As per title, went to look at kitchen rewire this evening, no probs all straight forward, as I’m about to the leave lady says while you here I keep getting shocked from this wall when I washed it down?
Turns out someone has extended old 4 mm stranded cooker circuit with 2.5 and put a double socket on the end, but they decided to just twist the cable together and use a little insulation tape and left on a 32mcb....
Anyway what is people’s preferred method of jointing two different size cables?
Going to change the mcb but also curious as to which cable type id select if filling out a certificate?
Hope that all makes sense and as always thanks to all
 
Sorry SC was just trying to work out how to alter my thread....should’ve said the join is in a back box that was plastered over....happy to cover with a blank as it’s not visible..
 
As per title, went to look at kitchen rewire this evening, no probs all straight forward, as I’m about to the leave lady says while you here I keep getting shocked from this wall when I washed it down?
Turns out someone has extended old 4 mm stranded cooker circuit with 2.5 and put a double socket on the end, but they decided to just twist the cable together and use a little insulation tape and left on a 32mcb....
Anyway what is people’s preferred method of jointing two different size cables?

Going to change the mcb but also curious as to which cable type id select if filling out a certificate?
Hope that all makes sense and as always thanks to all
Fit a switched fused spur where the cable changes sizes. Or rewire the whole circuit to a 20 Amp radial.
 
Thanks people, yep already in the process of Lowering the mcb, yep just one socket on the circuit...no different to a spur on a 32a ring I suppose? I see your thinking there Danny but I think I’ll downgrade anyways.....
 
Thanks wilko and Sc yep that’s what I’ll be going for....I was just over thinking it, if it was in the kitchen where I’m rewiring I’d just do away with it and put the socket on the new ring
 
The blank plate won’t be visible any more @DefyG as there is now a unit in front of it, prior to that someone had attempted to hide the joint in a back box that left the edges exposed but painted over and that was causing the shock
 
FFS,

Screenshot 2019-03-30 at 19.48.05.jpg
 

Reply to Joining different size cable..... in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

So, I already have solar (an older FITS installation) and it's been particularly successful so I want to extend this. I'd like to do two things at...
Replies
1
Views
553
Hello all, I've just been perusing the AM2/E/S threads on here. Thought you might like a bit of a review. If, like I did, you find yourself...
Replies
7
Views
2K
Now and again, I need to join a cable that is buried in a wall, sometimes in a stud wall, sometimes to be plastered over. Sometimes when someone...
Replies
56
Views
77K
We recently had a thread or two about some cables that were almost certainly tinned copper, but people continued to suspect they were aluminium...
Replies
7
Views
3K
T
Hi, First let me just say that I am not an electrician although in the past I've done the usual garage and shed wiring without having any...
Replies
24
Views
8K
Thai Amateur
T

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock