Discuss Just a quick question in the UK Electrical Forum area at ElectriciansForums.net

Doomed

-
Esteemed
Arms
Reaction score
685
In a large yard, incomer in corner, TNS, feeds some switch gear and then a long length of SWA to garage in other corner of yard about 100m away.
By garage I mean a big garage, water canteen and all.
Readings are good at the garage sub board.

There is a bit of me that wants to TT the garage, but I know with the ground there I will struggle to get a good reading.

As its TNS I don't have to TT do I?, so please tell me to stop being stupid and leave it alone.
 
This is not necessarily being stupid, but the decision is not based on distance as seems to be suggested in the OP.

You need to understand why some installations may have a seperate TT earthing system set up at outbuildings before assessing this and making a decision.

Is main bonding required at the outbuilding? If it is not then you can stop there. If main bonding is required at the outbuilding then does it have a suitably sized cpc or bond from the MET through to the outbuilding?
If it does not then you need to assess whether it is better to install it or to convert the outbuilding to TT, cost can have an influence on this decision.
 
With a tns system your requirements for minimum bonding conductor size is significantly less than pme, hopefully at least your swa csa should be of a sufficient size to comply even if there is no additional earth conductor core within the swa, as youve said the readings comply

Hope i have understood your point?

Why would you want to TT it?

This then brings up the issue for the need of global rcd protection likely required for the garage which can sometimes have equiptment that might be a problem or even a safety issue if nuisance tripping/ and or high earth leakage occurs

In my opinion your likely making future problems for yourself
 
Again, thank you.
I sometimes over think and start doubting my knowledge and memory. You have all put my mind at rest. (well, one small part of it at least).

So what is the answer regarding the need for main bonding?
Is it required and if so does the submain include an earth of sufficient size to provide main bonding?
 

Reply to Just a quick question in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

Was having a poke around the old man's house today. Anyway. DB is under stairs (18th ed following a recent extension. Not done by me but it's...
Replies
7
Views
739
Hi fellow sparks, I've just started out on my own so I'm spending a lot of my time trying to find out the correct way of doing things of...
Replies
13
Views
882
Insulation test live to earth = 0.7 ohms. This is a long length of buried swa cable (approx 100m) from mains in to submain. Test done with live...
Replies
35
Views
2K
Hi, I have a Victron Multiplus-II 5kVA inverter/charger with Pylontech US5000 batteries installed in my house along with a 6.8kWp PV array and...
Replies
12
Views
481
Hi all, Been browsing these forums for a while, always great to learn a new way to skin the same cat. Anyway, cut a long story short, was an...
Replies
11
Views
690

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Electrical Forum

Welcome to the Electrical Forum at ElectriciansForums.net. The friendliest electrical forum online. General electrical questions and answers can be found in the electrical forum.
This website was designed, optimised and is hosted by Untold Media. Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock