever it was was a right pita, but still, it can't be nice for them to see that if that pop back on every now and then.
 
So many names have disappeared from this thread.
I wonder what happened to spartykus, I liked him.
Pity we have to see the given name 'sausage'. I'm sure who ever it was was a right pita, but still, it can't be nice for them to see that if that pop back on every now and then.
It shouldn't say 'sausage' it should say 'Knob head, nob head, door handle head'. Even if they were horrible, they shouldn't have to look at that.
 

Reply to joining 16mm T&E in the Australia area at ElectriciansForums.net

Similar Threads

Client has had a meter installed for a new consumer unit in their shop they are looking to rent out the spare space for a barber shop so they want...
Replies
10
Views
497
I'm practising EICRs on friendly locations as I'm still in training - technically done my 2391-52 but frankly need loads more practise. I've just...
Replies
11
Views
961
Hello all, I wonder if I can get some opinion on my deliberations on an old TPN installation with numerous 1P sub-boards wired up with 16mm T&E...
Replies
5
Views
1K
Im starting a re-wire of a top floor flat, they have run an 16mm T&E with a 6mm earth from the ground floor to the 3rd floor feeding the CU...
Replies
18
Views
1K
Hi all, Have a relatively simple question. Doing a rewire to make a circuit in a single room. My father is a retired spark, so no worries about a...
Replies
7
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock